called to this tonight its the boiler with the green knobs turbo max plus 828e.worked ok on central heating but when hot tap was run boiler display quickly rose to 120 degrees and boiler blew off on prv.looked at diverter spindle through hole and could see spindle move when changing from htg to hw .also went into parameter 35 on operating codes and could see them changing from 1 to 0 showing operation of diverter control.there is very little advise in the manual on checking things.I am assuming a blocked hw heat exchanger (it was to late to strip and check). also the manual states the diverter and pump need to be removed is this the case as it looks as if it can be removed without the pump being taken out.also if removed will the DHWheat exchanger need new seals .Also can anyone describe the Aqua start system is it a pre heat ?
thanks ant