Hi folks, I’m in need of some sound advice.

We have recently had a ground floor extension and have had underfloor heating (company: JK UFH) installed throughout most of the downstairs. We have a few rads still left downstairs and the entire upstairs is still heated through rads.

We have a vented (gravity fed) central heating system (about 0.3 bar), heated from an oil fired Thermecon boiler. The header tank is in the loft and the boiler in the garage. It’s an S plan setup with two 2 port valves that control the flow to the CH and to the water heater tank (immersion).

The plumbers have just connected the UFH as a direct T -off from the flow (just after the boiler) and the return just before the boiler, as the UFH manifold is in the garage also.

The UFH has not been placed on a separate thermostat or controlled with a separate port valve, therefore it’s a dumb system and will only receive hot water if either the hot water tank or the CH are calling for heat. My plan is to get it on its own zone, however as things stand, I simply can’t get it to get hot at all. The best I’ve managed is 30 degrees while the boiler is running.

The pipework from the boiler to the manifold and CH is 22mm and all rads are on 15mm

My understanding is that I have the following options, however I’m a little in the dark as to the best course of action, so any advice and opinions would be welcome.

  • I’m told that an additional pump is needed to get the hot water sent to the UFH manifold, however where would this pump go? before or after the T-off to the UFH manifold? Also, would a second pump run the risk of over pumping into the header tank, adding crap into the system? Or should this pump replace the current one on the first floor.
  • Install more valves to enable the UFH to be diverted all hot water at the times it requires it, therefore going from a 2 valve to a 3 valve system. I’m thinking this will mean that the UFH will only get hot if the others are not calling for heat.
  • Make the CH system unvented (pressurised) with an expansion vessel and filling loop. My worry here is that pressurising the system might find weakness in the pipework (house was built in 1990). Also I’m guessing that even after this is done, I still need to zone the UFH onto its own circuit.
  • I’ve read that Installing a plate heat exchanger to the UFH would add pressure and get the heat through the system, however I’ve no Idea if this is a valid option and I’m assuming I still need to zone the UFH off.
  • Some combination of the above
I have linked an image of my setup. I’m not a plumber so please let me know if I have missed some crucial piece of information here.

My Setup
 
Whoever did the underfloor has totally shafted you.

Connections to manifold after pump, additional 2 port valve for control.

You say it runs throughout ground floor, do you not have room thermostats that will control actuators on the manifold.

Really needs eyes on by a competent engineer.
 

Reply to How can I get heat into Gravity Fed UFH system in the Water Underfloor Heating Advice area at PlumbersForums.net

Similar plumbing topics

Hi everyone, Looking for a bit of advice, recently went to a job where heating was operating when called for however not for the hot water. I have changed the 3 port actuator Honeywell head however this doesn’t seem to have solved the issue, does this mean that the programmer is faulty? Or is...
Replies
8
Views
214
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
1
Views
76
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up to 1.3. I've had an engineer look inside the boiler and he can't see anything wrong. I've checked the pipes all over the house and cannot see any...
Replies
1
Views
92
Hi, My current hot water system needs to be replaced. Anyone got any suggestions or can recommend any plumbers around Derrimut area that won't rip me off? An office guy recommended me to apply for government rebates and get it installed through timetosave.com.au. How reliable is this...
Replies
6
Views
276
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
4
Views
377
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock