mattytheplumber

hi guys, just need some advise on this one.....

I got called to a job today and when i asked for the heating to come on the boiler fired up and the pipes round the cylinder were all hot and both sides of the pump!! I tried bleeding the rads to try drag any air out the system but this didnt work. the man said he would be happy for us to do a power flush to get rid of this problem and also any sludge in the system. i just want to know if you guys think that the flush would cure the problem.

thank a lot.:)
 
You'll need to fault find on the ch/hw elect circuit, check the programmer/stats and zone valves are functioning correctly b4 u charge for a p/flush.

Have u done any fault finding at all?
 
There is power going to the programmer and it is turning the heating on. The two port valve is working corectly too! one rad got warm closest to the boiler but that was it. so with the one rad getting warm i thought there must be a block????

He has no room stats anywhere in the house just one thermo rad valve downstairs. :confused:
 
Is the pump Circulating?

Checking for blockages or airlocks would be my next step aswell. Do u know about the fridge magnet trick when checking for chokeages?
 
fridge magnit??? no :eek: ha


The pump is running yes, and what would you advise the best way to check were the block could be??

If it is a block, witch it sound like, i assume a flush would do the job?? I know its not the most cost effective but i think the guy would like one anyway. :confused:
 
fridge magnit??? no :eek: ha


The pump is running yes, and what would you advise the best way to check were the block could be??

If it is a block, witch it sound like, i assume a flush would do the job?? I know its not the most cost effective but i think the guy would like one anyway. :confused:

Yes but is it circulating? Take the bleed screw out the pump and check it's rotating.

Take a normal fridge magnet and check it against sections of copper pipework where u suspect the blockage may be, parts of the return or maybe the cold feed, the magnet will stick to copper pipework choked with magnetite, it will not stick to areas that are not blocked. If it is completely choked in a certain area then I doubt a p/flush will clear a choked pipe on it's own, it would usually need cut out and replaced.
 
nice trick, never tried it myself. atleast you can probably say the blockage is either flow or return before first radiator. bit of a nightmare locating blockages, can see why your thinking power flush
 
Is the header tank full? Check that the ball valve hasn't got stuck. I assume that you have tried manually opening the motorised valve?
 
Taking the screw out and checking the pump is rotating is not sufficient to prove the pump is circulating properly. I have had a few cases where the impeller is worn or broken and although it may circulate somewhat it does not provide enough head.

Matty
Check the water quality and you will know if it needs a flush.
 
yes the motorised valve is working corectly and the header tank is full. The pump is working but if your saying you had cases were the blades have worn, i have spare pumps in the van so will try a new pump and see if this resolves the problem. thanks
 
Status
Not open for further replies.

Reply to rads not getting hot, but hot water is!!! in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi all I have a problem with my hot water header tank getting warm water into it from the bottom of the header tank (not the hooked...
Replies
1
Views
693
Hi - I'm a reasonably experienced DIY plumber but just can't work out why the last new rad I've installed is cold - would really appreciate your...
Replies
7
Views
669
Hi, I have a sealed system with 18 Rads/towel rads which is run by a greenstar boiler with a sealed hot water tank. I'm using a tado thermostat...
Replies
19
Views
2K
Hoping somebody can help, So, in a nutshell… Standard 90s Westbury home – condensing boiler, pump, wall thermostat, etc etc... Normal, common or...
Replies
8
Views
597
I have an old Potterton suprima boiler with a hot water tank and pump. We have hot water but no heating, the light on the boiler is showing amber...
Replies
14
Views
2K
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock