In our very old listed building shop we have an Ideal Concord CX boiler.

The radiators downstairs all come on and are lovely and warm but all the upstairs are staying cold. The overheat light has come on on the boiler. I have pressed thes overheat reset button and it seems to light the boiler but after a time the light comes on. This doesn't seem to make the downstairs radiators go off as they stay warm and it just upstairs. I have today gone round and bled all the radiators which has made no difference.

i could understand the boiler being faulty if none of the radiators worked but don't get why downstairs is ok and upstairs isn't.

any ideas?
 
[DLMURL="http://www.ukplumbersforums.co.uk/im-looking-plumber-gas-engineer/"]I'm looking for a Plumber or Gas Engineer[/DLMURL]
 
You have a circulation problem, maybe zone valve,(2 port valves) or pump not working properly. This puts insufficient flow through boiler, hence cut out on over heat stat. Make sure isolation valves either side of pump are full open. The boiler itself is simple and robust and unlikely to be cause of problem.
TRVs on downstairs rads closing down and restricting flow. Temporary fix if you can't get circulation to upstairs rads. Remove downstairs TRVs and set boiler dial to 2.
 
Last edited:
You have a circulation problem, maybe zone valve,(2 port valves) or pump not working properly. This puts insufficient flow through boiler, hence cut out on over heat stat. Make sure isolation valves either side of pump are full open. The boiler itself is simple and robust and unlikely to be cause of problem.
TRVs on downstairs rads closing down and restricting flow. Temporary fix if you can't get circulation to upstairs rads. Remove downstairs TRVs and set boiler dial to 2.


Will have a look at the Manul as not sure where the valves are in the pump. I assume when you mention to set boil dial to 2 you mean the thermostat control knob
 
Your pump is likely to be a large ported version. The isolation valves will be the gate valves either side. Most likely fault is 2 port valve, somewhere along pipework not opening.
Caution:- Although turning electrics off to boiler should isolate other controls, do not take it for granted in old building and check for voltage before removing heads.
 
Your pump is likely to be a large ported version. The isolation valves will be the gate valves either side. Most likely fault is 2 port valve, somewhere along pipework not opening.
Caution:- Although turning electrics off to boiler should isolate other controls, do not take it for granted in old building and check for voltage before removing heads.


Ok thank you
 
If you say that you bled the upstairs rads and they are full, I can't see it being a stuck ball valve causing your problem. If that was the case, the system would have had to empty to a level that affected circulation.

Are they full ?


I'd be inclined to think, faulty zone valve, pump ( possibly).

Can you you give us a bit more info ?

What size of pipework is this ?
Is this a domestic property ?
What size CXA is it ?
Are all upstairs rads stone cold ?
Did this happen all of a sudden or was it gradual?
 
Last edited:
The F&E tank will be a small header tank situated above the level of the highest radiator usually in the loft, or at ceiling height if roof is flat. As above, if rads can be bled it should not be the problem,however, it is the easiest thing to check and eliminate before seeking solutions elsewhere.
 
The F&E tank will be a small header tank situated above the level of the highest radiator usually in the loft, or at ceiling height if roof is flat. As above, if rads can be bled it should not be the problem,however, it is the easiest thing to check and eliminate before seeking solutions elsewhere.


Its all above so will show your posts to somene that may know, thank you for your help
 
Its all above so will show your posts to somene that may know, thank you for your help
Invest in a heating engineer who will explain your system and service your boiler. When the thermocouple fails, which can be expected every few years, you will then have a contact to call rather than a cold shop. Essential that ventilation to boiler has not been compromised and remains adequate. Also checks to spillage and flue.
"MAY KNOW" and gas boilers don't mix too well.
 
Last edited:
You will need a commercial gas engy and not a domestic
 
You will need a commercial gas engy and not a domestic
The Concord CX 40: CX 50: CX60 are clearly identified in the MIs as commercial boilers.
However, theUser PlumbersForums.net Instead - Copy the content, don't link to it Definitions Revised April 2016, defines commercial work as:-
"gas fired commercial boilers, single or in groups greater than 70kW(net)". The implication is that with a commercial boiler less than 70kW other considerations define commercial work in the same manner that work on a domestic boiler can be commercial, dependant on pipework and meter. If this anomaly has been clarified I would welcome someone putting up the link.
 
The Concord CX 40: CX 50: CX60 are clearly identified in the MIs as commercial boilers.
However, theUser PlumbersForums.net Instead - Copy the content, don't link to it Definitions Revised April 2016, defines commercial work as:-
"gas fired commercial boilers, single or in groups greater than 70kW(net)". The implication is that with a commercial boiler less than 70kW other considerations define commercial work in the same manner that work on a domestic boiler can be commercial, dependant on pipework and meter. If this anomaly has been clarified I would welcome someone putting up the link.

My understanding is if it says commercial must be a commercial gas safe engy

But if you have 3 domestic boiler under 70kw you can work on them on a domestic ticket
 
The Concord CX 40: CX 50: CX60 are clearly identified in the MIs as commercial boilers.
However, theUser PlumbersForums.net Instead - Copy the content, don't link to it Definitions Revised April 2016, defines commercial work as:-
"gas fired commercial boilers, single or in groups greater than 70kW(net)". The implication is that with a commercial boiler less than 70kW other considerations define commercial work in the same manner that work on a domestic boiler can be commercial, dependant on pipework and meter. If this anomaly has been clarified I would welcome someone putting up the link.

Unless the manufacturer has categorised the appliance as commercial.
 
If Manufacturer says it's commercial, I would go off that, regardless of what Gas Safe's definition of things this week !
 
I thank you all for your prompt responses.
If the forward slash,/, after boilers was replaced with, &, the definition would read:-
"commercial boilers & single or groups greater than 70kW(net)"
This would remove the ambiguity.
 
I thank you all for your prompt responses.
If the forward slash,/, after boilers was replaced with, &, the definition would read:-
"commercial boilers & single or groups greater than 70kW(net)"
This would remove the ambiguity.

But would also nail it down which as you know gas safe don't like :D or they would say down to each engineers opinion
 
Status
Not open for further replies.

Reply to Help with Ideal Concord CX boiler in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi, I have 3 port value for HW & CH. Loft extension added many years ago so they added a T to go upstairs, only 2 rads up but 11 downstairs...
Replies
0
Views
272
My heating system comprises an Ideal Logic 12 boiler located downstairs and a Gledhill OV SOL cylinder located upstairs . The problem is that when...
Replies
1
Views
511
Hi Could I ask for some help with a water flow rate problem. I have good mains water pressure on the ground floor. There is no tank in the loft...
Replies
24
Views
1K
Hi everyone, New here & my first post! I have a Worcester greenstar 24i, it is a conventional boiler, it has a water tank upstairs. For the...
Replies
26
Views
2K
Hi all, Hoping to check if I have a genuine fault, or something I've overlooked. I've just moved into a my first house with a conventional...
Replies
5
Views
948
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock