Scenario is a restaurant with toilets on the lower ground floor, svp goes up to third floor offices and away into the roof somewhere. 2 cubicles and basins in ladies, 3 connected urinals and 1 cubical in gents. Problem is pans backing up and not clearing. I've seen the gents back up just by having clean cold water poured in from a bucket and thought the problem was air related. I checked with building control about placing a dirgo valve so low in the system and they ok'd it but apparantly it hasn't solved the problem. We've checked the horizontal soil pipe and its clean and appears to fall the right way, so can anyone scratch an idea off their forehead please?

Cheers

Chris
 
The problem with a dirgo is its an air admittance valve for releasing a vacuum. You seem to have a back pressure problem not a vacuum problem.

Any poly bags gone down the drain?

I would inspect the outside manhole first off, and work back to wc's.

If nothing, then it could be back pressure which unfortunately you may need to ventilation the drain through the soil pipe. Not easy and got to be outside or joined back into stack above highest fitting. That is of course supposing the stack is vented and not just fitted with another dirgo in the roof space.

Good fortune
 
thanks Bernie, you make a good point re the dirgo valve.

to test that out, can we simply take it off and leave the pipe open for an hour or so to check if the problem still occurs?

The problem has been taxing the locals for months and the pipework has been rodded twice to no avail.

Re your last paragraph, are we trying to create a positive flow into the stack with the additional ventilation, rather than simply allowing air to be drawn in when needed?
 
The problem with a dirgo is its an air admittance valve for releasing a vacuum. You seem to have a back pressure problem not a vacuum problem.

Any poly bags gone down the drain?

I would inspect the outside manhole first off, and work back to wc's.

If nothing, then it could be back pressure which unfortunately you may need to ventilation the drain through the soil pipe. Not easy and got to be outside or joined back into stack above highest fitting. That is of course supposing the stack is vented and not just fitted with another dirgo in the roof space.

Good fortune

so your saying it could be due to a 'dirgo' in the upper floors creating mass air intake/.? so it will need investigating the complete stack system.
 
Sorry Redsaw, are you querying what Bernie said or asking me a question?

Chris
 
Sorry Redsaw, are you querying what Bernie said or asking me a question?

Chris

yeh, but no but.

saying the soil could be pressurising with air from the upper floors pushing air block from draining toilet in basement.
like bernie says, it needs air out-let not intake in the lower flors, proberbly?

i would try to check the entire stack if poss.
 
ok, I understand. The easy bit's writing it eh? I can't see how we'd get another vent up 3 floors. (That'd be why Bernie said outside, I suppose).
If there is a dirgo valve on the top of the stack, is it any good to remove it?
 
Hi. If there is a a vale fitted at the head of the stack, i certainly would remove it and monitor results of lower floor performance. If it does the trick extend system to terminate to the atmosphere in the form of a vent. Good Luck
 
Status
Not open for further replies.

Reply to Restaurant toilet problem in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
344
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m planning to pour a 100mm deep concrete patio on 100mm hardcore. In order to achieve the same final height to line up with the rest of the patio, I...
Replies
6
Views
245
I was stupid enough not to check the position of the pipes under the tiles when installing a toilet and drilled right through the center of a 16 mm copper water pipe. I exposed the pipe by removing a ~30cm section of the plastic sleeve and a ~10 cm section of the pipe around the hole. Several...
Replies
0
Views
190
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock