you don't need to turn down the tank stat it must be at 60 degrees to kill bugs. it only needs moving down towards the bottom third of the tank
 
looks like the feed and vent are the wrong way round. swap them over, lower pumo below the bypass(wrong side of pump) and fir auto by pass valve. should fix problem
 
None of this is meaning much to me as I'm not a plumber myself. Is all of the advice given to fix the knocking problem only right? So what would be rough costs to get someone out to move the stat down lower (or can I do this myself?) and to sort out the bypass/valve/vent changes required? Would the work be guaranteed to stop the noise or would I pay anyway and then see if it works kind of thing? Just a rough cost estimate from someone...are we talking ÂŁ50 ÂŁ100 ÂŁ500 ?
 
A Y plan (your system, with a mid position valve) does not under most circumstances, need a bypass.

IMG_5758.JPG

As they have fitted one to the wrong side of the pump it is causing the water to short circuit with most of the water following the red line where it should follow the pink line back to the boiler. When on for CH only the bypass is cut out of the circuit and if on for HW and CH it won't effect it as much.

Close the bypass by turning the screw on the silver valve so that it is across the pipe.
You can leave the tank stat where it is. Turn it to 65 deg.
Your room stat sited upstairs is in the worst position (heat rises), and should really be downstairs. It doesn't matter what temp it reads or what your neighbours and friends set theirs at. Set it at what you feel comfortable at (and it won't be 18 unless you like wearing a jacket to watch the telly).
 
tamz has pretty much described the problems there for you. you can shut off the bypass which should sort the issue or better still resite it. yes in most cases it doesnt need a bypass as there is always a route for the water unlike an s but it is recommended
 
Thankyou! I 100% understand what you guys mean now having seen the above diagram. OK, so the chrome valve on the bypass...which way should I turn it to close it? I assume clockwise? It was at horizontal i.e. 9 and 3 O clock, and I turned it a quarter of a turn clockwise to 6 and 12 O clock and it started dripping as I turned it. It got stiff after a quarter turn clockwise so I stopped, but I think I could turn it more. Should I force it till it won't go any further or is a quarter turn enough? I don't think it is closed but not sure. Thanks all for the help so far. Also, I noticed with HW and CH on, I still think it knocks a bit. It is quietest when just CH on which would fit with info above as bypass not used then. It is def air in the pipes. Can tell by the way the pump sounds and behaves.
 
if the line on the top is in line with the water flowing its on. if its adjacent it is off, just use a slottede screwdriver to turn it the correct way
 
EDIT:

In that case then, it was already off as it was going accross the pipe before I adjusted it :(
 
Last edited by a moderator:
I just turned it 180 degrees the other way to the off position to see if it made a difference. Not sure why it leaks when I turn it. Anyway, I turned the HW on on its own and so far it has not knocked. However, I think the knocking usually occurs only when the HW first starts up having been off for a while. First thing in the morning does seem worst (6:30am), however, it does do it in the afternoon when it comes on again around 3pm sometimes. I will test it tomorrow morning and see if anything has changed. Thanks for all your help.
 
is your cold water inlet the first pipe on the flow before the pump? the second one being 22mm and going over the cistern?
 
Status
Not open for further replies.

Reply to Some advice on two different problems please? in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold...
Replies
2
Views
221
Hi everyone, Looking for a bit of advice, recently went to a job where heating was operating when called for however not for the hot water. I...
Replies
8
Views
396
Hi, I have a Worcester 28i junior boiler that has started to lose pressure, only when using the central heating. When using hot water I have no...
Replies
6
Views
266
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4...
Replies
9
Views
452
S
Hi, I seemed to have a blockage in kitchen sink. A plumber came and cleared all the pipework that is visible inside my home (there was debris and...
Replies
2
Views
160
Sonya K
S

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock