Discuss I have a nu-heat UHS installed in 2006. Recently I’ve noticed a dark orange coloured substance appearing in 2 of the flow in the USA area at PlumbersForums.net

Messages
4
Can anyone help me identify the cloudy orange contaminant and suggest a remedy?
 

Attachments

  • 0CCD1677-6EED-4FB1-BC98-5EC2C92F25B9.jpeg
    0CCD1677-6EED-4FB1-BC98-5EC2C92F25B9.jpeg
    415.9 KB · Views: 27
  • D5AC6738-7575-4CCD-8812-C175855B6F92.jpeg
    D5AC6738-7575-4CCD-8812-C175855B6F92.jpeg
    429.9 KB · Views: 25
  • 51F5FE56-C5CA-4633-A185-5E06B119C19A.jpeg
    51F5FE56-C5CA-4633-A185-5E06B119C19A.jpeg
    400.7 KB · Views: 26
It is corrosion caused by oxygen in the heating system it needs flushing out throughly and a quality biocide chemical treatment added like Sentinel x700 . Kop

Why is it so much worse on two of the gauges?

The left gauge takes 4 litres, the right one takes 2.5 and the middle 2 are much lower flow. I’ve hardly had the system on since I noticed it in case I worsened a problem that might be resolved better if I didn’t. Thank you very much for your comment. Do you have an idea where the corrosion is coming from? The boiler does gurgle for a few seconds after starting up.
 
It is corrosion caused by oxygen in the heating system it needs flushing out throughly and a quality biocide chemical treatment added like Sentinel x700 . Kop
Thank you very much for that reply. Do you know where the corrosion comes from? The oil fired boiler does gurgle for about 4 seconds on initial start up.
 
Your oil fired boiler is just a steel jacketed box with a burner firing into it, the combination of steel and water and heat without a corrosion inhibitor added will cause rust and sludge to form in the system, your system is long overdue a water change and chemical treatment this should be done every 5 years as a rule Do you have a service agreement ? when was the boiler last serviced ? it is now part of a service to check the water quality and pH level and address any issues found . Regards Kop
 
Last edited:
Your oil fired boiler is just a steel jacketed box with a burner firing into it, the combination of steel and water and heat without a corrosion inhibitor added will cause rust and sludge to form in the system, your system is long overdue a water change and chemical treatment this should be done every 5 years as a rule Do you have a service agreement ? when was the boiler last serviced ? it is now part of a service to check the water quality and pH level and address any issues found . Regards Kop
Thanks for the info Kop. My boiler is serviced annually but I’VE never been able to get a plumber very interested in servicing the UHS though items have been changed when they’ve been malfunctioning. The boiler feeds both the UHS and upstairs radiators and I’ve checked that the corrosion inhibitor appears to be okay in the rads and the radiator water shows clear. Sentinel X100 is used but I wonder if this suits both the steel rads and the plastic UHS? Any idea what might specifically cause the contaminant in the UHS without discolouring the rad circuit?
 

Attachments

  • 423C373D-05F5-4679-96A6-6B5FA41C2A3E.jpeg
    423C373D-05F5-4679-96A6-6B5FA41C2A3E.jpeg
    259.1 KB · Views: 10
  • E0BBE8BA-0CC5-41F6-A376-F298CE45DF21.jpeg
    E0BBE8BA-0CC5-41F6-A376-F298CE45DF21.jpeg
    233.7 KB · Views: 9
The suggestion to use X700 as well is that while X100 will work as a corrosion inhibitor, X700 will prevent bacterial growth at the low temperatures found in the UFH section of your system. I'm not sure exactly what that has to do with the rust (on the gauge springs?) however, but I suppose there is the possibility that the brown is some form of bacterial growth.
 

Reply to I have a nu-heat UHS installed in 2006. Recently I’ve noticed a dark orange coloured substance appearing in 2 of the flow in the USA area at PlumbersForums.net

Similar plumbing topics

Recently had a Viessmann Vitodens combi boiler installed, quite often when the adjacent cold mixer tap is opened the boiler starts for a few seconds! Can anyone tell me what is causing this? And how to cure?
Replies
3
Views
196
Hi they used to say as a last resort you could discharge the D2 pipework at high level and turn it back to the wall. Similar to a combi boiler. I have just looked back through the regs this seems to have changed and it isn't mentioned now. It now mentions if at high level it should be discharged...
Replies
11
Views
246
Hi, My current hot water system needs to be replaced. Anyone got any suggestions or can recommend any plumbers around Derrimut area that won't rip me off? An office guy recommended me to apply for government rebates and get it installed through timetosave.com.au. How reliable is this...
Replies
6
Views
285
Hi everyone, Looking for a bit of advice, recently went to a job where heating was operating when called for however not for the hot water. I have changed the 3 port actuator Honeywell head however this doesn’t seem to have solved the issue, does this mean that the programmer is faulty? Or is...
Replies
8
Views
250
Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer warming up. The heat exchanger has been changed 6 months ago, so I do not believe it is that. Does anyone have any ideas on what it could be? Thanks
Replies
4
Views
221
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock