Hi all hope you can help me with my dilemma.

Scenario : 1950s built detached house in London
Approx 150 sqm Ground / 140 sqm 1st Floor / 100 sqm 2nd Floor
Double Glazing Argon Filled Low E Stuff
Pitched Roof with 100mm Celotex
Walls Cavity with insulation
6 Bedroom
5 Bathroom (3 Shower / 2 Baths)
10 Radiators ( 7 on 1st Floor / 3 on 2nd floor)
5 Towel Rails (Water Heated)
Shared Occupancy (7 Adults / 4 Children)

Typical Evening Usage : 8 Showers + 1 Bath to be taken approx 10 min each over a period of 4 hours - possibility of Bath run at same time as 2 other Showers.
Typical Morning Usage : Washing up / Washbasins / 2 Showers one after the other over a period of 2 hours.

Underfloor Heating on Ground Floor (approx 700m pipe) - covered in tile over 100m2 and 18mm wood over 40m2.

I have had 3 plumbers come in to design system..hence dilemma

Plumber 1 : 2xBoilers Keston 28 Qudos + 1x400l Unvented Tank
Plumber 2 : 1xBoiler Valliant 837 + 1x500l Unvented Tank
Plumber 3 : 1xBoiler Veissemann 200W 35Kw + 2x200l Unvented Tanks

Which of these will provide me with the most efficient system and enough water for my purpose - I also have 700m of underfloor heating to consider.

Underfloorheating only requires water @ 30 deg is there a boiler which can have such an output for 1 zone and 80 deg for another ( water tanks + radiators + towel rails ) ? Or is this not the right way to go about things - I want max condensing for efficiency ?

Is one 35kw boiler better than 2x18Kw ones? I was thinking perhaps run 1 tank and underfloor heating off one and another tank and rest of heating /rails of the other ? System would be a s-plus plan ? 4 zone Hortsmann programmer ? would it be wise to run the tanks in parallel or split 1 tank for kitchen + 2 bathrooms and the other for the remainder 3 ? How about in parallel and manually switching one off in summer when demand is not that high ?

Apologies in advance for the lengthy note but wanted to provide as much info so I could get some realistic feedback.
 
Ask 10 plumbers and you will get 10 different answers.
Personally i think plumber 1 has the best idea but i don't like Kestons (i used to mainly for the flueing, but they became a source of trouble and have a bad rep and may have improved).
A 400 litre cylinder should provide all the water you need but you should restrict the flow through the showers.
The underfloor heating water is supplied through a blending valve which can be set to whatever you require regardless of the flow temp. Get the underfloor designed for you. Manu's do it for free.
In this situation 2 boilers cascaded would be a better idea than 1.
It is too late to think about this much so these are just quick answers.
 
Thanks for the reply !

Can you explain some more about what 'cascading' is in terms of boilers ?

Also, if I went for a 2 boiler setup any suggestion on power output ? will 2 x 24kw do ?

Any mkaes to avoid i.e. keston as you have mentioned.

Any particlularly reliable boilers ? what about Worcester Bosch or Veissmen ?
 
Go for Worcester bosch,using accredited installer to give you 5 year warranty,supply heating thru low loss header, made by VA heating,(look on internet for site)HW water depends on occupency and the structure of the building to take weight.Dont over size boilers.dont use Keston unless flueing option is restricted.and it goes on.
 
I think it would be a good idea to present this to Vaillant/WorcsB/1 other technical sales dept and get them to specify - then find an installer. This is a big building and your wants are specific so it makes sense to get the manufacturers to do a bit for free.

I also have my ideas which could futher confuse things.

Whats your budget ? this is not a cheap system

centralheatking
 
Scenario : 1950s built detached house in London
Approx 150 sqm Ground / 140 sqm 1st Floor / 100 sqm 2nd Floor
Double Glazing Argon Filled Low E Stuff
Pitched Roof with 100mm Celotex
Walls Cavity with insulation
Have you done a heat loss calculation?

If not use Boiler Size Calculator. You will then have a good idea what size boiler you need just for heating.

As for hot water, it does not matter what size HW cylinder you have if the incoming mains is not able to deliver the required flow and pressure. So if you have two showers and a bath running at the same time there could be a requirement for 30 to 45 litres per minute.

You can check the flow rate at the kitchen sink cold tap using a marked bucket and a watch. If you have a garden tap straight off the mains, do the test with the garden tap closed and then with it open. The rate with the garden tap open is the important one, but the lower the difference the better. Don't forget that everything will be fed from the incoming mains - showers, baths, toilets, washing machines etc.
 
Have you done a heat loss calculation?

If not use Boiler Size Calculator. You will then have a good idea what size boiler you need just for heating.
Just done a quick calc using the above link

Assuming three rectangular floors each 15m x 10m, I got a result of approx 23kW. So how does one installer come up with a 35kW boilers?? The other two aren't far off the mark, but feeding a HW cylinder from a combi boiler is unusual.
 
I tried on some boiler sizing websites and I too got around 22kw.

But surely this is heating only ( I have been quoted 12kw as required for the underfloor heating by a supplier).

Would the 12 Kw left over from a 24kw boiler be enough for the rest 1st and 2nd floors ?

I see that 2kw is added for heating water - this sounds far too less ? and surely would mean recovery times of hours instead of minutes - I am out of my depth here so pls humour me if this is not the right thought process !

Heatrae Sadia I spoke to yesterday and they said their tanks have quick recovery as long as the boiler is powerful enough - enough means what in laymans terms ?

This still leaves me with not fully knowing if for example a Worcestor 30CDI for is going to be able to handle all the requirements ? e.g. water / heating / underfloor - all calling for heat at the same time e.g. cold mornings through winter months.
 
Central Heatking asked about budget set aside - approx ÂŁ15k including the underfloor heating
 
Viessmann can do the lot from one boiler 200-w and a correctly sized vitocell cylinder, different temps to different zones ie underfloor and rads. also weather compensated.

35kw way over sized i'd be looking low 20kw + Hot water demand

give Viessmann a call and see if the will recommend a installer in your area

Eco
 
the advatage of two boilers is your never without at least some heating and hot water and generally speaking they dont work out much more exspensive even the best boilers breakdown and usually just when you need it most
 
Thanks for all the replies and information so far - you guys are really helpful :)

I will speak with Veissmen tomorrow and find out what their thoughts are.

Just out of curiosity - 3 zones all want water at different temps albeit at the same time.

How would a boiler handle that ?

I understand system boilers have flow/return for 2 circuits i. DHW and CH so in theory one could set the DHW to 70 deg and CH to 65 ? but what about the underfloor heating - if this is tee'd off the heating circuit with a zone valve - boiler will still send down water at 65 deg only to be dropped down to 30 deg by thermo valve in underfloor heating manifold for its usage. This would be inefficient as return to boiler is no where near the 54 deg mark which is ideal for condensing ? and also boiler unnecessarily running at higher temp than what is actually needed ( if only underfloor heating was calling ).

Does this mean that in order for the boiler to work effciently and in condensing mode - CHW and Underfloor heating should be on both together or CH only and not under floor heating on its own - what impact does the much cooler circuit from the underfloor heating have when combined to the return from the CH circuit - would this not also bring down the temperature from the desired mid 50' degC ? e.g mixing hot (55deg) with cooler water (27deg) ? and again not encouraging boiler to condense ?

I am just trying to get my head around this so pls be patient with my questions ..
 
the Viessmann 200 can do different zones and temps at the same time :)

you can run the underfloor direct from the boiler with no mixing valve. if you use their unvented cylinder it does not need a seperate 2 port valve, the boiler controls the hot water temp.
 
Last edited by a moderator:
A Viessman or no other boiler can supply water at different temperatures for different circuits at the same time. What it does is an inbuilt divertor valveis fitted and some smart electronics ramp up the power when the valve opens. That puts the full output to the water when required then cuts back to the other circuit when satisfied.
A 4-500litre cylinder will have a coil rated at around 30kw. To give recovery rates that are anywhere near what a manufacturer quotes the full boiler output has to go through the coil ie divertor valve and the flow temperature would have to be around 75° to achieve this.
2 boilers might be better than one for reasons among others previously stated by steve.

Speak to the manu's and see what they recommend rather than us lot throwing different things in the mix. They will design and recommend the best system for you. As i said 10 guys will give 10 different answers.
Viessmann are good boilers btw.
 
A Viessman or no other boiler can supply water at different temperatures for different circuits at the same time. What it does is an inbuilt divertor valveis fitted and some smart electronics ramp up the power when the valve opens. That puts the full output to the water when required then cuts back to the other circuit when satisfied.
A 4-500litre cylinder will have a coil rated at around 30kw. To give recovery rates that are anywhere near what a manufacturer quotes the full boiler output has to go through the coil ie divertor valve and the flow temperature would have to be around 75° to achieve this.
2 boilers might be better than one for reasons among others previously stated by steve.

Speak to the manu's and see what they recommend rather than us lot throwing different things in the mix. They will design and recommend the best system for you. As i said 10 guys will give 10 different answers.
Viessmann are good boilers btw.

Take tams advice
Ps ÂŁ15000 is not a big budget for what your looking for in London
 
But surely this is heating only ( I have been quoted 12kw as required for the underfloor heating by a supplier).
It does not matter how the heating is provided - underfloor or radiators - the amount of heat is the same. Assuming your house is 10m x 15m, the approximate heat losses for each floor (ignoring hot water) are:

Ground floor - 8.13kW
First Floor - 5.28kW
Second Floor -7.06KW

I would query how the third supplier gets 12kw for underfloor.

Don't forget that these figures are based on an outside temperature of -1C and room temperature of 21C. If you want to use different figures, it proportional to the difference. The difference is currently 22 degrees (21-(-1)) so if you want to allow for -5C outside and 23C inside the difference is 23-(-5) = 28 degrees. You would then increase the above figures by 28/22 to give the new requirement.

I see that 2kw is added for heating water - this sounds far too less ? and surely would mean recovery times of hours instead of minutes
This does not mean that you have only 2kW available to heat the water, you have the whole of the boiler output available if necessary. Assuming a 22kw boiler including the 2kW, if it was so cold outside that it took 20kW to heat the house, then you would have only 2kw for the cylinder. But that's exceptional, most of the time the heating will be much less than 20kw so more is available for hot water.

There is an easy way round this: heat the water at separate times from the house. This can be done in two ways - separate times and/or giving hot water priority. Separate times is ideal for overnight heating of the water. Hot water priority just means that if, during the day, the hot water needs to be heated, the circulation is stopped through the central heating and all the boiler output is directed through the hot water cylinder. If you have a fast recovery cylinder this may only take 15 or 20 minutes.

This still leaves me with not fully knowing if for example a Worcestor 30CDI for is going to be able to handle all the requirements ? e.g. water / heating / underfloor - all calling for heat at the same time e.g. cold mornings through winter months.
It will certainly be large enough for central heating (rads and underfloor). As for water, as you will have a HW cylinder you are not heating the water instantaneously, as with a combi boiler. Provided the cylinder has enough stored hot water to satisfy the maximum instantaneous requirement before the water temperature drops too far, say 10-15degC, there should be no trouble. The real problem is whether there is enough flow and pressure to meet the worst situation. Have you checked the flow rate?

Did you know that, as your floor area exceeds 150m² total floor area, you have to set up separate more than one heating zone with individual time and temperature control for each zone? I would suggest a separate zone for each floor.
 
ok update...

I spoke to Technical at Veismann and they have advised on the following.

Vitodens W200 30Kw ( he said 35kw is overkill)
Vitocell 300-300l or 500l tank
Weather Compensation Controller
Devicon addition
Thermovalve

Basically he suggested zoning off into 3 areas.

1. Hot Water Tank
2. Rads and Rails ( 10 Rads and 5 rails )
3. Underfloor Heating

Devicon will include divertor/controller/pump instead of pump/thermovalve in underfloor system. This will supply water @ 30 deg for the system not 65 deg and then have the thermocouple bring down to 30deg. This will improve efficiency - there is a safety valve (not sure of its name) this will shut off circuit if the water exceeds 35deg to protect underfloor circuit.

Weather compensation allows control of temp+flow into heating + water + 2 additonal circuits depending on how many devicons you have connected. It also has a sensor fitted to North Face of house to increase/decrease power from boiler depending on weather.

Heat exchanger guaranteed for 10years.

System does sound ideal - can I get some honest opinions on this pls now that I have some feedback from manufacturer?

Personally I am convinced with the system except for the necessity to but unvented tank from Veismann too - I was thinking of Telford unvented Tempest/Tornado indirect tanks. Can't see any compatibility issue as tanks just have a temp sensor right ?

Also I read somewhere that if buying get a Solar Ready Twin Coil cylinder, even if you don't have Solar Power, connecting both circuits to flow/return will provide more efficiency over same sized single coil cyclinder... is this true or just a myth ?? as always appreciate any feedback guys :)
 
Stick with the viessmann cylinder its a lot easier to install and control from the boiler.

You will have the dogs dangly bits of a system

Eco

Ps if thinking of solar in the future get the viessmann solar cylinder and the boiler controls this also.
 
Last edited by a moderator:
Hi I thought I'd give an update ..all fitted. System I went for in the end was Worcestor 30CDI Regular x 2, Telford
Tempest Unvented 400l tank, honeywell 2 port valves, grundfos alpha A rated pumps, Honeywell Thermostat Timers, low loss header, 2 expansion vessels one for tank one for system, 2 x spirotraps to catch any rubbish in system.

There is no provision for external weather compensator with my Honeywell clocks so this has been left out.

I have had some fun trying to setup the pumps / boilers to work in the most efficient way as plumber did just the pipework and my elctrician did the wiring.

Although I am fairly technical I can't really get my head around the different pump settings. There are 7 settings on each pump. Constant speeds 1, 2, 3 and then PP1,PP2, CP1,CP2. Constant speeds are obvious to understand but not sure about the Constant Pressure / Proportional Pressure ones. When are these suitable etc ?

I have 2 x 15/50 pumps setup as shunt pumps for the boiler / low loss circuit. Each one is connected to its own boiler and currently these are set to PP2. One of these also feeds the towel rad circuit which is 15mm throughout and has 5 towel rads placed on both the 2nd floor and first.

I have a 15/50 for the ground floor UFH circuit supply set at PP2.
2 x 15/60 for the 1st/2nd floor heating circuits set at PP2.
1 x 15/60 for the Hot Water Tank set at PP2.
1 x 15/50N secondary return set at PP2 with the night setback switched on.

One thing I have noticed is that if I set the shunt pumps to a slower speed the circuit does not heat up.

I am not sure if this is the most efficient setup for the pumps and open to any suggestions ?

Also, am struggling to get around how to set the boilers up in the most efficient way so that when the demand is not that great only 1 comes on and when max demand is required i.e heating circuits + water then both come on.

I have tried setting 1 boiler to heat temp 3 and the other to max but still even if just UFH is calling both boilers fire up which means approx 40kw of power for 12kw demand ? The circuits are all calling both boilers.

I will post some pictures once I get a chance.
 
Status
Not open for further replies.

Reply to Whole House Plumbing advice / help desperately needed !! in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up...
Replies
2
Views
250
PSxxxxxx
P
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4...
Replies
9
Views
409
Hi everyone, Looking for a bit of advice, recently went to a job where heating was operating when called for however not for the hot water. I...
Replies
8
Views
356
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold...
Replies
2
Views
182
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock