I have a 16 year-old Worcester Bosch Greenstar 35 CDi combi boiler, which is recently suffering from intermittent issues with the hot water.

I usually get the shout from a family member who’s in the shower and found there’s no hot water. If I’m near the boiler when this happens, I can see the burner light is on, and then I can hear a banging sound coming from inside the boiler which last 3-5 seconds, before the burner cuts out and it all goes quiet, the temperature (2-char) display at this time is showing a number in the 80s or 90s.

I have discovered that if I power the boiler down and leave it for 15 mins, then most of the time it comes back on and operates normally. Other times it takes a few resets.

This issue happens about once ever 5or 6 weeks.

I have had it recently serviced, and during that time, the problem occurred for the engineer also.

He speculated that it might a faulty temperature sensor/regulator (or something like that) inside the boiler.

Any one got any ideas what it might me? Any advice would be really welcome.

Thanks,
 
Do you have any other showers / problems with any taps ?
 
Can you test that shower running as it could be the shower cartridge that’s gone

The banging is a overheating noise
 
Can you clarify what you mean by “… test shower running …”? The shower is running fine, and when the boiler is turned off and on again, the hot water is fine in all taps including the shower.
 
I mean does the other shower make the boiler do the same fault ?
 

Reply to Intermittent Hot water issue with Worcester Bosch Greenstar 35 CDI in the UK Plumbing Forum | Plumbing Advice area at PlumbersForums.net

Similar plumbing topics

Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer warming up. The heat exchanger has been changed 6 months ago, so I do not believe it is that. Does anyone have any ideas on what it could be? Thanks
Replies
4
Views
212
Hi All I have a leak coming from within my Mira Elite QT shower. It seems to be flowing from behind the switching Control. Any ideas what could be causing this leak. Already Changed the Pump Elbow as one of the clips had popped which was causing a second small leak, Any idea? Is it time to buy...
Replies
0
Views
224
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
304
I was stupid enough not to check the position of the pipes under the tiles when installing a toilet and drilled right through the center of a 16 mm copper water pipe. I exposed the pipe by removing a ~30cm section of the plastic sleeve and a ~10 cm section of the pipe around the hole. Several...
Replies
0
Views
173
We are from Alberta, and I own an electrical company. I have been asked by a BC Mechanical P. Eng. to install an emergency STOP button at the man-door to the boiler room. It's intent is to 'halt' the operation of the boilers in the room should there be an emergency. He is demanding that I do...
Replies
5
Views
233
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock