Discuss trianco oil fired external (with cylinder in attic) gravity fed system in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Status
Not open for further replies.
M

markmonty

i am on a job where the radiators down stairs are heating good but the 3 upstairs rads have no heat whatsoever, the boiler is outside at back door of house and is working perfectly,pump sounds great and set at 3, radiators are full of water upstairs yet no heat apart from at one which has tiny bit of heat at valve and up one side of radiator, im thinking air lock or needing balanced, any other suggestions would be much appreciated , mark montgomery
 
the pump must be ok as downstairs heating perfectly all 4 radiators, thanks for your suggestions guys i will check
 
Have you tried shutting down all other rads other than the three affected to force any air round? What is the water condition like if a part gravity system it must be quite old have the inhibitor levels been maintained?
 
If the pump was at fault Id expect the opposite symptoms ie warm upstairs (thermals) and not downstairs. Sounds like a blockage, as Roger says, turn the good ones off. Check the controls upstairs especially any TRVs - is the pin stuck down?
 
If the pump was at fault Id expect the opposite symptoms ie warm upstairs (thermals) and not downstairs. Sounds like a blockage, as Roger says, turn the good ones off. Check the controls upstairs especially any TRVs - is the pin stuck down?

I agree with bunker on that one
 
Status
Not open for further replies.

Reply to trianco oil fired external (with cylinder in attic) gravity fed system in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

  • Question
Central Heating Pump - G Pump Force HE-RS25/6PWM-130 Hi, I would be grateful if someone could explain whether our CH system can cope with the...
Replies
7
Views
613
Hi All, In Dec 2023 I had my annual boiler service and asked the plumber to change 2 radiator valves as the radiator in the toilet downstairs was...
Replies
7
Views
528
Hi all, Got a nightmare situation with a central heating system I recently adopted. It's an open vent system with a combined F&E pipe, with a...
Replies
17
Views
2K
  • Question
Hi folks, I’m in need of some sound advice. We have recently had a ground floor extension and have had underfloor heating (company: JK UFH)...
Replies
1
Views
4K
P
Hi there, please help dont have a clue how to set this up. Ive recently installed a complete new central heating system in my house myself. The...
Replies
22
Views
4K
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock