bassmonster

Plumbers Arms member
Plumber
Gas Engineer
Messages
562
I've not seen this type of filing loop? is it an old type thingy or some form of improvisation?
also, the electric power cable seems to have a dodgy connection and is going behind the pipes...is this ok as i would personally never do that as it's next to pipes that become very very hot..

oh, and the condensate trap discharge pipe is what seems to be like from a washing machine

thank you.

(i'm working towards my ACS)

IMG_20140224_155108.jpg
 
The terminal strip is a shocker.... The quick fill looks ok as I presume the longer of the valves has a built in check valve.
Wire looks to be too close to the gas pipe(should be 25 mm +).
Where's the safety valve pipework?
 
I'd class the cable as NCS, but the terminal strip is shocking, should be wired properly or hidden in a junction box.
The safety valve pipework may also be known as the pressure relief valve pipework or safety blow off?
 
the boiler is a Baxi combi 105he. these were discontinued back in 2007.

so if the wiring is NCS and the condensate trap too, does that mean it would equate to AR?
 
the boiler is a Baxi combi 105he. these were discontinued back in 2007.

so if the wiring is NCS and the condensate trap too, does that mean it would equate to AR?

No - Ncs no matter how many are just ncs

been a few years but 2 AR's on a open flued appliance is upgraded to id, that's the only time you 'add' them together to go to the next level. Somone please correct me if I'm wrong ;-(
 
Last edited by a moderator:
There's no way I would walk out the door and leave that cable like that it would take 10 min to run a new cable from the spur back to the boiler
If the landlord agree to it of course otherwise I would id the boiler
 
can you classify something external from the boiler and its parts under the unsafe sitituations proceedure? or does it come under another part some other regulations
 
Last edited: