Got a problem with a Worcester combi not firing in the morning from cold.

Boiler approx 14 years old.

Pressing the reset button once only gets the boiler to fire OK.

The fault is intermittent and happens about once per week.

The fault is not connected with frosty weather.

The tank had been contaminated with water and there was dross in the oil line. Flushed line and emptied water out.

Changed pump and solenoid coil, made little difference.

Any suggestions?
 
Have you tested the resistance on the Limit stats? if they are greater than 1 ohms they have a short circuit which could do this.
check aps aswell and thermistors.
clean venturi

Does it have a programmable room stat? i'd check the connections on that.

but hey i am not an oily engineer.
 
Capacitor? Losing charge/whatever it is after a cold spell?
 
I'd try a new capacitor.

But I did have one a couple of years ago, intermittent lockout on a morning and it was the transformer.
 
Last edited:
Could be a micro leak on the oil line allowing air to build up in the line whilst the boiler is off over night then clearing after the first fire until the next extended off period
 
First I would check the motor starts on the split second every time, (give it loads of starts to test, with your ear near the burner) - any slight hesitancy & I would think capacitor.
Normally Control box does that, once in a while lockout, but photocells can do weird things.
As has been suggested, check the transformer is making a strong & constant spark.
 
Status
Not open for further replies.

Reply to Worcester Combi not firing in morning in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi, Can I pick your brains? My boiler is often reluctant to start, sometimes it does, sometimes it seems that it will if the demand is from the...
Replies
19
Views
1K
W
  • Question
My Worcester Combi Boiler is not working, instead the display flashes on and off repeatedly, as shown in <a href=" View...
Replies
1
Views
435
I have a 16 year-old Worcester Bosch Greenstar 35 CDi combi boiler, which is recently suffering from intermittent issues with the hot water. I...
Replies
6
Views
3K
S
Having a few issues with my combi boiler, its 14 years old now and due to be replaced as we are building extension, but need to get another 10...
Replies
3
Views
951
  • Question
A customer rang this morning, says they have a intermittent fault on the boiler P3. Its a Worcester CDI30 I think from a past visit. I did quote...
Replies
2
Views
4K

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock