Johnny

hi all.

i got called to a house today where water is dripping from the tundish

iv checked the TPRV valve and recharged the expansion vessel with no success

iv only recently gained my g3 and i was sure this would of sorted the problem but it has'nt

im confused of what to try next??

All thoughts would be appreciated

thanks
Johnny
 
first identify where the water is coming from?? this may mean removing pipework to access the prv and tprv valves before they join together.

Also check the pressure reducing valve is working and not letting too much pressure passed.

if the expansion vessel is set correct and the pressure reducing valve is good then its most likely the valve thats passing is faulty.
 
have the customers been messing round the valve as sometimes they dont re-seat properly
 
Status
Not open for further replies.

Reply to unvented system problem! in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

hello we have an unvented system. we have an issue where the hot water is hot for 10 seconds and then luke warm, turn off taps / wait and turn back and it repeats itself. had boiler checked and told it was the expansion vessel. Had the expansion vessel drained and recharged. plumber told me...
Replies
5
Views
689
Morning All I have a Megaflo unvented cylinder . Water had been dripping into the tundish so I tried to recharge the air gap, but when I went to turn the pressure relief valve it would not turn at all, as it usually would. My shower has been dripping in the bathroom next door , could in anyway...
Replies
1
Views
411
Potable water unvented expansion vessel needs replacing - water is coming down the tundish. What else needs to be replaced. Does the enginneer need a G3 unvented certificate to do this work and what are the consequences if he does not have one
Replies
4
Views
914
Hi, I have an unvented water heater which for some reason every year causes me issues. At the end of 2023 I noticed that the pressure valve gauge was going up when the water tank was switched on. My local plumber came and re-pressured the expansion vessel as it was flat, afterwards we tested...
Replies
5
Views
498
Good afternoon, I am experiencing a pressure issue with my heating system and was hoping to receive additional insight as to what the problem could be. We have a biomass boiler and stratification tank set up and recently had an issue with boiler pressure dropping off when the system was cold...
Replies
9
Views
366
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock