Hi,

I'm hoping someone has had this problem before and solved it and can help...

I've a combi boiler and when I switch on the hot water from any of the taps in the house everything seems to work fine. Water starts to flow and warm up but after a few seconds when the water is hot the flow rate drops off and if I don't open the tap more the combi will switch off. If I open the tap a bit more the hot water will continue. If I open the hot water tap fully then I only ever get cold water.

Anyone seen this sort of behaviour and know how to cure it?

Any help appreciated.
uk-Pedro
 
I can only, think that the domestic hot water heat exchanger, is blocked.
But don,t take my word.
Look at my username, thanks.
 
HI, Alanc, the diverter valve would not reduce flow??????
I assume.
 
Hi,

I'm hoping someone has had this problem before and solved it and can help...

I've a combi boiler and when I switch on the hot water from any of the taps in the house everything seems to work fine. Water starts to flow and warm up but after a few seconds when the water is hot the flow rate drops off and if I don't open the tap more the combi will switch off. If I open the tap a bit more the hot water will continue. If I open the hot water tap fully then I only ever get cold water.

Anyone seen this sort of behaviour and know how to cure it?

Any help appreciated.
uk-Pedro
help if you include some detail of the boiler make model etc
 
If your diaphragm is pin holed then the switch can slowly close/open causing flow changes at outlet.
 
If your diaphragm is pin holed then the switch can slowly close/open causing flow changes at outlet.
if you say so but ive never seen that

Hi,

I'm hoping someone has had this problem before and solved it and can help...

I've a combi boiler and when I switch on the hot water from any of the taps in the house everything seems to work fine. Water starts to flow and warm up but after a few seconds when the water is hot the flow rate drops off and if I don't open the tap more the combi will switch off. If I open the tap a bit more the hot water will continue. If I open the hot water tap fully then I only ever get cold water.

Anyone seen this sort of behaviour and know how to cure it?

Any help appreciated.
uk-Pedro
i think its the taps that are dropping back and closing the flow down as your setting them to only slightly open
try opening the tap full and closing the main into the boiler to get temprature right
 
Last edited:
Its got to be a blockage at the plate to plate heat exchanger or direct H/E depending on what sort of combi you have. Never heard of a diverter causing this though? Could be wrong, after all we are all learning!!

Just read your post again (must read more carefully) If the flow at your taps doesnt slow down then there could be other issues such as a diverter valve or thermistor. Could you let us know what model you have?
 
Last edited:
Hi, is this only happening with one tap or all, have you got the correct flow rate when the taps are fully open to suit the make and model of combi . ? Rod

Hi, i think steve is right it,s easy to get to deep to quickly, Rod.
 
Last edited by a moderator:
I think steve is right too. I seen this prob many times especially on old taps of large bore.
If the hot tap has a rising spindle this can stick when it heats up and effect flow drastically.
Best fix is get an engineer to fit a flow reducer to the cold feed, rated as per boilers spec. This will control the flow of water through the boiler, then any tap can be opened fully and only good DHW will come through - it will be a little slower but at least its hot!!
Changing the taps alone could improve the situation a little.
 
If your diaphragm is pin holed then the switch can slowly close/open causing flow changes at outlet.
id love to hear you explain how a divertor valve can alter the flow of dhw seeing as the dhw doesnt pass through it try it next time your infront of a boile take the water section of and push the divertor back and forth see if it affects the flow
 
Steve, i think its all the taps that are affected so might not be the taps unless its a big coincidence.
 
Thanks for all the posts.

Sorry for not putting the combi details on but it is a Glow-worm Compact 100e.

Stevetheplumber: The taps are new as I replaced them hoping that would cure this issue... I'm opening the taps enough to get splashed by the water at the start but as soon as the water gets up to temperature then I only get a trickle unless I open the tap some more. What do you mean by "closing the main into the boiler"? Is there a tap I need to fine tune to get the right amount of water flow into the boiler?


Rod_A: This is happening to all hot taps - which were replaced in the hope of fixing this issue.

Beeline: I'd rather not restrict the water going into the boiler if I can avoid it but if that's my only option then I'll take it.

Thanks for all the suggestions so far.

Regards,
uk-Pedro
 
Hi you may need to check if the right flow restricter is fitted in the mains to the combi as they can alter the flow rate a diverter valve will not affect the flow it will only affect the temp have you always had this problem
 
Last edited by a moderator:
Is the consensus to fit a flow restrictor on the boiler supply pipe?

Thanks,
uk-Pedro
 
Last edited by a moderator:
Is the consensus to fit a flow restrictor on the boiler supply pipe?

Thanks,
uk-Pedro
just close the inlet valve till it delivers the flow it says in the manufacturers instuctions with the tap full open the check temperature against the spec if at the correct flow rate your not getting the correct temperature rise then you will know there something amiss with the boiler which will then need to be checked to see if its burning the correct amount of gas for that you will need a gas safe engineer unless you know how to rate an appliance from the gas meter it can be done with out opening the boiler so if you google it im sure you will find instructions and relevant info for your boiler this is the only way to test changing parts haphazardly will be exspensive
 
Hi all, really interesting post.
I am on the trail, that say the dhw heat exchanger was corroded, then on mains water pressure, no fault would be present.
If you call for heat, on a corroded exchanger, then the internal construction may compress, and reduce the flow and cause the over-heat stat too operate.
Just a theory!
THANKS.
 
Hi all, really interesting post.
I am on the trail, that say the dhw heat exchanger was corroded, then on mains water pressure, no fault would be present.
If you call for heat, on a corroded exchanger, then the internal construction may compress, and reduce the flow and cause the over-heat stat too operate.
Just a theory!
THANKS.
first rule of plumbing KISS KEEP IT SIMPLE STUPID nine times out of ten its going to be something simple the same faults and problems time after time so always do the basics before getting into more exotic faults and theorys

incase you take offence at kiss im not calling you stupid its just a good rule to remember
 
Thanx, steve good advice.
No offence takin.
Just thought, I would offer that !:)

Damm, I cannot post a smiley!
 
Last edited by a moderator:
hi, regards flow adjustment ,the older combi,s had an adjustment srcew on the body of the divertor valve this slowed the water down passing through the dhw h/ exchanger which did not affect the noise level, you might find that closing down a ball type isolating valve on the incoming main will make a [mains pressure noise though the boiler and system when hot water is drwn off ] ROD.
 
Last edited by a moderator:
I've now run a test and think there may be a problem with the boiler.

According to my boiler manufacturer the flow rate I should be getting is below:
Glow_Worm_Compact_100e_Flow_Rate_Diagram.gif


In the test I did, the temperature difference was 36.8C and it took 1:47 minutes (1.78) to fill a bucket with 6.4L of hot water. This seems to equate to a flow rate of 3.6L/min. At the temperature difference I measured I should have got around 13L/min but instead got 3.6L/min. This all assumes my calcs are correct...

Can anyone suggest which bit of the boiler to check? I live in a hard water area so this may be due to that but since I'm a newbie to boilers I'd appreciate your input.

Thanks again.
uk-Pedro
 
hi, back to the plate heat exchanger i think not alot else to look for. Rod
 
HI, payney just out off interest, how come it would take an enginneer 5mins, too sort out, if you are one, and still have not told the OP, what the problem may be?
Don,t want to sound, in conflict.
Just interested!:)
 
HI, payney just out off interest, how come it would take an enginneer 5mins, too sort out, if you are one, and still have not told the OP, what the problem may be?
Don,t want to sound, in conflict.
Just interested!:)

Yes i am a breakdown engineer and a very good one at that thanks! People on here are all trying to help but unless you are there with the boiler in front of you its hard to tell the guy what needs doing as there are a procedure of checks to go through! I personally am not an engineer that walks into a property without tools and says oh yes its your Plate to plate or its your filter blocked on the cold inlet etc etc! When i order a part it is 100% the CORRECT part!! And i dont order 3 or 4 parts just to be sure!! Tell me do you honestly think if you were called to this job you couldnt diagnose it in say 20 mins???
 
plate heat exchsanger would be my long distance diagnosis as well
why doesnt op just call an engineer
the best you can hope for on the net is a guide the problem being being in front of the appliance makes all the diff
did a vaillant same thing took out old dhw exchanger didnt seem blocked at all but it was
boiler work cannot effectivley be done over the net as part b works with part c that tells part d so you have to physically get in there to check things
 
Last edited by a moderator:
the section of the mis youve primted is the central heating pump chart you need the dhw output
 
Thanks for your help guys.

The reason I'm on here is to try and see if what is wrong with my boiler is easy to fix and if it is and it's safe, I'll have a go myself. If it's something complicated or if I deem it unsafe to have a go then I wont. At the end of the day it's my choice if I want to try and fix something myself or not, and it's everyones choice if they reply with helpful information or not and in general people do.

If something is easy to diagnose in person then it shouldn't be any harder to diagnose over the internet with enough explanation but it's up to the individual person helping if they want to take the time and effort to explain or not. Like payney1974 says, there are procedures to diagnose something. These procedures aren't known by me or your average end user but they can be followed by most people.

Anyway, thanks for the help.

Regards,
uk-Pedro
 
HI, PAYNEY, I have no doubt you are an engineer, but I do doubt, you can diagnose a fault, 100 per/cent correct?:)
 
HI, PAYNEY, I have no doubt you are an engineer, but I do doubt, you can diagnose a fault, 100 per/cent correct?:)
none of us is ever a hundred per cent right learning but if youve been fixing boilers for a few years you can normally be right 98 per cent of the time
and if you know the =make and model you can often narrow it down before you even see the boiler as same boiler have same faults
 
HI, PAYNEY, I have no doubt you are an engineer, but I do doubt, you can diagnose a fault, 100 per/cent correct?:)

YOU NEVER answered me! Could you not diagnose this fault in 20 mins ? If you are an apprentice i apologise but you do seem to be taking the p*** now a little!
 
NO, need too get shirty payney, all I sayin very hard too diagnose 100% correct, first time.
After all you offered, four reasons that may be possible.
You can shout, if you wish.
Not an apprentice.;)
 
NO, need too get shirty payney, all I sayin very hard too diagnose 100% correct, first time.
After all you offered, four reasons that may be possible.
You can shout, if you wish.
Not an apprentice.;)

Your not listening! Ive offered four things that it could possibly be, in front of the boiler it would take an experienced engineer 10 mins max to diagnose which one. When you turn on a hot tap on a combi system and the pressure is good but then slows down on every dhw outlet in the property its obviously a blockage of some sort (do you at least agree with that?). When you turn off all dhw outlets eventually the pressure at the outlets will equalise with the mains pressure (Thats why it seems ok at first) then as soon as a outlet is opened the pressure is reduced due to the blockage.( sorry i cant put it any simpler than that) At along distance guess (and thats all it is, a guess) it would be plate which is so easy to check you can just whip it out fill with water and then hold it vertical, the flow rate on ch side should be exactly the same as dhw side (thats a tip just for you learning:D) . As ive said before we are just trying to help but it is very hard to diagnose correctly over the Internet, have you added anything worthwhile to this thread or do you just want to talk down to more experienced engineers?
 
Status
Not open for further replies.

Reply to Hot water goes cold unless it is trickling out in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

I live in an apartment block where generally hot water is supplied from the communal hot water cylinder and cold water to bathrooms is supplied...
Replies
4
Views
670
Hello All, I wonder if you can help me? I have intermittent hot water low flow from all taps in my 4 bedroom house upstairs and downstairs. I...
Replies
3
Views
406
Can anyone help me with an ongoing issue I've had since I had an annual service on my combi boiler, which is a Potterton Performa 24. Literally...
Replies
3
Views
382
Looking for any ideas to help. I've a Heatrae Sadia Hot Water tank, heated through Oil fired boiler (working fine). A week ago I reset the air...
Replies
8
Views
382
Hi, I hope someone can help. I’m hoping this isn’t a permanent problem. We’ve converted a gravity vented hot water system, into an unvented...
Replies
18
Views
1K
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock