Cooperman1

I am looking at getting an unvented cylinder to replace my existing traditional vented system with cold water storage tanks. Water pressure into the house is 5 bar at a flowrate of 18 ltrs/min. I am concerned about getting a Megaflo as with a relatively low flowrate I understand that the Airgap will need to be recreated occasionally. Would it be better to use another make like Range Tribune, which has an external pressure vessel, and then I won't have any "Airgap" issues ?

Thanks for your help in advance
 
Hi. Either the calculations are wrong or your first work must be a new supply pipe. As with a head of 5 bar and a 15 mm supply pipe say 30 m run from mains one would expect somewhere about 42 litres / min
 
Thank you justlead1, but my initial question is around preferences for the Megaflow with its airgap and other systems with built in or external pressure vessels. My question is, why should you need to re-pressurise or "recreate the airgap"? What circumstances make this necessary?

Updating my current heating system which can be left completely unaided (with perhaps the intermittent yearly or so service) to a "current" "modern" system which has some temperamental nuance of worrying about airgaps - seems a bit of a backward step in technology!


Look forward to any help.
 
Its no big deal resetting the air gap, drain and fill. If going with an expansion vessel , it will be checked for pressure periodically as well. Any one with unvented will be able to sort.
As an add on , I tend to agree with just lead with 5bar and only 18ltres you have a valve not fully open , a blockage or the tap you flowrate at is very restricted, depending on which it is it is not necessarily a problem
 
Status
Not open for further replies.

Reply to Unvented cylinders in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

I live in an apartment block where generally hot water is supplied from the communal hot water cylinder and cold water to bathrooms is supplied from cold water tanks in the loft. It is a vented system. However, in a basement flat and a ground floor flat cold water supply to bathrooms is...
Replies
4
Views
605
I have been facing central heating low pressure on unvented hot water RM Cylinders but can't see any leak on the PRV, expansion vessels and plasterboard celling. I have got unvented pressurized RM Cylinders hot water system with 27KW Worchester gas boiler with expansion vessels . When...
Replies
2
Views
471
losing pressure
L
S
Hi All I had an unvented cylinder fitted about 6 years ago. It only supplies hot water to my shower. I was hoping for a much better flow rate from the shower but it seemed no different from the original combi boiler hot feed. There is (unusually) a lever that lets me select the combi or the...
Replies
2
Views
539
Steveo111
S
I had my indirect hot water cylinder removed a few days ago and the central heating boiler and pump is turned off at the fuse spur right next to the boiler. I have been without hot water for a few days which is fine - The plumber left the flow / return to the cylinder uncapped as well as the...
Replies
3
Views
978
Hi all. As the title says, I have a problem with an unvented cylinder I had installed last year where the first time I turn a hot tap on after the cylinder has been heated I get what sounds like a vibration. It generally starts about 1s after I open the tap and lasts for about 1.5s. I've...
Replies
27
Views
2K
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock