I've not seen this type of filing loop? is it an old type thingy or some form of improvisation?
also, the electric power cable seems to have a dodgy connection and is going behind the pipes...is this ok as i would personally never do that as it's next to pipes that become very very hot..

oh, and the condensate trap discharge pipe is what seems to be like from a washing machine

thank you.

(i'm working towards my ACS)

IMG_20140224_155108.jpg
 
The terminal strip is a shocker.... The quick fill looks ok as I presume the longer of the valves has a built in check valve.
Wire looks to be too close to the gas pipe(should be 25 mm +).
Where's the safety valve pipework?
 
What's a safety valve pipework?
Which If any unsafe situation would the wire be classified as?
 
I'd class the cable as NCS, but the terminal strip is shocking, should be wired properly or hidden in a junction box.
The safety valve pipework may also be known as the pressure relief valve pipework or safety blow off?
 
If the condensate hose is not the manufacturers proper hose then that's another score against it.
 
What boiler is it, as it looks a bit like a potterton.
 
the boiler is a Baxi combi 105he. these were discontinued back in 2007.

so if the wiring is NCS and the condensate trap too, does that mean it would equate to AR?
 
the boiler is a Baxi combi 105he. these were discontinued back in 2007.

so if the wiring is NCS and the condensate trap too, does that mean it would equate to AR?

No - Ncs no matter how many are just ncs

been a few years but 2 AR's on a open flued appliance is upgraded to id, that's the only time you 'add' them together to go to the next level. Somone please correct me if I'm wrong ;-(
 
Last edited by a moderator:
No - Ncs no matter how many are just ncs

been a few years but 2 AR's on a open flued appliance is upgraded to id, that's the only time you 'add' them together to go to the next level. Some please correct me if I'm wrong ;-(



You are correct
 
There's no way I would walk out the door and leave that cable like that it would take 10 min to run a new cable from the spur back to the boiler
If the landlord agree to it of course otherwise I would id the boiler
 
can you classify something external from the boiler and its parts under the unsafe sitituations proceedure? or does it come under another part some other regulations
 
Last edited:
No - Ncs no matter how many are just ncs

been a few years but 2 AR's on a open flued appliance is upgraded to id, that's the only time you 'add' them together to go to the next level. Somone please correct me if I'm wrong ;-(
You are incorrect.
Two or more NCS's relating to open flued appliance flue & ventilation may be upgraded to AR if you deem them serious enough. It is at your discretion.
 
There's no way I would walk out the door and leave that cable like that it would take 10 min to run a new cable from the spur back to the boiler
If the landlord agree to it of course otherwise I would id the boiler
Why would you ID this?
 
Would u leave a live cable exposed like that cause I wouldn't it's up to u at the end of the day .
 
You are incorrect.
Two or more NCS's relating to open flued appliance flue & ventilation may be upgraded to AR if you deem them serious enough. It is at your discretion.

I was always told 2 ncs on either flueing or ventilation would make it AR nothing about just on open flued.
 
Would u leave a live cable exposed like that cause I wouldn't it's up to u at the end of the day .

You advise the responsible person that there is an electrical fault that needs to be addressed urgently and put it on your paperwork. Its not a gas fault so you cant use gas unsafe procedures to turn off the boiler. If you are an electrician as well I would imagine you could through electrical regs.
 
anybody notice the weird looking joints on the flow and the gas? no way are they 22mm sockets
 
You advise the responsible person that there is an electrical fault that needs to be addressed urgently and put it on your paperwork. Its not a gas fault so you cant use gas unsafe procedures to turn off the boiler. If you are an electrician as well I would imagine you could through electrical regs.

Like I said its up to the person what u do
To be honest I would just put it right for the sake of a bit of cable before I left take 5 10 min and a clear conscience to boot
 
I was always told 2 ncs on either flueing or ventilation would make it AR nothing about just on open flued.
Are you going to AR a room sealed appliance for flue term too long, not sealed round wall and no terminal guard?
Unless anything has changed in 4 years from my last ACS applies to open flue flue and vent issues only.
 
Are you going to AR a room sealed appliance for flue term too long, not sealed round wall and no terminal guard?
Unless anything has changed in 4 years from my last ACS applies to open flue flue and vent issues only.

It is still at your discretion. I resat mine 2 years ago and I spoke to the gas safe bloke about it as my thing was no terminal guard and flue hole not sealed so how can I AR that and thats when he said about your discretion.
 
It is still at your discretion. I resat mine 2 years ago and I spoke to the gas safe bloke about it as my thing was no terminal guard and flue hole not sealed so how can I AR that and thats when he said about your discretion.
I would be AR'ing every other boiler if this applied to room sealed.
The discretionary multi NCS elevated to AR applies to open flue only as a number of flue & vent NCS's may amount to something more dangerous.
If I am incorrect I really need to back to basics.
 
I would be AR'ing every other boiler if this applied to room sealed.
The discretionary multi NCS elevated to AR applies to open flue only as a number of flue & vent NCS's may amount to something more dangerous.
If I am incorrect I really need to back to basics.

Seems I was wrong just double checked.
 
You really had me starting to doubt myself for a second.:wink5:

I might have to change my training center and get my gas safe inspector sacked as both of them have told me that 2 ncs make an AR (With discretion)

Although if you came across a room sealed flue terminal which was too close to an internal corner and too close to an opening. The day you test it and do a room CO its a still day and has no problem passes all tests, You know that with even the slightest wind in the correct direction that it will fail badly but on that day it passes that then would have to be 2x NCS would be a pass? To me it should be any flue as all boilers have the potential to kill if installed incorrectly or in a bad state.
 
I might have to change my training center and get my gas safe inspector sacked as both of them have told me that 2 ncs make an AR (With discretion)

Although if you came across a room sealed flue terminal which was too close to an internal corner and too close to an opening. The day you test it and do a room CO its a still day and has no problem passes all tests, You know that with even the slightest wind in the correct direction that it will fail badly but on that day it passes that then would have to be 2x NCS would be a pass? To me it should be any flue as all boilers have the potential to kill if installed incorrectly or in a bad state.

Haha don't sack anyone, listen and understand the regs, there has never been a directive to count two or more NCS on a RS appliance as AR, NEVER
it has only ever applied to OF appliances where the NCS are linked/related, the best example being a vent fault and a flue fault
Conversely if you have an OF boiler with a vent fault and a 13amp fuse in the spur don't make the boiler AR because the NCS's aren't going to affect the way the other one performs
 
I was always told 2 ncs on either flueing or ventilation would make it AR nothing about just on open flued.

So a RS boiler with a clip missing from a flue extension and and undersized compartment vent would make this RS boiler AR
 
So a RS boiler with a clip missing from a flue extension and and undersized compartment vent would make this RS boiler AR

I have already pointed out that I was wrong in an earlier post.

I have always used discretion and explained what needs doing not necessarily AR a boiler if it doesn't deserve it.

When I did my course last the blokes quote was " if there's no terminal guard then you only need to find 1 more NCS then it is AR" (might not be word for word but that was pretty much what he was on about) how many open flued appliances need terminal guards? So he was obviously on about room sealed appliances as well.

I have checked the unsafe procedures which was why I said I was wrong.
 
I have already pointed out that I was wrong in an earlier post.

I have always used discretion and explained what needs doing not necessarily AR a boiler if it doesn't deserve it.

When I did my course last the blokes quote was " if there's no terminal guard then you only need to find 1 more NCS then it is AR" (might not be word for word but that was pretty much what he was on about) how many open flued appliances need terminal guards? So he was obviously on about room sealed appliances as well.

I have checked the unsafe procedures which was why I said I was wrong.

always said gas was a bit of a minefield.

i always thought no terminal guard on rs boiler would be AR alone, same for flue not sealed in
to outside brickwork
 
You cannot classify Electrical defects as NCS, AR or ID. They are all Coded faults 1 being the most dangerous 5 being less severe. On Gas 2 AR's is AR. ID is ID, 2 NCS's can be lifted to AR depending on engineering judgement, as Kirk has said.
 
You cannot classify Electrical defects as NCS, AR or ID. They are all Coded faults 1 being the most dangerous 5 being less severe. On Gas 2 AR's is AR. ID is ID, 2 NCS's can be lifted to AR depending on engineering judgement, as Kirk has said.
I said it first!:smug2:
And applies to open open flue only in case anymore confusion.
 
While we are talking about electrical issues with gas.
A boiler with no earth is potentially dangerous and BG/SG would classify it as AR.
Any input?
 
While we are talking about electrical issues with gas.
A boiler with no earth is potentially dangerous and BG/SG would classify it as AR.
Any input?
A code 2 fault then under the electrical regulations for a potential danger.
 
Here's another photo from the same property...what would you classify the overflow and pressure relief pipe as? i'm thinking the pressure relief should be AR as that can cause scolding if a person was to walk past?
IMG_20140224_154943.jpg
 
Not as per MI, or contravention of building regs ( if we look in there it will describe how plumbing needs to be fitted safely etc) NCS, AR & ID are gas classifications, only BG have decided in their wisdom to attach these classifications to plumbing issues
 
Not as per MI, or contravention of building regs ( if we look in there it will describe how plumbing needs to be fitted safely etc) NCS, AR & ID are gas classifications, only BG have decided in their wisdom to attach these classifications to plumbing issues

Seems at last someone knows his regs :)
 
PRV not terminating correctly is NCS, isn't that in the regs?
 
Also, if the joints are flared on the gas pipe, isn't that ID?
 
Not as per MI, or contravention of building regs ( if we look in there it will describe how plumbing needs to be fitted safely etc) NCS, AR & ID are gas classifications, only BG have decided in their wisdom to attach these classifications to plumbing issues

I would say it's ncs as you haven't installed it to the MI and installing an appliance to the MI a requirement of GSIUR !
 
Status
Not open for further replies.

Reply to NCS - filling loop and electric cable, condensate discharge pipe? in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi folks, I have a problem with an airlock forming every time the overhead tank becomes empty. Even when I fill the overhead tank to the brim...
Replies
6
Views
864
A number of issues have been raised from a boiler replacement. Boiler not operating and with no pressure. Tile damage Sprawling pipe layout in...
Replies
21
Views
5K
Now sorted... don’t bother reading this stupid long post. Hi, I’ve got a bit of a head scratcher here and wondered what you guys would make of...
Replies
7
Views
2K
Sharp Point
S
E
  • Locked
Hi, Hopefully someone can offer some advice. Recently we had a new Combi Boiler fitted (a Worcester Greenstar 28 Condensor Boiler). The engineer...
Replies
23
Views
8K
eimaj12000
E
G
  • Locked
Hi all. Not sure if this is the right place for this (please excuse me as I am new to the forums) but im having ongoing problems with out...
Replies
7
Views
6K
Dotty
D
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock