Custard went off on holiday, came back boiler didn't fire up.
EA code, reset -nothing. Called me, got there, checked for gas, checked condensate pump ok, took cover off to check ignition and the flame rectification lead was disconnected? How would this happen?
Any clues? igotnoidea
Super Moderator
Staff member
S. Mod
Plumber
Gas Engineer
Subscribed
Messages
34,363
Solutions
2
Sometimes they go loose and with the heat they could pop / not make contact
How did they feel when you pressed them back on ? You can close the spring clips a bit to tighten them
Warning If Your Asking Advice About Repairing A Fuel Burning Appliance, Dont Be Alarmed / Put Off If We Ask For Your Registration
Plumbers Arms member
Plumber
Gas Engineer
Sometimes they go loose and with the heat they could pop / not make contact
How did they feel when you pressed them back on ? You can close the spring clips a bit to tighten them
Fine clipped on with a satisfying click.
Super Moderator
Staff member
S. Mod
Plumber
Gas Engineer
Subscribed
Messages
34,363
Solutions
2
Fine clipped on with a satisfying click.
Strange then maybe there were never fully seated and slowly started to wobble off
Warning If Your Asking Advice About Repairing A Fuel Burning Appliance, Dont Be Alarmed / Put Off If We Ask For Your Registration
Plumbers Arms member
Plumber
Gas Engineer
Strange then maybe there were never fully seated and slowly started to wobble off
Yeah weird, will check in future services/ visual inspections. cheers
Plumbers Arms member
Plumber
Gas Engineer
Your maybe being filmed by rogue traders , hope u never said it was major job lol
Esteemed
Plumber
Gas Engineer
Subscribed
Had a few not fully seated on a service. How was the burner seal?? Any signs of heat damage anywhere?
Esteemed
Plumber
Gas Engineer
Subscribed
Plumbers Arms member
Plumber
Gas Engineer
Had a few not fully seated on a service. How was the burner seal?? Any signs of heat damage anywhere?
DIDN'T check!! I didn't *work* on the boiler before then, only opened up case and found lead disconnected~ THO' they recently had boiler serviced by another company, the landlord has a contract with-details not known to me.. maybe they didn't put the lead back properly IF they even took it off to service?
Reply to odd one, worcester greenstar, 40CDi, classic, regular in the Plumbing Jobs | The Job-board area at PlumbersForums.net
Hi,
I have a worcester greenstar 30 CDi Classic regular.
The central heating is working fine but the water is not heating.
If i put the system...
I am a retired gas engineer. Corgi and Domestic Electrics + Building Surveyor. I have a Greenstar CDI 35kw that I fitted in my own home 15 years...
In our Village Hall we have a Ideal Concord CXS/SD40/H central heating boiler. This was installed new when we had an extension built and the...
Hi
Can anyone help?
I've got a problem with an intermittent EA fault on a Worcester Greenstar 38CDi Classic GC 47-406-38. I was called out to it...
My Worcester Greenstar 29 CDI boiler made a loud bang earlier today, and has now stopped working.
It is flashing the 'EA' error code, which...