Discuss Can a Viessman system boiler be fitted with Albion unvented cylinder? in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Status
Not open for further replies.
S

sharmistha

I'm trying to pair a Viessman Vitodens 100W (30kw) systems boiler with a Albion Ultrasteel (AUD180) Direct Unvented hot water cylinder. My builder tells me that the two are incompatible. He has not suggested an alternative..... Is it true that the 2 can't be fitted together? An expert's opinion would be most appreciated. Thanks!
 
You cant use any make of normal boiler to heat a Direct cylinder. Direct cylinders dont have a coil and are usualy heated by a couple of electric immersion heaters. Excellent choice of boiler though, if its a new system from scratch then you have the facility from the Viessman to 4 pipe it so no need for a 3 or 2 port etc.
 
Last edited by a moderator:
You cant use any make of normal boiler to heat a Direct cylinder. Direct cylinders dont have a coil and are usualy heated by a couple of electric immersion heaters. Excellent choice of boiler though, if its a new system from scratch then you have the facility from the Viessman to 4 pipe it so no need for a 3 or 2 port etc.

It is a brand new boiler. As is the cylinder. What Cylinder would you suggest I use? I know we need 170-180L capacity, but don't know what to get. Thanks in advance for your help! -s
 
Any Unvented cylinder that is Indirect, use the viessmann Branded one, they are made by Gledhill now and so are very reasonably priced, with The Viessman system you can use thier plug and play hot water sensor probe. Search for a local Viessmann aproved installer via the Viessmann site the aproved installer can give you a 5yr garentee too and will be able to advise you best.
 
I've fitted a few Vitodens systems with various makes of unvented cylinders, including an Albion. Just spoke with the customer today & he's is very happy. You can use the direct sensor, but to comply with G3 you need to run a 2-port valve off an 'internal H-1 board'. You get the board from Viessmann & it clips into the flip down wiring centre. As its Viessmann, the instructions are normally only in German but the Tech Help will walk the installer through
 
Status
Not open for further replies.

Reply to Can a Viessman system boiler be fitted with Albion unvented cylinder? in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold...
Replies
2
Views
247
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up...
Replies
2
Views
310
PSxxxxxx
P
Back
Top