Discuss Ideal Classic NF80 problem in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Status
Not open for further replies.
J

jnw

I have been called out to service an Idel Classic NF 80 boiler
wich was not working. When I undone the control box so that it was
hanging on its wiring the boiler started up as it should. so I put the contol
box back in position and then nothing so undone the control box again as
before and the boiler stated working again. So I checcked all the connections and all the wires for continuity and all seems fine but when I
Screw the control box back the boiler fails to start. I have been in contact with technical support and they say it must be a loose connection but I still have not found one. Has anybody had a problem like
this or any idea what it could be.

Thanks Jeff
 
Well if you can not find a loose connection ,it is probably a dry joint on the pcb,remove pcb board and resolder main connection points and relays
Some would say just replace pcb
 
I have been called out to service an Idel Classic NF 80 boiler
wich was not working. When I undone the control box so that it was
hanging on its wiring the boiler started up as it should. so I put the contol
box back in position and then nothing so undone the control box again as
before and the boiler stated working again. So I checcked all the connections and all the wires for continuity and all seems fine but when I
Screw the control box back the boiler fails to start. I have been in contact with technical support and they say it must be a loose connection but I still have not found one. Has anybody had a problem like
this or any idea what it could be.

Thanks Jeff


Had a similar issue with an ideal elan, again pcb flap down it worked fine, pcb flap up it was clicking and clunking, it turned out to be the aps wires, but I changed pcb and harness and it was fine mate
 
Status
Not open for further replies.

Reply to Ideal Classic NF80 problem in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Evening All, Been having on and off issues with a Greenstar CDI classic Combi were the hot water is not heating up but only intermittently. Some...
Replies
2
Views
524
We have an all Vaillant setup - an EcoTEC Plus 637 system boiler plus wired VR720 and VR92 SensoCOMFORT controller, driving two CH zones plus DHW...
Replies
4
Views
611
I have a home with an oil boiler in a garage turned into a flat, heating both flat and main house, running c plan with two pumps, two motorised...
Replies
0
Views
422
Hi, I need some urgent advice. I've Just come home after going out for evening, to discover hallway floor and kitchen floor covered in water. On...
Replies
1
Views
539
My Grant combi oil boiler is giving me quite a headache at the moment. When I returned home last Friday I'd no heating or hot water. An engineer...
Replies
3
Views
593
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock