H

haydencookdonna

Problem is I can only get heating, when tank stat is calling for hot water. I've got a Baxi Solo, with Drayton controller, and Honeywell room and tank stats, and a Honeywell mid position 3 port valve. Thought the valve may be sticking, so removed the head, and the valve with pliers moves freely. when moved over makes no difference, to heating or not. Voltage to room stat ok. Voltages at 3 port as follows.

ch+hw on White 234v Green 51v Orange 237v.
ch+hw off W 3v G 240V O 77v.
Hw only on. W 5.7v G 240v O 77v.
Ch only on. W 240v G240v O 80v.

Motor on head seems to move when not attached to valve body.

It's freezing, and i'm fed up drawing off hot water every hour or two, to fire up my heating system. Help Please!!!!!!!!! Thanks in advance. Greg
 
Voltages at 3 port as follows.

ch+hw on White 234v Green 51v Orange 237v.
ch+hw off W 3v G 240V O 77v.
Hw only on. W 5.7v G 240v O 77v.
Ch only on. W 240v G240v O 80v.
Presumably you mean Grey, not Green.

The actuator is faulty - that's the box on top of the valve.

You can replace the actuator on its own. Cut the cable without disconnecting the wires, then you will know where they go when fitting the new actuator.

Any plumber's merchant will stock the actuator.
 
Yes Sorry! I meant Grey and not green. If the actuator is faulty, why does removing it and moving the valve with pliers manually not ake a difference? Thanks. Greg
 
according to honeywell site faultfinding guide on mid position y plan
suspect the v4073a valve is faulty only if the valve does not operate as specified in the following checks.
Valve open for heating only
procedure
switch off mains supply.
disconnect grey and white wires from appropriate junction box terminals.
reconnect both grey and white wires to permanent live in junction box.
switch on mains supply,
valve motor should now move to fully open heating port A.
the motor should stop automatically when port A is open, and stay in this position as long as power is applied to white and grey wires.
when port A is fully open , the orange wire becomes live, to start pump and boiler.
double check by feeling that port A is getting progressively warmer.
hope this helps as although fully qualified sparks and done a honeywell course ive still to get to grips with these plans as i do not get to work on them often cheers
 
If the actuator is faulty, why does removing it and moving the valve with pliers manually not make a difference?
You said that all you can get is heating when the tank stat is calling.

A quick explanation:

HW only - boiler lit from cylinder thermostat Call terminal
HW and CH - boiler lit from cylinder thermostat Call terminal
CH only - boiler lit from orange wire

You will find that there are three wires to the same terminal: Cyl Stat Call, Valve Orange and Boiler ON.

The reason you can only have CH with HW is that the voltage on the orange is only 80V, which is not sufficient. The solution is a new actuator.
 
Status
Not open for further replies.

Reply to Honeywell 3 port valve Problems!! in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi everyone, Looking for a bit of advice, recently went to a job where heating was operating when called for however not for the hot water. I have changed the 3 port actuator Honeywell head however this doesn’t seem to have solved the issue, does this mean that the programmer is faulty? Or is...
Replies
8
Views
317
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
155
Hi, I have a Worcester 28i junior boiler that has started to lose pressure, only when using the central heating. When using hot water I have no issue, however, when running the heating the pressure drops. Im looking for some ideas on what could be causing this. I have no sign of pipe leaks...
Replies
6
Views
208
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
374
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock