A

Adam10

I have an issue with a plumbed in mains pressure mixer shower. When running the shower the boiler will cycle to a very nice warm temperature around 56degC(?) and then switches off (as it is up to temperature?). The shower will then use up its reserve of warm water then start to refill it. Trouble is by the time the boiler kicks in again to maintain the temperature it has dropped to around 30 degC, and the shower feels freezing cold until it warms the water again then the cycle will start again. Roughly every 5 minuets.

The boiler is Vokera Linera 24 Boiler, recently serviced and last year had most of the major components replaced whilst trying to diagnose a different issue.

What would be the probable cause and how could I resolve this to give a nice constant flow of warm water to the shower?

Many thanks in advance
Adam
 
One of two things, a restriction in the shower head or, more likely the minimum burner pressure has not been set correctly. There is an upper and lower pressure bracket, because your shower will allow a lower flow, then the burner pressure should modulate down to prevent overheating. If the pressure has not been set low enough, then the temperature sensors will turn the burner off until it cools down...and then start up again. the effect is hot water followed by cold
 
One of two things, a restriction in the shower head or, more likely the minimum burner pressure has not been set correctly. There is an upper and lower pressure bracket, because your shower will allow a lower flow, then the burner pressure should modulate down to prevent overheating. If the pressure has not been set low enough, then the temperature sensors will turn the burner off until it cools down...and then start up again. the effect is hot water followed by cold

Ok great. Ruled out a restrictions so I'll have a look down the pressure route. Is this somthing that is fairly easy to do by hand? Anything I should be looking at in the manual? I've had a good dig around at parts in the boiler before although am I best getting an engineer out to sort?

Many thanks
Adam
 
Ok great. Ruled out a restrictions so I'll have a look down the pressure route. Is this somthing that is fairly easy to do by hand? Anything I should be looking at in the manual? I've had a good dig around at parts in the boiler before although am I best getting an engineer out to sort?

Many thanks
Adam

Don't want to be a jobsworth mate, but if you're not Gas Safe trained you can't work on a gas appliance (it breaks the law). Think u need an engineer<:[
 
Status
Not open for further replies.

Reply to Boiler Hot Water Temperature Fluctuation in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Looking for any ideas to help. I've a Heatrae Sadia Hot Water tank, heated through Oil fired boiler (working fine). A week ago I reset the air gap as I was having dripping from the pressure relief valve. Since then I've lost a lot of pressure from the hot water feed to my shower. The rest of...
Replies
8
Views
277
I live in an apartment block where generally hot water is supplied from the communal hot water cylinder and cold water to bathrooms is supplied from cold water tanks in the loft. It is a vented system. However, in a basement flat and a ground floor flat cold water supply to bathrooms is...
Replies
4
Views
595
Hello, and thanks for taking the time to read. I'm trying to work out if the idea I have is practical? The water pressure in my newly renovated house (4 bathrooms is tragic). Current set up is: A hot/cold mixer in the main ensuite which is ok as long as you don't run anything else. One electric...
Replies
3
Views
377
M
Hello, We’ve recently moved into a fairly old, fairly big detached house (i.e. fairly draughty, but not too bad by any means) with a fairly new well maintained Worcester combi boiler. We weren’t convinced the heating was working right and then got hit with a £610 energy bill for the first 6...
Replies
0
Views
257
MartinPod81
M
Hello! Im Martyn Im new here and have joined for some advice on a couple of things. Ive got an issue with a Mira mixer shower that has increasingly become harder to operate. The shower was installed before I moved into the house. Basically what happens is that I turn the shower on so there's...
Replies
1
Views
329
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock