291
hi as above baxi due tex needs toping up every other day, PRV not passinf nothing running down the con pipe, in a bunglow so all pipe are eather in the loft or in the wall nothing under ground, any one any thoughts l;ost for what to check next.
 
isolate the boiler via the isolation valves leave the boiler off for one day if pressure holds its not the boiler
 
Is the auto air vent in boiler passing?
Slight leak on a lockshield valve?
Automatic air vents in attic leaking?
Because it needs topping up every other day , it sounds small and evaporating on hot pipe work. IMHO
 
Status
Not open for further replies.

Reply to baxi due tec lossing water in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Baxi Duo Tec 28 Hot Water Issue. Hi, I have a Nazi duo tec 28. I’m having an issue with my hot water. If the CH is on, and I turn on the hot water I get warm/tepid water provided the HW temperature dial is set about 3o’clock. If it’s set any higher, I get an E28 fault, and my water goes cold...
Replies
1
Views
692
Deleted member 120897
D
Hi, Just checking I'm not talking rot. Today I visited a house with a Baxi 228 combi boiler. The technical spec for the DHW output is shown in the image. Boiler was installed 27 months ago. Baxi is claiming 13.3 litres @ DT 30. I set the boiler DHW temperature to a high setting. I was...
Replies
6
Views
1K
We need an urgent advice, we have a gravity water system and we are in a middle of loft conversion. We are adding an en-suit in loft and prefer to have a good water pressure there. What we want, is to either be able to run multiple showers at once, or if one person is having a shower, other...
Replies
2
Views
994
M
Hello! Overview: typical 3 bedroom 1930's semi-detached property. Had a single storey ground floor extension circa two years ago, during which time the boiler was replaced with an Ideal Independent and moved from back bedroom into the loft above. Problem: since the boiler was replaced and...
Replies
1
Views
651
Hi - I'm hoping someone can help with some advice. Ahead of some renovation work, we had a 50 year old old floor standing boiler in the utility room removed and a new Worcester Bosch Greenstar 24Ri wall mounted in the garage. Aside from being old, the original boiler worked perfectly. A full...
Replies
2
Views
716
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock