B

bbasmdc

Hi, my builder has rerouted my DHW pipework and we cannot get the air out. Interestingly the cold water "top up" to the boiler joins the flow vent and connects to the flow side of the piping. So as the boiler is pumping the hot water it is fighting against the cold water top up that only has gravity on its side.
Isnt it normal for the cold water boiler "top-up" that comes from the header tank to connect to the return path to the boiler?
Regards
 
Hi. Historically the cold feed to the system would have been connected to the return. However heating has been *******ized over the years so as to reduce cost etc. Once you introduce a circulater / pump the physics change, as a result you may find that a connection into the return will cause water to push out of the heating system vent pipe providing you with a radiator in the loft in the form of a cistern, not recommended. There was a time when the practice you describe appeared in text books. Now the majority of new systems are pressurised sealed systems which allow artistic liecence to the installer. Good Luck
 
Status
Not open for further replies.

Reply to Indirect hot water system pipe layout in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold...
Replies
2
Views
221
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up...
Replies
2
Views
283
PSxxxxxx
P
Hi, I have a Worcester 28i junior boiler that has started to lose pressure, only when using the central heating. When using hot water I have no...
Replies
6
Views
269
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4...
Replies
9
Views
459
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock