Look there is a leak somewhere after 3rd valve it might be small and going somewhere you can't see might not be your fault it could be a pin hole in pipe up might just be better roping it out and doing it again if that the easiest way
 
Look there is a leak somewhere after 3rd valve it might be small and going somewhere you can't see might not be your fault it could be a pin hole in pipe up might just be better roping it out and doing it again if that the easiest way

After this pressure test, that has got to be the next move, I'm hoping the tissue I have round every joint is going to be wet, at least I will know then and do something about it

It is brand new copper at the monent, do I run it in poly or more copper ?
 
I hope you get it sorted let me know how you get on

I'll be letting EVERYONE know, I would hate anyone to have to deal with something like this again


Should have gone for an hourly rate, would have paid for Christmas somewhere sunny
 
If you can check all the pipe as it probably not your joints as you already checked them it's a hard one mate I do feel for you
If you change whether poly or copper it's your choice personaly I prefer copper
But nothing wrong with plastic it has it's place
 
We live and learn mate

After 40 years I thought I had seen it all, but this has me beat

I prefer copper, sweated joints myself, usually regard plastic and pushfit as a DIY thing (but the fittings are handy in tight spots or a loft with old style lagging (inflammable)
 
Interesting...

long shot and I'm sure its been ruled out all ready, I have read all the threads quickly (six pages) so my apologies in advance... Mixer tap body allowing cold into hot water side of life? as I say a long shot
 
I use all all sorts in right place
Copper
polypipe
Loads of underfloor pipe
Pipe in pipe
But will always prefer copper
 
Interesting...

long shot and I'm sure its been ruled out all ready, I have read all the threads quickly (six pages) so my apologies in advance... Mixer tap body allowing cold into hot water side of life? as I say a long shot


mmmm, havent thought of that, but the cold tap in the bath has been off and not dripping into the container I have wired on tto the spout
 
No, he means cold pushing through tap back through hot pipe which shouldnt be the case if your hot is off a combi.
 
Sorry that wouldnt be the case because it would come out of spout. Still if you got isolation (ball'o'fix) on your bath tap supplies it wouldnt hurt to turn them off and check.
 
No, he means cold pushing through tap back through hot pipe which shouldnt be the case if your hot is off a combi.

Ah right, I follow, both the hot tap and cold are off

I'm grabbing at straws here (just hope there isnt a leak on the dam straws though :-( )

I really didnt think this topic would stretch to so many pages, sorry lads, you must have better things to do with your Sunday evenings
 
Sorry that wouldnt be the case because it would come out of spout. Still if you got isolation (ball'o'fix) on your bath tap supplies it wouldnt hurt to turn them off and check.

I hadnt put them on the bath or HB, was relying on the no 3 SC to isolate them (not often people change taps or do washers) there is one on WC, though, (that washer in there gets done more often I have found, but they have a standard BV in that)
 
you must have better things to do with your Sunday evenings
Actually no, im on-call and its my birthday so i cant drink, and ive only had two jobs today, so im like a coiled spring ready to pounce. By the way, where are you?
 
Actually no, im on-call and its my birthday so i cant drink, and ive only had two jobs today, so im like a coiled spring ready to pounce. By the way, where are you?

West London, Northolt, the job is 15 minutes away, its a tip, they just upsticks and went on holiday, leaving me, a chinese kitchen fitter (who speaks no English) a house sitter who is Sri Lankan (and speaks no English) its a bloody nightmare

I'm supposed to be retired, I did all my on call stuff at LHR, 1 in 3, a call out every night while on call,

Not much of a birthday, but try and have a happy one :)

(I have got to the age when I dont celebrate, I commiserate)
 
Its not true how loud you shout at them, they still dont understand you:mad::mad::mad:
 
A combi, but that is fed from SC 2, there isnt a problem on that side, its from SC 3 to the bathroom, just on the CWM which feeds just the bath, HB and WC

Just to reinterate (there are a lot of pages to go through, and rather than read the lot, here it is in a nutshell)

SC 1 feeds everywhere, SC 2 feeds the granny flat, boiler, sink in the granny flat, shower, WC in the granny flat AND the new kitchen

SC 3 feeds JUST the bathroom on the main house and just CW and this is where the problem is, the meter only runs when SC 1 and SC are open but taps are shut (WC isolated)

Okay ?

Clear as mud :):)
 
Last edited by a moderator:
Come on Derrick the suspense is killing us, how did you get on today?

Is your customer a happy chappy yet?
 
Come on Derrick the suspense is killing us, how did you get on today?

Is your customer a happy chappy yet?

I couldnt do buggerall, the chippies router busted, and he cant cut the hole for the sink and I couldnt even get close to any pipework

I went in the bathroom though, the dam tissue was dry and still no puddles, I disconnected the cold tail on the bath and put the gauge on, reading 3.72 bar, and turned the water off, I will find out tomorrow if there is any drop in pressure (it didnt while I was there though)
 
I've got to admit, I'm looking forward to finding out what the issue is here. Keep us posted mate.
 
I've got to admit, I'm looking forward to finding out what the issue is here. Keep us posted mate.


When I got there I half expected everyone on this thread to be there, just to see what was going on with it and laugh at me :):):)
 
THE INTRIGUE AND SUSPENSE IS WORTHY OF AN HITCH COCK MOVIE. Sorry about the capitals.
 
That is one scary avatar croppie!! You look a wee bit maaaaad in the heeed!!
 
So Derrick you can see all of the pipework from the meter to the services? There isnt anywhere that you cant see? Im just baffled how this is happening...there has to be a leak somewhere...and theres a lot of people on here who want to know where it is haha
 
So Derrick you can see all of the pipework from the meter to the services? There isnt anywhere that you cant see? Im just baffled how this is happening...there has to be a leak somewhere...and theres a lot of people on here who want to know where it is haha


Not quite from the meter, but from the main SC (no 1) in the house, and then from SC 2 which goes to the bathroom, just feeding the cold side of both the HB and bath, then the WC
 
here is an update :)

I got there and still cant put the kitchen sink in, this chippy hasnt cut the hole for the sink yet (his router died)

I went up in the bathroom expecting the worse, the pressure gauge had dropped .2 of a bar, not much at all, I thought, the meter was still turning though, but still slowly

So it hasnt got any better or any worse, but I cant understand why the meter is still turning and I have lost so little pressure

Bit of an anti climax, isnt it ?

Still no closer to solving this :(
 
Anti climax ain,t the word , i feel more deflated than watching 44" chest lol , at least you know for sure that you do not have a leak ! now you need to look at the incoming main or get the board out and show them it must be a dicky meter
 
Anti climax ain,t the word , i feel more deflated than watching 44" chest lol , at least you know for sure that you do not have a leak ! now you need to look at the incoming main or get the board out and show them it must be a dicky meter

I had the guy out before, he said the meter was fine (how he knows without having it dug up I dont know) he said it only moves when water flows, well it was still moving and I still had pressure (for over 24 hours, standing pressure) so something is wrong somewhere
 
Im sure i read somewhere that if some drunk youths walked by in the night and decided it would be funny to smash up the meter face (assuming its external) that the water board would replace the meter. wink wink.......
 
Im sure i read somewhere that if some drunk youths walked by in the night and decided it would be funny to smash up the meter face (assuming its external) that the water board would replace the meter. wink wink.......


That would only happen if the plumber left the cover up and they used something from all the rubble outside, though

I suppose I had better start leaving the cover down in case that happens :confused::confused::confused:
 
Don't think they have to be drunk.

I came across this thread a couple of days ago and wondered how long it would be before someone suggested changing the meter. I'm dontknowitall on purpose but I think you've done enough to try an eliminate all the other possibilities.

One other thought I had was to cut the house pipework as near the meter as you can and pop a stop end on the incoming mains (then check the meter then re-solder). I'm intrigued now as to what the answer is - hope you tell us after nine pages of this!!
 
Don't think they have to be drunk.

I came across this thread a couple of days ago and wondered how long it would be before someone suggested changing the meter. I'm dontknowitall on purpose but I think you've done enough to try an eliminate all the other possibilities.

One other thought I had was to cut the house pipework as near the meter as you can and pop a stop end on the incoming mains (then check the meter then re-solder). I'm intrigued now as to what the answer is - hope you tell us after nine pages of this!!


As much as I would like to, the poly is underground, from the meter until it comes up in the kitchen, then there is about 6 inches to the first SC
 
And you said with valve no.1 (main sc) closed the meter stops.......... which kinda negates stopends on the mdpe..... can't be the mixer hot tap letting back into the cold supply cos you're running a combi and what you would have there is a loop, which once it was up to pressure the meter would stop running........ no leaks, no major pressure drop........

hmmmmmmmmmmm............

Old Balvenie time methinks.......... and another day pondering someone elses problem rather than my own!

Oh. And thanks for all your messages about me handsome visage.

I love you all too.............

I Think............
 
Last edited by a moderator:
Ooh! Ooh! Ooh! Thought of another one!

What leg is the heating filler loop sitting on? What pressure is the heating system at? Is the fill valve letting by and throwing water out the PRV?
 
Croppie's like a dog with a bone on this one! LOL. Good thunking though mate.
 
Ooh! Ooh! Ooh! Thought of another one!

What leg is the heating filler loop sitting on? What pressure is the heating system at? Is the fill valve letting by and throwing water out the PRV?

sorry, that is fed from SC 2, the only bit that is a suspect leak is from SC 3
 
You know what it is now don't you Derrick! you're on the windup now lol

Fair one, I'd do the same!
 
You know what it is now don't you Derrick! you're on the windup now lol

Fair one, I'd do the same!

I wish I was,

The gauge has shown very little drop in pressure, the meter is still turning (AND I still cant get the sink finished)

The cold feed to the bath has a gauge fitted, the hand basin cold tap is off, the WC is on, and the cistern is full
 
could you put a dye in the cistern to see if its is passing? there wouldnt be any chance that the water is just drying up? no de-humidifiers or anything?:confused:

sounds like a nightmare
 
have you isolated the cold feed to the boiler with all the stopcocks open and then checked the meter for movement? with a water meter fitted the expantion in the dhw pipe could pin hole the plate hex, with out a mini expansion vessel fitted inthe cold feed pipe to take up the expation of the dhw it could leak mains water into the heating circuit exiting out of the prv or down the condensate,just isolate cold feed to check?? long shot i know but hey, were all trying with an headline like "a real brain teaser,its got me beat"
 
Hey derrick hows about you disconnect everything on the sc3 leg and cap off , then check the flammin meter and if it still moves get a shotgun out. lol
 
I have to say thats the first thing i would have done, cut the pipe and cap it off. All this umming and arring about what it might be is ridiculous, just disconnect it and start again.
 
Status
Not open for further replies.

Reply to A real brain teaser, its got me beat in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi everyone, Could someone please explain if this set up is normal and what changed: Stopcock under kitchen sink turns off cold water supply in...
Replies
7
Views
834
Hi everyone, I turned my cold water feed off in the airing cupboard which supplies only cold water to my bathroom but it also turned the water to...
Replies
3
Views
484
Where and how does the water supply work and is there only one rising main pipe and where is it usually located? I am top floor flat, mains fed...
Replies
2
Views
596
Hello, I have quite low flow rate for my electric shower (a piddling 5L/min), and would like some tips or advice about how to solve or find the...
Replies
14
Views
894
Essaboy
E
Hi all. As the title says, I have a problem with an unvented cylinder I had installed last year where the first time I turn a hot tap on after the...
Replies
27
Views
2K
Back
Top