Hi, just about to bite the bulklet on a new boiler and radiators, Vaillant EcoTec Plus 32kW.

Is 10mm pipework to the radiators sufficient?

Thanks
 
Existing system ?
 
Hi Shaun, the existing system is 15mm i think, but its ALL being renewed. Boiler, pipes, rads.

Then no 15mm copper would be best especially with part L of efficiency being law now where you have to design systems to be effective have they done a heat loss ?
 
Hi Shaun, the existing system is 15mm i think, but its ALL being renewed. Boiler, pipes, rads.
Depending on number of rads, 15mm copper (13.6mm ID) is fairly restrictive (compared to 22mm) requiring greater pump head/energy if you are referring to the main flow/returrn piping.
 

Reply to Vaillant EcoTec - 10mm pipework to radiators? in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

Copper pipes, I think its fair to say, is not what it used to be, the copper is getting thin while the cost is going up. Meanwhile, plastic Pushfit seems to be getting better and better, cost and convenience was always better, but now the quality is to, have we reached a stage where plastic will...
Replies
2
Views
231
Hi. I need a new toilet supply line but don’t know the size type of the fitting at the shut off valve. It is not 3/8 compression. It is a plastic nut about the same size as the one going into the cistern but has a different thread. Attached is a photo. Can you advise. Thanks.
Replies
2
Views
182
I have an ideal vogue max S18 boiler and I’m considering fitting auto balancing TRVs, my question relates to the boilers pump. I see a boiler pump menu for either 70% or 100%, so, is the pump set at either one of two fixed speed percentages or does the pump actually vary speed, (modulate)...
Replies
1
Views
139
We are from Alberta, and I own an electrical company. I have been asked by a BC Mechanical P. Eng. to install an emergency STOP button at the man-door to the boiler room. It's intent is to 'halt' the operation of the boilers in the room should there be an emergency. He is demanding that I do...
Replies
5
Views
242
Recently had a Viessmann Vitodens combi boiler installed, quite often when the adjacent cold mixer tap is opened the boiler starts for a few seconds! Can anyone tell me what is causing this? And how to cure?
Replies
3
Views
196