My custard wants us to put a tall towel rail in his utility room. Single storey extension with a loft directly above. The new (oil) boiler is in the same room. Vented system. F&R go up from the boiler and along the loft.
He wants the towel rail piped from above onto the top of the rad.
I cant see any reason not too, we could Tee AAVs on the pipe above - does this sound ok?
Thanks
 
Ts fine BUT

you'll struggle to get it to heat at the bottom.
it will track through the top.

so providing it isnt a fancy silly one.
you can use a union on one side and solder a length of 15mm into it to act as a diffuser to the bottom.
 
Ooh that's clever, solder a length of 15mm into a compression coupler and drop that onto the flow you mean? Just a lock shield on the return?
 
If you soldered a length of 15mm onto a 15mm-1/2" comp f/i you can then wind a rad valve on as well. So still have trv and lock shield. That's the theory at least.
 
You don't need AAVs in the loft if you are teeing into the flow & return to boiler at same level or less.
Any air will go into rest of system. AAVs leak anyhow if they get a lot of heat & also they suck in air on the return pipe when circulating pump is on.
 
Just a 3/4 rad union and lockshield.

Go into your merchants and ask to look at the union lockshields.
See which one will fit in some 15mm tube :)
ImageUploadedByTapatalkHD1426612083.834851.jpg

The bore should be big enough on some to get it in and solder it

Then wind it into the rad
 
Did it today, worked a treat and yes thanks Pheonix, we still put a thumb vent on it to let the air out of the rad save most of it gettin upstairs. cheers all.
 
Status
Not open for further replies.

Reply to Rad fed from above... in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

I need to extend my central heating from my newly built extension in to the old part of my house. I need to feed 3 rads in separate bedrooms on...
Replies
2
Views
169
Hi all, Got a nightmare situation with a central heating system I recently adopted. It's an open vent system with a combined F&E pipe, with a...
Replies
17
Views
2K
E
I reckon if I did a survey of 100 heating engineers, asking what would they recommend for heating a granny annexe being built onto the side of my...
Replies
0
Views
260
eco-heating options
E
Sorry I have sort of asked this before, tried professionals but not great 1st experience hence DIY attempt attempt again. 2 completely cold...
Replies
3
Views
671
Hi there. I’m currently basically re plumbing my downstairs having already done most of the upstairs. Valiant 35kw boiler in the loft CH F + R...
Replies
0
Views
312
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock