Sounds like air in the system, try bleeding all radiators and any manual / automatic vent points. If no air comes out I'm afraid you'll have to hire another plumber or get the first one back, I hope you haven't paid him!

I would never leave a customer like this
 
Sounds like air in the system, try bleeding all radiators and any manual / automatic vent points. If no air comes out I'm afraid you'll have to hire another plumber or get the first one back, I hope you haven't paid him!

I would never leave a customer like this

We have paid him as it was working. Albeit was only £240 but it's the time frame.
 
I have header tank and cold water tank, both full.

Also now can't get the cap off to fit Immersion heater. Omfg
The smaller of the 2 tanks, what was the condition of the water like, did you try pushing a screwdriver or something into the tank outlet to make sure it was clear?
 
Ok am I doing something wrong, this is the tap the plumber drained the water out of the system with above the boiler. In my little mind I thought if I opened that valve/tap water should come out, am I wrong do I have to open anything else. I don't want to completely drain everything down just view the water or make sure it's making it to the boiler and it's not just air pushing around.
 

Attachments

  • IMG_20190804_165017_50.jpg
    IMG_20190804_165017_50.jpg
    262.7 KB · Views: 8
Ok am I doing something wrong, this is the tap the plumber drained the water out of the system with above the boiler. In my little mind I thought if I opened that valve/tap water should come out, am I wrong do I have to open anything else. I don't want to completely drain everything down just view the water or make sure it's making it to the boiler and it's not just air pushing around.

Yes that’s the drain cock and is used for draining purposes.
 
So I should have water come out of that?
Water will come out so long as the washer isn't stuck or the valve blocked. If the plumber recently used it then it should be fine. What I would do is attach a hose, open the valve and then go in the loft to check that the water level in the tank drops and refills. This will prove if the cold feed is blocked or not.
 
Water will come out so long as the washer isn't stuck or the valve blocked. If the plumber recently used it then it should be fine. What I would do is attach a hose, open the valve and then go in the loft to check that the water level in the tank drops and refills. This will prove if the cold feed is blocked or not.

Nothing comes out when I undo the square bit, do I have to push or press anything, it opens very easily but not even a drip out of it when square bit fully open.
 
Nothing comes out when I undo the square bit, do I have to push or press anything, it opens very easily but not even a drip out of it when square bit fully open.
If it was me, I'd slightly unscrew the circular nut that the square nut passes through, don't take it all out but it will allow you open the drain valve further, this can sometimes free off the washer in the valve. Be warned though, if the washer is knackered you could find the valve won't re seal. Personally I'd wait till tomorrow till shops are open to get a replacement if needed.
 
If it was me, I'd slightly unscrew the circular nut that the square nut passes through, don't take it all out but it will allow you open the drain valve further, this can sometimes free off the washer in the valve. Be warned though, if the washer is knackered you could find the valve won't re seal. Personally I'd wait till tomorrow till shops are open to get a replacement if needed.

I Agree with Craig, best wait til tomorrow :)
 
I've given up properly now.

That lock ring thing was quite loose.

My partner said she saw the the plumber draining water out there with hose attached with clear water running through, again in my head the colour of water in header tank how can it be running clear.
 
I think it's beyond my knowledge understanding. I can see how it all works but I'm not a plumber and I think it's best left to the professionals, just not the same one we had before.

Thanks again for all the advice.
 
Well another 5 hours with a different plumber and guess what, no hot water or heating. I'm at work but the Mrs has said they have replaced a load of pipework in the airing cupboard and got some sludgy water out. But it's still coming up flow error. Going to have to come back another day, dread to think on cost of this little lot. Sad times.
 
Well another 5 hours with a different plumber and guess what, no hot water or heating. I'm at work but the Mrs has said they have replaced a load of pipework in the airing cupboard and got some sludgy water out. But it's still coming up flow error. Going to have to come back another day, dread to think on cost of this little lot. Sad times.
When you get home take a pic of the new pipe work, just to keep us updated.
 
Did you ever contact @Brambles about the work? You initially told him you would give your original plumber another chance first but obviously he's been sacked off now.
 
I haven't yet no, we got the other plumber to fit the 3 way valve then paid him as it was ok for a couple of days then we went away . The Mrs then called the people that service our boiler yearly and to be fair they turned up as promised, even put a job off to do ours. If it's just a case of flushing the rads with a hose pipe that's something I can do easy enough, had rads off before and fitted new ones so sure I can manage that.
 
I think that's what it's looking like. They drained water off as per pic.no real metal bits just sludge and mucky water. Their opinion and that's all it is at the moment is as soon as the pump starts to drawer water it's drawing sludge slowing everything down to a stop.
 

Attachments

  • 15650279055935397636329458110501.jpg
    15650279055935397636329458110501.jpg
    1.4 MB · Views: 14
Tall glass what they fetched off

Small glass what I've just drained out of tap off the top of the boiler pipe
 

Attachments

  • 15650296999754567895464705969238.jpg
    15650296999754567895464705969238.jpg
    1.3 MB · Views: 15
  • 15650297160128048946572465347743.jpg
    15650297160128048946572465347743.jpg
    1.2 MB · Views: 18
When it's in hot water on from programme, with cylinder start set to 55-60 boiler should fire. Probably heads gone on actuator or fault with motor or three port wiring
 
A bit more info, when the new Plumber was doing his stuff the water he got to run clear and the hot water started to heat up, he then tried the heating side and that screwed the whole system.water went all crap again and boiler wouldn't fire.
 
That's new pipes, not as many as I thought but new none the less.
They've replaced the cold feed, it's a typical place for the system to block up there. Obviously there's no way of knowing whether it was blocked or not though. I personally wouldn't have installed a iso valve either, I'd have gone with a full bore valve and removed the handle so it can't accidently be turned off.
 
A bit more info, when the new Plumber was doing his stuff the water he got to run clear and the hot water started to heat up, he then tried the heating side and that screwed the whole system.water went all crap again and boiler wouldn't fire.
Sounds like a good power flush should see you right.
 
To me it looks like the pumps are fine it's the fact that the flow and return are joined together that gets me.

But in all honesty I cant really make every thing out as it hurts my eyes. RIP it out and do it again.
 
To me it looks like the pumps are fine it's the fact that the flow and return are joined together that gets me.

But in all honesty I cant really make every thing out as it hurts my eyes. RIP it out and do it again.
It's not required but I thought that was a bypass and that the gate valve would only be partially open.
 
I’d think about getting in touch with @Brambles, very knowledgeable (more than me, which isn’t hard :D). Didn’t know he was near to you? Might actually get it sorted.
 
The pump just switches off when the flow message comes up but yes it displays between 29 and 34 watt when running.

OK then, if that is a 6M pump and running on fixed speed 3 @ 30W then it is only circulating ~ 0.2 m3/hr or 3.3 LPM, just turn the rotary knob fully clockwise and then back it off a little, when it starts up adjust it to read 4M (flashing), it will then change to display the power, if, in fact the flow rate is only ~ 3 LPM then it will only read 15/18w, the higher the better, to give any meaningful flow at this setting it should read ~ 25W which is ~ 13/15 LPM.
 
JP

I would be wary of trying to fix this by making ad hoc modifications ( new bits of pipe and valves et al ) and then trying to run the system. You run the possible risk of either making the problem worse or possibly causing expensive damage to the boiler.

Isolate the heating system other than one radiator (preferably the one closest to the boiler ) and then systematically work through the boiler + single rad hydraulic system. At the same time check and test the individual controls against the logic diagram. Also fit a quality magnetic filter on the return to the boiler.

Once you are satisfied that you have a clear hydraulic path on your mini system - configure the pump to run with the boiler off and satisfy yourself you have a good clean flow path.

Thereafter and only when you have a clear hydraulic flow path, get the boiler operational at minimum rate and stable before you systematically look at the rest of the system.

At the end of the day, you have a fairly straightforward system to analyse, approach it in a logical step by step fashion - and make sure that you have not had anyone in to work in this problem who has changed the flow paths.

Always have in mind that you may have more than one problem with the system - hence the need to be systematic, patient and don’t jump to conclusions (sludge is an issue, but in my experience, a serious sludge problem = no flow, not erratic flow which are (to my mind) the symptoms you are describing ).



A suggestion - get the new iso valve by the pump removed - it is not full bore so is restricting flow - it may seem churlish, but the last thing you need at the moment is anything that disrupts or distorts the hydraulic flow

Hope this helps
 
Last edited:
JP

I would be wary of trying to fix this by making ad hoc modifications ( new bits of pipe and valves et al ) and then trying to run the system. You run the possible risk of either making the problem worse or possibly causing expensive damage to the boiler.

Isolate the heating system other than one radiator (preferably the one closest to the boiler ) and then systematically work through the boiler + single rad hydraulic system. At the same time check and test the individual controls against the logic diagram. Also fit a quality magnetic filter on the return to the boiler.

Once you are satisfied that you have a clear hydraulic path on your mini system - configure the pump to run with the boiler off and satisfy yourself you have a good clean flow path.

Thereafter and only when you have a clear hydraulic flow path, get the boiler operational at minimum rate and stable before you systematically look at the rest of the system.

At the end of the day, you have a fairly straightforward system to analyse, approach it in a logical step by step fashion - and make sure that you have not had anyone in to work in this problem who has changed the flow paths.

Always have in mind that you may have more than one problem with the system - hence the need to be systematic, patient and don’t jump to conclusions (sludge is an issue, but in my experience, a serious sludge problem = no flow, not erratic flow which are (to my mind) the symptoms you are describing ).



A suggestion - get the new iso valve by the pump removed - it is not full bore so is restricting flow - it may seem churlish, but the last thing you need at the moment is anything that disrupts or distorts the hydraulic flow

Hope this helps

thanks for that, it is getting a bit to much for me really I can only do very basic stuff. we just need someone to fix it lol , its been nearly 5 weeks now and I have no more hair left to pull out. I have a logical mind but I just cant seen to get my head around this. if we could just get hot water that would be ok for now until the rest can be fixed but its just not going right. in my head yet again ive got set the timer so its just HW which should close the rads off? drain the water out from the tap above boiler until it runs clear and see if the boiler then kicks back in or is that too simple, if that worked for a couple of days or so I could start opening one rad at a time. im getting to a point where im over thinking and clutching at straws I think.
 
JP

I have not seen the system - but it is not complex. At a basic level there is something that is severely restricting flow - I doubt that that is just sludge ( but I am possibly wrong).

From a heat perspective, the issue you appear to have is either at or before the three position valve and the heat exchanger, where the pipework is of a reasonable diameter - but the heat exchanger obviously is not.

I would not keep on trying to fire the boiler until I was satisfied that I had a clear hydraulic path through the boiler - if you do and the overheat sensors fail ( unlikely, but if they are being tested repeatedly!) you could make the current problem worse.

On issues where a number of people have tried to fix it, you sometimes find that with the best will in the world they have changed something that has compounded the problem.

It is unlikely that the people you have had to look at the system are novices, but I think it is likely that you have at least two concurrent problems.

With respect to the people who have “serviced” your boiler - they have not in my view done a proper job - the quality of your system water has not got into that state in a year.

It is generally easier ( in my experience ) to get a system operational from the central heating circuit rather than the hot water side ( it eliminates any potential issues that may be within the tank pipework)
 
I haven't changed anything its all been done by "qualified " plumbers.

the boiler was serviced in February if I remember correctly.

Its probably most unlikely but you can easily check that the circ pump is pumping in the right direction by checking the arrow on the pump body, also if you are thinking of doing a few things yourself, if you can run the pump with a separate (elec) supply with boiler powered off and then open that three way valve manually to its various settings you can then play around with venting rads etc and see if that pump power increases (speed 3), it should increase to ~ 38/40 W and you will then know that you are getting a decent flow before firing up the boiler again.
If a decent flow rate cannot be achieved then possibly the boiler Hx is fouled.
 

Reply to water help no hot water in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

We have hot water, tank for hot water why is the hot water boiling hot from tap,and shower, We are on a schedule for hot water via our hive app...
Replies
4
Views
318
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold...
Replies
2
Views
229
The Water Board have just replaced the main water supply to our property. We have a ground floor combi boiler. The central heating system for the...
Replies
9
Views
566
  • Solved
Hi, I am looking for a bit of advice. Our Gledhill hot water tank was installed incorrectly 18 months ago and has been sending bubbling hot...
Replies
2
Views
526
M
Hello, We’ve recently moved into a fairly old, fairly big detached house (i.e. fairly draughty, but not too bad by any means) with a fairly new...
Replies
0
Views
288
MartinPod81
M
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock