n141311

hi all,

I know this is a long shot but I'm wondering if there are any M&E contractors who specialise in plumbing that can help me. I think my plumber has messed up the plumbing for my property by using the wrong pipe size
frown.gif



BACKGROUND & DESIGN CHALLENGE

I've got an 8 bedroom, 8 bath property that I'm refurbishing and want to have piping hot, high pressure showers in the ensuites with a system that can accommodate all showers being used at same time during peak periods. As the property will be used as a boutique luxury hotel - these design requirements are a must.

The property is split into three sections with the boiler being located in the centre - with 4 bedrooms on one section of the house, and another 4 bedrooms on the other section of the house.

I had Bosch do me a system design to meet this design challenge and they proposed an unvented system comprising:
  • 2 x Greenstore cylinders 300l
  • Worcester GB162 50kw boiler
  • Salamander home boost pump
  • 28mm piping branching into 22mm
  • No point double coiling

The inputs they were given along with layout designs were:
  • -!Current standing pressure is 4.2 bar
  • - Over 22 litres per minute flow rate on cold
  • - At 4bar pressure, shower will deliver 17 litres of water per minute
  • - 8 thermostatic showers to be installed at the property and used during peak periods
  • - 8 size heated towel rails (to come on at same time as radiators) - 1,119 BTU per radiator
  • - 15 radiators - average 3,500 BTU per radiator
  • Property is split into two sections with the boiler being located in the centre: section 1 will have 4 bathrooms section 2 will have 4 bathrooms
  • - During peak times (mornings) 8 showers will be used simultaneously!
  • - Heating will be on 8hrs a day, 7 days a week during the winter
  • - Heating will be on 3hrs a day, 7 days a week during the summer

WHAT HAPPENED NEXT

I had work start on section A of the building comprising 4 bedrooms and bathrooms. The plumber re-did all of the pipework for radiators, hot and cold feeds for showers and basins....except he decided to use 22mm pipework branching off into 15mm instead of follow Bosch' guidelines.

I am now worried about the impact this deviation will have - will it still be able to meet the design challenge or does it make no difference?

I did some back of the envelope calcs and wondered if someone can:

a) help me validate if my back of the envelope calcs / assumptions / conclusions are correct? I am not an engineer or plumber.

b) suggest if there's a possible fix to still ensure I can meet the design challenge for the rooms that have already been piped up (luckily they are positioned close-ish to the boiler)

I have a CAD version of the property layout as well las technical docs for all of the proposed equipment to go in.

MY BACK OF THE ENVELOPE CALCS & ASSUMPTIONS

Grohe Grohtherm Cube Perfect Shower Set - 34506000
  • Assuming 11.5 litres per minute flow rate per shower
  • Ave shower time will be 20mins
  • Assuming 8 showers during peak times, that’s 92 litres per minute required
  • 22mm pipe has flow rate of 0.6 litres per second // 36 litres per minute
  • 28mm pipe has flow rate of 1.1 litres per second // 66 litres per minute

Assuming there will be a feed for section A of the property covering 4 bathrooms and another feed for section B covering bathrooms, this means max flow rate required will be 11.5 litres per minute * 4 showers = 46litres per minute needed from each main feed

Conclusion 1. 28mm piping should be used to meet the 46 litres per minute (22mm would be restrictive at max flow of 36)

However, there is also the issue of ensuring the cylinders themselves can supply enough water given peak time demand and then push it through at appropriate flow rate to avoid loss of pressure. To aid this, the spec indicated 2 x greenstore unvented cylinders at 300l each.
  • Greenstore SC300 can re-heat 300l of water in 24 mins = 12.5 litres a minute
  • At 2 cylinders in tandem, this means a re-heat capacity of 25 litres per minute
  • Going back to design challenge of 8 showers on at same time during peak periods:
  • 600 litre total capacity would be used up in 6.5mins (600 litres / 92 litres per min)
  • But in those 6.5 mins, the cylinders would reheat 163 litres of water (25 litres per min reheat capacity * 6.5 mins) = 1.7 mins
  • Total shower time at max demand: 8.2 minutes (6.5 mins from 600 litre capacity + 1.7 mins from reheat capacity)

Conclusion 2. while this doesn't quite meet the 20 mins at 100% utilisation, I think Bosch' proposed 2 cylinders is quite balanced because not everyone will shower for 20mins and it's unlikely that all 8 showers will be used at exactly the same time for exactly the same duration. If one or two people did find cold showers, total reheat time is quite healthy at 25l per minute - essentially covering 2 showers at 11.5 litres per minute flow rate.

CAVEATS & IMPORTANT NOTES

I know I've totally neglected pipe runs and the number of bends. I have layout drawings and a CAD version of layout that I can share if necessary.[/LIST]
 
I think your going to have fun at the start

Got a few questions

What boost pump have you got / link or pics and do you have a tank supplying thins or just straight off the mains

And what's your incoming mains pipe size ?

To get a re heat time for your cylinder (24mins)

You need to have 39kw going through the coil

And you have two

So there's 78kw just for the cylinders and let's say another 20 for rads etc

So that's in the middle of winter you need 98kw heating load for a re heat time of 24 mins

Let's say your fine with 48 mins re heat time

You need aprox 19.5 kw per coil (39kw for both coils)

Plus your 20 for your heating 59kw needed

Where in the country roughly are you ?
 
I think your going to have fun at the start

Got a few questions

What boost pump have you got / link or pics and do you have a tank supplying thins or just straight off the mains

And what's your incoming mains pipe size ?

To get a re heat time for your cylinder (24mins)

You need to have 39kw going through the coil

And you have two

So there's 78kw just for the cylinders and let's say another 20 for rads etc

So that's in the middle of winter you need 98kw heating load for a re heat time of 24 mins

Let's say your fine with 48 mins re heat time

You need aprox 19.5 kw per coil (39kw for both coils)

Plus your 20 for your heating 59kw needed

Where in the country roughly are you ?

Hi Shaun,

I'm based in Yorkshire. We have a U16 gas meter providing mains supply to the boiler. The re-heat time came from the Greenstore TC300 spec.

Salamander home boost pump (not yet fitted): Home Boost

Greenstore TC300 cylinder: Greenstore SC Cylinder Series - Worcester Bosch

In terms of the pipe sizing to achieve design requirement - do you have a view on this? Part of house has been done in 22mm branching into 15mm but Bosch had specified 28mm branching off into 22mm.
 
Last edited by a moderator:
Right your on a looser before you start

That pump won't do anything for your mains water

You would need either a break tank and pump to push your lpm up to around 80-100lpm

Or an accumulator sized correctly

42-35mm to the cylinders in and around 35-28mm out and to close as possible to each set of 4 then 22mm to each

Also pg 7 on your manual indirect coil heat exchanger rating in kw
 
My best advice is start looking for a commercial heating engy

Because you will need other things like

secondary returns
Low loss header
Balancing valves depending on length of circuits

Etc
 
I think you should seek advice from a company, or consultant, who does a lot of this type of work. It definitely looks 'commercial' not 'domestic' to me and needs to be 'designed' not lashed up using rules of thumb.

The assumptions you put in about what performance is needed at periods of maximum demand are going to make a big difference to the cost and performance of the system. E.g. where did you get the '20 mins' average figure from? The average (domestic) shower apparently lasts 8 minutes:

People's showering habits revealed in survey - BBC News

and that average includes teenagers!

I imagine that, if one knows where to look, there are data available for shower usage patterns in hotels.
 
Sounds like you need a Mechanical Consultant first unless you can find someone you trust to D&B.

Crazy if Bosch specced a Salamander home boost pump!
 
Hey all,

Thanks for so much for the replies. Bosch didn't spec the salamander pump...that was the plumber who cocked up the pipework. Sigh.

Can anyone recommend a good mechanical consultant and plumber in the Yorkshire area that can help? The problem is that a lot of the M&E firms seem too big to care about a job this size, but it's too large for the smaller plumbing firms.

None of this would have been needed if the plumber had just followed Bosch' spec.
 
My best advice is start looking for a commercial heating engy

Because you will need other things like

secondary returns
Low loss header
Balancing valves depending on length of circuits

Etc
Hi Shaun - thanks mate. Even with secondary returns, etc - can the situation be rectified given part of the plumbing has been done in 22mm branching into 15mm? I don't want to rip it out as 4 of the rooms have been acoustically over-boarded and skimmed
 
New posts
Status
Not open for further replies.

Reply to Ahhh is there an M&E plumbing contractor in North East that can help me in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Background I have a small one-bedroom flat in the roof space in a victorian house. There are three floors below and each floor has a single...
Replies
3
Views
596
Hi, We are having PV panels fitted which will dump the excess energy into our hot water tank. Our house originally had a large 210L economy7 hot...
Replies
1
Views
633
Is there a standard for the above?, ie primary flow rate, primary flow temperature, reheat time from X degC to Y degC, continuous flow rates at...
Replies
0
Views
548
Hi all This is only about my third/fourth post, so go easy. Also, I'm only an enthusiastic amateur, not a pro... I'm having issues with the...
Replies
7
Views
2K
Hi to all, Seeking your advice here - a very long back story to get you well informed: I am a complete DIY and plumbing novice with very little...
Replies
6
Views
3K
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock