Does anyone have any experience in failing PRVs?
in my property in France, I have a Sauter 200l electric wall hung water heater. The inlet PRV on the old heater kept letting by. Found another PRV on the incoming main. The main PRV showed 2 bar on the gauge which is clearly wrong. Took it apart and put it back together. Adjusted the incoming pressure to the meter to try and get more pressure in the house. I should mention that the start to all this was almost zero water pressure coming to the house. I know the main supply pressure is ok because there's a separate supply going off of the main before the first PRV and the pressure was fine.
Turned up the pressure, all good to the house but the water heater PRV then let by. PRV is rated at 7bar and there's clearly not that much getting to any tap!
so, changed the PRV, no improvement. Took the opportunity to replace the old water heater and fitted a brand new PRV which was an exact 7bar item to the old one. Turned the water on, instantly let by. Turned off the water main and put back on a quarter turn only. Almost nothing to the taps but the water heater PRV let by instantly.
Essentially, no matter how little pressure is coming from the main, the PRV releases. Same on the new one as was on the old one. Could these French units have a quirk that once they let by they don't actually ever reset again?
not quite sure where to go next, different make of PRV perhaps? I've never had an issue in the UK with any I've fitted but I'm not 100% on anything non UK

Any my help much appreciated on any ideas, I know this is a question not about the UK but the principals remain the same I assume.
 
Would probably try another. They should be automatically resettable. When you say passing, do you mean releasing or just leaking?
 
Passing as in pretty much letting all the incoming water instantly come out of the relief valve. It's not appearing to now be releasing based on a pressure build up but more that it just simply can't hold the water at all. Seems rather odd that this second one has the same issue as the first yet neither are on the same heater since its been changed.
the prv does appear to operate in that you can turn it to test its operation and it closes back off as it should, but literally a couple of seconds later it starts to stream out. I think it has to just be bad luck and a faulty second valve?
 
You have another problem. I'm not sure what the regulations are in France with regards to unvented cylinders but we can only apply what we know over here.

Which is stop playing with it and get someone in who knows what they're doing.

Job 38.11
 
Status
Not open for further replies.

Reply to PRV fault in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hello plumbers in my internet. So the Mrs want a spray mixer tap in the kitchen as we had two separate taps. I changed the tap for a temporary two hole mixer but the cold water pressure is high mains fed and the hot is low pressure immersion tank fed. I've been trying to find info on what I...
Replies
2
Views
137
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
139
The fittings below are for a mixer bar attached to a self contained shower. i.e not a wall. The attaching screws have snapped. I could get two new brackets, dismantle that existing one and start again or I could try and re attach via those screws, removing the broken ones from the plate and wall...
Replies
1
Views
201
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m planning to pour a 100mm deep concrete patio on 100mm hardcore. In order to achieve the same final height to line up with the rest of the patio, I...
Replies
6
Views
243
I was stupid enough not to check the position of the pipes under the tiles when installing a toilet and drilled right through the center of a 16 mm copper water pipe. I exposed the pipe by removing a ~30cm section of the plastic sleeve and a ~10 cm section of the pipe around the hole. Several...
Replies
0
Views
189
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock