trrence

Hi

I have a problem that with the CH turned off but the DHW resevoir thermostat turned on at the front of the boiler it has suddenly started to heat all the radiators in the house and the boiler is obviously constantly firing up to keep the tank hot. It has been losing pressure for a while but I think that is due to a faulty air bleed valve. Can anyone advise please?
 
I have now managed to trace the fault to the fact that the radiators are getting their hot water from the CH return into the boiler so they are feeding in reverse. However when the heating is switched of and the CH turned on it works the correct way around. Can anyone help please as it is driving me nuts?
 
I have now managed to trace the fault to the fact that the radiators are getting their hot water from the CH return into the boiler so they are feeding in reverse. However when the heating is switched of and the CH turned on it works the correct way around. Can anyone help please as it is driving me nuts?

Sounds like the solenoid for your CH is stuck open - allowing the hot water from the pump to pass??
 
Jim, thanks for responding.

I did find the fault in the end, it turned out that this boiler has 2 non-return valves fitted in the dual pump housing. The CH valve was stuck open after a summer of no use so it was just a case of flushing the system through and stripping the valves out and replacing. Job done for under a tenner which was a relief.
 
Status
Not open for further replies.

Reply to Warmflow 70/90 Boiler in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
160
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up to 1.3. I've had an engineer look inside the boiler and he can't see anything wrong. I've checked the pipes all over the house and cannot see any...
Replies
2
Views
237
P
Hi everyone, Looking for a bit of advice, recently went to a job where heating was operating when called for however not for the hot water. I have changed the 3 port actuator Honeywell head however this doesn’t seem to have solved the issue, does this mean that the programmer is faulty? Or is...
Replies
8
Views
326
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
376
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock