Well I'm not getting into the thorny subjects of drugs, and what we've tried or haven't.

Suffice to say that a nice cold beer is the only inebriation I like. Or scotch, or brandy, or wine, turps.....the list goes on!!
 
Right I have been to house and measured the rads. All are Quinn double convector details listed below. Need 34KW to drive the rads so not 100KW. Can anyone recommend a boiler with correct capacity?
But you don't know if the radiators are correctly sized?

Use the Whole House Boiler Size Calculator to find out what size boiler is required.

It does not matter if the radiators add up to more; it just means they can run at a lower temperature.
 
But you don't know if the radiators are correctly sized?

Use the Whole House Boiler Size Calculator to find out what size boiler is required.

It does not matter if the radiators add up to more; it just means they can run at a lower temperature.

Worked out what house requires previously and size, volume and construction need 32kw. Rads output 34kw.

Worcester TSM has been to house today to talk to engineer and he has said it needs a 65KW boiler and a U16. I am trying to get the contact details for the worcester TSM so he can explain his thinking.
 
Worked out what house requires previously and size, volume and construction need 32kw. Rads output 34kw.

Worcester TSM has been to house today to talk to engineer and he has said it needs a 65KW boiler and a U16. I am trying to get the contact details for the worcester TSM so he can explain his thinking.

What the hell?

I implore you, please get another heating engineer round. This stinks. Even if you do it on a Saturday and just pay him to specify the system for you.
 
Most will add 10% to each rad/room when sizing rads, which explains the discrepancy you've found.

Again, get a new engineer!
 
Worked out what house requires previously and size, volume and construction need 32kw. Rads output 34kw.

Worcester TSM has been to house today to talk to engineer and he has said it needs a 65KW boiler and a U16. I am trying to get the contact details for the worcester TSM so he can explain his thinking.

A 40CDI should be fine. I recently fitted a 40CDI regular on a house with 31 rads. The whole house heating calc came to just over 37KW and it works perfectly well and is in no way undersized from an output perspective!

I don't think you need a light commercial boiler for what you have... 40KW domestic is fine
 
Absolute horse sh 1 t if you need 65 kw you have a swimming pool to heat also, I specialise in larger properties and from the info you have given no way!
 
Earlier you said that you had used several online calculators and could only get to approx 25kW. Which one did you use to get the 32kW?

Used whole house boiler sizing method which came out at 23kw Calculated Boiler Size

Used heat loss calculator to work out how much power required for each room and that came out at 23KW Trademate by City Plumbing Supplies

I also used [DLMURL="http://www.theradiatorcompany.co.uk/heatoutput/"]Radiator Heat Output Calculator and size calculator - The Radiator Company UK[/DLMURL] to see what radiator output was required for each room. Got the output for each room, added up and total was 24KW

Not sure if needed to add 2KW for HW so have added just in case which brings it up to 25-26KW

The 34 KW figure comes from using the radiator manufacturers technical data. I have looked up the output of each rad installed and the total out of all rads is 34KW.

Head spinning now :-( Have asked another installer to come to house and take a look.
 
Last edited by a moderator:
In from cold has keen confused - 100,00 btu not 100KW 30 kw will do his place
on a system boiler set up. 100kw will light up over 1600 60 watt light bulbs
- old type !!!!!!!!!! or 100 1 bar lecky fires
Hi All

New member and first post.

I'm not in the trade so hoping folks on here with all the knowledge can assist.

Got 5 bed detached Victorian house that has no central heating so in process of getting boiler and rads spec'd.

Have been told that will need a 100kw boiler and that this boiler will need a a larger gas supply pipe even though there is 22mm already.
Was hoping for a combi as there is only one bathroom with shower over bath.
Room sizes (in metres) are listed below, All double glazed with solid walls but I calculate heat requirement at 25KW so where the 100KW comes from I have no idea hence this post. All the on-line calculators I have used are all coming in around 25 - 26 KW for heating.

Hope someone can help or offer advice. I would think 100KW is large enough for a school or factory or a 5 bed with 14/15 rads.

Cheers

Room H, W, D
Living Room 3.1, 5.49, 4.88
Sitting Room 3.1, 4.22, 3.91
Dining Room 3.1, 3.23, 3.12
Kitchen 3.1, 5.18, 4.47
Bed 1 3.1, 4.42, 3.2
Bed 2 3.1, 4.42, 2.29
Bed 3 3.1, 7.21, 3.56
Bed 4 3.1, 3.86, 3.23
Bed 5 3.1, 4.27, 4.11
Bath 3.1, 4.42, 3
 
In from cold has keen confused - 100,00 btu not 100KW 30 kw will do his place
on a system boiler set up. 100kw will light up over 1600 60 watt light bulbs
- old type !!!!!!!!!! or 100 1 bar lecky fires
Hi
That's exactly what I thought but installer and now worcester TSM have said that not the case. So, with all the advice from everyone on here and my initial concerns I have another instaler scheduled to survey.
I am amazed that a representative of the manufacturer can give such poor advice :-(
 
Used whole house boiler sizing method which came out at 23kw
You said earlier that you were considering a combi boiler as you had only one bathroom/shower. Is this still the case?

If it is, the size of boiler is really determined by the hot water requirement, which depends on the maximum incoming cold water flow rate. You can easily check this at the kitchen sink cold tap using a bucket marked in litres and a watch with a second hand. Time how long it takes to fill to the top mark (usually 10 litres); then convert this to litres per minute. The required Hot Water output of the boiler is at least 2.5kW per litre/minute; i.e a flow of 10 litres per min will require a 25kW HW output.

You can ignore the 2kW allowance for HW if you have a combi boiler.

As for the advisability of having a combi boiler, don't forget that all taps, hot and cold, as well as washing machines, dishwashers etc are fed from the one source: the incoming cold main. So there could well be a reduced flow rate if more than one tap etc is in use at the same time. If you have a garden tap, you can do a basic test to see what the effect will be. Repeat the flow test, but this time with the garden tap full open. You will then find the reduction in flow rate.
 
so you could thank us all talk to the organ grinders not the monkeys
Hi
That's exactly what I thought but installer and now worcester TSM have said that not the case. So, with all the advice from everyone on here and my initial concerns I have another instaler scheduled to survey.
I am amazed that a representative of the manufacturer can give such poor advice :-(
 
so you could thank us all talk to the organ grinders not the monkeys

Many thanks go to all who have participated on this thread.
Without professionals like yourselves willing to share your knowledge and experience folk like me are in the dark.

Many thanks once again for everyone's help.
 
Status
Not open for further replies.

Reply to 100KW gas boiler for domestic install! in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi Guys Im doing a new build near Brecon, Powys. Its going to have oil boiler, heat store (big one) and radiators. No under floor heating. The...
Replies
0
Views
1K
I
Dear All, Please kindly advise, i don't know what else to do! Had new boiler Vaillant 424 heat only open vent boiler installed with new flue and...
Replies
53
Views
5K
Deleted member 120897
D
Hi all, At our old flat, we had a combi boiler which dealt with heating and hot water without an additional tank. There was an external timer...
Replies
9
Views
4K
Deleted member 126113
D
Hi, Getting an extension built as well as some alterations to the layout of our house. Been quoted £6k incl VAT for the plumbing and heating...
Replies
6
Views
2K
Wondering if there are plumbing gurus here who can suggest what could be the issue .Recently changed to gas heating and have a viessmann vitoden...
Replies
41
Views
14K

Newest Plumbing Threads

Back
Top