In the install manual for Atag condensing system boilers, it says that the 3way valve must be fitted to the return. At present I have an open vented fully pumped system. And the 3way is fitted to the flow as you would expect. So I rang Atag dealer and asked why fit it to the return and I was told it prevented negative pressure and water hammer. When I mentioned this to some plumbers who fit other types of condensing boilers it was a suprise to them too. Any advice would be appreciated.
 
i take it they mean to avoid negative pressure inside the boiler then. Where does the pump go then? If thats what the manufacturer recommends, thats what you should do
 
Just cleared it all up with Atag engineer.......it's only when using the Atag Valve with weather compensating. If you are not using the outside temp monitor or the Atag 3way valve which apparently rattles when positioned on the flow so they now put on the return.
 
If the MI says must be fit to the return then the 3 port must be fit to the return
 
Status
Not open for further replies.

Reply to Atag 3way valve on return!! in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hello plumbers in my internet. So the Mrs want a spray mixer tap in the kitchen as we had two separate taps. I changed the tap for a temporary two hole mixer but the cold water pressure is high mains fed and the hot is low pressure immersion tank fed. I've been trying to find info on what I...
Replies
2
Views
166
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
160
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
376
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock