Discuss HOW TO: Replace an expansion vessel easily on a Worcester 28CDI in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Status
Not open for further replies.

Nostrum

Plumbers Arms member
Plumber
Gas Engineer
Messages
3,399
This has come up in a few threads so I thought I would give it a try and if it helps, make a quick how to for others to see.

Ok, so the CDI range isn't known as one of the easiest boilers to work on, the expansion vessel is fitted by way of a large cable tie right in the back end of the boiler.

EV281.jpg

In front of it, and subsequently what usually has to be removed in order to replace it, is pretty much everything. If you follow the manual, which I have done in the past you will soon find a long list of parts needed to be removed, including the main heat exchanger, fan, plate heat exchanger, pump, pipework etc and can be quite a long job, especially if the existing O rings leak.

So, providing you can access one side of the boiler, there is a much easier way of changing the vessel.

Start by removing the side panel, 2 screws in the front and one at the top

EV282.jpg

The lower panel in the above pic is what we are removing, but first a few things need to be removed to make life easier. Start with the stat wiring which sits up on the right hand side of the main heat exchanger.

EV283.jpg

Remove the 2 orange connectors (assuming you've already isolated electric etc) and pull them through the 2 grommets and tuck the cable away somewhere out the way under the boiler.

Next there are 4 screws which need removing, 2 in behind the PRV

EV284.jpg

The other 2 are behind this again and can be seen through the gap in the side panel, and accessed with a long pozi screwdriver

EV286.jpg

Next pop the white pin through to release the front fascia front the side panel, then release from the other side and let it dangle somewhere out of the way.

EV285.jpg

The only thing holding the side panel on now should be half a dozen rivets, these go through into the combustion chamber. Carefully drill these out making sure you don't go through the air pressure switch pipes in behind. I used a 4mm drill bit.

EV2812.jpg


I left the main wiring cable (white) connected as there is enough slack to move the panel out of the way with it connected. Disconnect the expansion vessel tube from the pump connection and vessel, you can bin this as the new vessel comes with a different tube. Cut the cable tie and remove the expansion vessel from the hole.

EV288.jpg


The new vessel slides in easily without any fuss as you would expect, but I took a photo of it so I need to write something!

EV289.jpg EV287.jpg


Reconnect the expansion vessel using the new tube supplied, sip tea, explain to the customer that it usually takes an hour and 5 bleeding knuckles to get this far. Quick :39:break, then;

Re-fit the panel, I then used pop rivets to replace the ones I had drilled out, the pipes to the right were in the way to get a few of the rivets back in, but make sure that all the rivets into the combustion chamber are re-fitted, for obvious reasons.

EV2810.jpg

Re-fit everything in the reverse order and admire the fact it looks like no-one has touched it.

EV2811.jpg



Thanks to the people who suggested this method, it could probably be done in 30 minutes if your not taking photo's along the way etc, took me about an hour all in, including changing the PRV which was stuck in due to a corroded retaining clip!

Hope that helps :grin:
 
Last edited:
Told you it could be done! Love the step by step photos excellent work!
 
Is it only the 28 or is the 35 the same as I have got 1 to change next week and I really dont fancy pulling everything out.
 
This has come up in a few threads so I thought I would give it a try and if it helps, make a quick how to for others to see.

Ok, so the CDI range isn't known as one of the easiest boilers to work on, the expansion vessel is fitted by way of a large cable tie right in the back end of the boiler.

View attachment 8032

In front of it, and subsequently what usually has to be removed in order to replace it, is pretty much everything. If you follow the manual, which I have done in the past you will soon find a long list of parts needed to be removed, including the main heat exchanger, fan, plate heat exchanger, pump, pipework etc and can be quite a long job, especially if the existing O rings leak.

So, providing you can access one side of the boiler, there is a much easier way of changing the vessel.

Start by removing the side panel, 2 screws in the front and one at the top

View attachment 8033

The lower panel in the above pic is what we are removing, but first a few things need to be removed to make life easier. Start with the stat wiring which sits up on the right hand side of the main heat exchanger.

View attachment 8034

Remove the 2 orange connectors (assuming you've already isolated electric etc) and pull them through the 2 grommets and tuck the cable away somewhere out the way under the boiler.

Next there are 4 screws which need removing, 2 in behind the PRV

View attachment 8035

The other 2 are behind this again and can be seen through the gap in the side panel, and accessed with a long pozi screwdriver

View attachment 8036

Next pop the white pin through to release the front fascia front the side panel, then release from the other side and let it dangle somewhere out of the way.

View attachment 8037

The only thing holding the side panel on now should be half a dozen rivets, these go through into the combustion chamber. Carefully drill these out making sure you don't go through the air pressure switch pipes in behind. I used a 4mm drill bit.

View attachment 8038


I left the main wiring cable (white) connected as there is enough slack to move the panel out of the way with it connected. Disconnect the expansion vessel tube from the pump connection and vessel, you can bin this as the new vessel comes with a different tube. Cut the cable tie and remove the expansion vessel from the hole.

View attachment 8039


The new vessel slides in easily without any fuss as you would expect, but I took a photo of it so I need to write something!

View attachment 8040 View attachment 8041


Reconnect the expansion vessel using the new tube supplied, sip tea, explain to the customer that it usually takes an hour and 5 bleeding knuckles to get this far. Quick :39:break, then;

Re-fit the panel, I then used pop rivets to replace the ones I had drilled out, the pipes to the right were in the way to get a few of the rivets back in, but make sure that all the rivets into the combustion chamber are re-fitted, for obvious reasons.

View attachment 8042

Re-fit everything in the reverse order and admire the fact it looks like no-one has touched it.

View attachment 8043



Thanks to the people who suggested this method, it could probably be done in 30 minutes if your not taking photo's along the way etc, took me about an hour all in, including changing the PRV which was stuck in due to a corroded retaining clip!

Hope that helps :grin:
yep said it could be done,done loads
 
Little off topic here

Can we have a sticky or forum that's locked to new post that contains useful info

Like this

Gasmans Worcester red gasket

My ideal resistance values

Etc?
 
Status
Not open for further replies.

Reply to HOW TO: Replace an expansion vessel easily on a Worcester 28CDI in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

    • Like
Looking for someone that can replace the expansion vessel on an old heating system that is losing pressure every day and needs topping up at least...
Replies
2
Views
477
Hello, I have to replace the flush valve and/or the washer but unfortunately it's inside the vanity unit. The only way is removing the toilet. I...
Replies
16
Views
636
Hello, I live in a two floor semi with a gravity fed conventional gas fired boiler (Potterton Kingfisher MF). The boiler is fed cold water from...
Replies
0
Views
520
Hey, I've got a Grant Vortex that's leaking water from the seal around the expansion vessel - it's the round type about 50cm wide. The system is...
Replies
2
Views
1K
A
We have a vaillant combi boiler that over ~ 2yrs loses a bit of pressure, and recently after 2 weeks away and no use the system would not fire and...
Replies
2
Views
513
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock