hi this has us a bit baffled our heating systems is cold water tank and little f e tank in the loft immersion cylinder in airing cubard and boiler in kitchen
The problem was the overflow to the cold tank keep dripping so I replaced the ballcock turned mains on watched it fill up and cut off nicely job done
Next day noticed overflow dripping went in loft looked in cold tank ball valve under water so turned isolating valve on mains in ran a few taps so water level dropped left it isolated over night the next day the water level was right up again to the overflow
The cold feed pipe from the bottom of the cold tank goes into bottom of cylinder now that pipe gets hot all the way back up to tank can even see in the tank swirling like it’s back filling with hot but run any hot tap and the cold feed pipe goes ice cold again for about a hour the heats back up
Iv had two plumbers look and are not sure
All taps are mixer type no taps or showers have been changed in last 4 years
Any help or ideas much appreciated I apologise for long post just trying to give as much details
 
Is your hot water hotter than usual?

Is your heating system fully pumped? or gravity for hot water circuit and pumped for heating? If it's a gravity system your boiler thermostat could have failed. This will overheat the water.

Alternatively do you use the immersion heater? Has it been left on by mistake (if it's on a high setting and left on it could be expanding your hot water excessively)?
 
If you have a hot water cylinder fed from that cold water cistern, the coil in the cylinder could be leaking. If so, the water from your heating system could be pushing into the coil from the small F&E and then passing through the leaking coil and up the cold feed into the cold water storage cistern.

If the ballcock of the F & E is not dripping or the water level in the F & E is lower than the water level in the cold water storage cistern, then I'm probably wrong in the above paragraph.

I like your approach to actually finding the fault, by the way.
 
Is your hot water hotter than usual?

Is your heating system fully pumped? or gravity for hot water circuit and pumped for heating? If it's a gravity system your boiler thermostat could have failed. This will overheat the water.

Alternatively do you use the immersion heater? Has it been left on by mistake (if it's on a high setting and left on it could be expanding your hot water excessively)?

At a guess I think the system is pumped there is a pump near bottom of cylinder

We did leave the immersion heater on for a few weeks straight just so we didn’t have to keep remembering to put hot water on
 
Th
If you have a hot water cylinder fed from that cold water cistern, the coil in the cylinder could be leaking. If so, the water from your heating system could be pushing into the coil from the small F&E and then passing through the leaking coil and up the cold feed into the cold water storage cistern.

If the ballcock of the F & E is not dripping or the water level in the F & E is lower than the water level in the cold water storage cistern, then I'm probably wrong in the above paragraph.

I like your approach to actually finding the fault, by the way.

Thanks

The level in F E tank never moves I put a mark on the side and water level still there weeks later

The two tanks are side by side on a platforms the cold shut off level is a fair bit higher than F E water level

I worry about if it’s over flowing and overflow pipe iced over then the tank would over flow hope that made sense lol
 
At a guess I think the system is pumped there is a pump near bottom of cylinder

We did leave the immersion heater on for a few weeks straight just so we didn’t have to keep remembering to put hot water on

Thinking heating system is pumped
HW gravity also should have mentioned we never switch immersion on just use boiler for hot water
 
74F08ECF-6258-4EBA-95B5-8999DA08ADFA.jpeg
No just the same it’s not discoloured either
Would any pictures be of any help in loft or cylinder layout
 
Thanks for the pic, your system is fully pumped - it's great to see the pipes in the cupboard insulated as well!

BTW did you replace the float "ball" when you replaced the ball cock? What I'm getting to is the float "ball" filling with water and opening the valve?
 
Thanks for the pic, your system is fully pumped - it's great to see the pipes in the cupboard insulated as well!

BTW did you replace the float "ball" when you replaced the ball cock? What I'm getting to is the float "ball" filling with water and opening the valve?

I didn’t replace the ball I gave it a good clean and shaked it couldn’t hear any water inside it but there only cheap I’ll get on tomorrow and give that a try
 
A mixer (shower or tap) can be passing mains cold water into the hot pipework and it will back fill through copper cylinder and up the cylinder feed pipe and into cold tank.
Monobloc mixer tap, like on a kitchen or basin are suspect.
Water passes through them while they are turned off if they have a fault. Even a pin hole of a connection inside the mixer tap between gravity hot & high pressure mains cold will cause an overflow on cwt.
 
On another point, - that shower pump has been installed completely wrong. Looks diy. I know this is nothing to do with the overflow.
The pump manufacturers instructions have been ignored obviously.
Pump would be best on floor in airing cupboard. Pipework is wrong - hot from cylinder and pipes from cwt. Ballvalve is supposed to be opposite side of tank to outlets.
 
A mixer (shower or tap) can be passing mains cold water into the hot pipework and it will back fill through copper cylinder and up the cylinder feed pipe and into cold tank.
Monobloc mixer tap, like on a kitchen or basin are suspect.
Water passes through them while they are turned off if they have a fault. Even a pin hole of a connection inside the mixer tap between gravity hot & high pressure mains cold will cause an overflow on cwt.

Iv isolated each cold feed to every mixer tap one at a time for a day at a time and not used the tap Keep checking the CW tanks still over flows
Also tryed running the hot on each tap and touching the bare copper pipe then turn tap to cold to see if the hot copper turns cold but every one stayed hot

Many thanks for your help the second plumber said the shower pump was wrong surprised it worked
 
If heating tank isn’t filling in, then it must be water coming from mains through a mixer. Check heating tank definitely not filling in by isolating water supply to it or tie heating tank ballvalve up.
Also check if you have any blending valves anywhere.
 
A mixer (shower or tap) can be passing mains cold water into the hot pipework and it will back fill through copper cylinder and up the cylinder feed pipe and into cold tank.
Monobloc mixer tap, like on a kitchen or basin are suspect.
Water passes through them while they are turned off if they have a fault. Even a pin hole of a connection inside the mixer tap between gravity hot & high pressure mains cold will cause an overflow on cwt.
Good one, and that would explain the symptoms - hot water flow up the cylinder feed pipe into the main header tank.
He good test it by closing the cold mains valve for a while. Fill a few saucepans for drinking water, and use the header tank for everything else. If he can isolate just the cold supply to the kitchen sink tap so much the better.
 
If heating tank isn’t filling in, then it must be water coming from mains through a mixer. Check heating tank definitely not filling in by isolating water supply to it or tie heating tank ballvalve up.
Also check if you have any blending valves anywhere.

Just looked in both F E and CW and water level in both looks good
I have isolated the F E tank is it still ok to have heating and hot water on or leave off while I see what happens in F E


Many thanks
 
Last edited:
Just looked in both F E and CW and water level in both looks good
I have isolated the F E tank is it still ok to have heating and hot water on or leave off while I see what happens in F E


Many thanks
Yes, but best to keep an eye on the level just in case. It shouldn't drop (except the normal fluctuation from hot to cold due to thermal expansion).
 
Yes, but best to keep an eye on the level just in case. It shouldn't drop (except the normal fluctuation from hot to cold due to thermal expansion).

Just been up to look F E about 3mm lower than it was (Been isolated for four hours) with heating and hot water on CW tank was a little higher Not near overflow but was filling from bottom could see swirls
So we have five mixer taps in the house on three of them Iv turned the cold isolating valve off no better
Kitchen and bath to try don’t think kitchen has isolation valve
Thanks
 
One way to check is turn all hot water off and disconnect hot below sink to see if mains water passing through that tap
 
A part blockage due to scale etc in the outlet of a single flow mixer tap could cause this if you have mains fed cold water, all mixer taps that are supplied from the cold mains should be bi-flow (duel flow) type which would prevent this happening.
 
A part blockage due to scale etc in the outlet of a single flow mixer tap could cause this if you have mains fed cold water, all mixer taps that are supplied from the cold mains should be bi-flow (duel flow) type which would prevent this happening.

I think all cold taps are mains fed how could I check to see if mine are bi flow or single
F E tank been isolated 24 hours now no real movement 3mm up last night then back down today could this rule out immersion coil split/hole
 
Yes, looks like it isn’t your heating system mixing with your water.
Just keep an eye on heating tank level though.
Probably your kitchen mixer would be my first check
 
Yes, looks like it isn’t your heating system mixing with your water.
Just keep an eye on heating tank level though.
Probably your kitchen mixer would be my first check

Thanks going to try what you suggested turn hot water gate valve off in airing cupboard then disconnect hot feed to kitchen mixer tap then should I try running the cold side of the tap if it leaks out of were the hot flexi screws into the bottom then
I’ll just replace for a new tap
Does that sound ok or have I missed something

Thanks
 
Yes, that’s more or less all you need to do, but the gate valve in airing cupboard that turns your hot off might break inside leaving you without hot water, so be prepared for that.
If it is a valve that has been used recently without trouble, then maybe you will be ok.
We plumbers prefer full flow large lever valves
 
I think all cold taps are mains fed how could I check to see if mine are bi flow or single
F E tank been isolated 24 hours now no real movement 3mm up last night then back down today could this rule out immersion coil split/hole
A bi-flow tap mixes the hot & cold water once it has left the spout, single flow taps mix the water in the spout so a blockage could result in backflow as the mains cold water is at a higher pressure.
 
Status
Not open for further replies.

Reply to Cold water tank in loft overflowing in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hello plumbers in my internet. So the Mrs want a spray mixer tap in the kitchen as we had two separate taps. I changed the tap for a temporary two hole mixer but the cold water pressure is high mains fed and the hot is low pressure immersion tank fed. I've been trying to find info on what I...
Replies
2
Views
140
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
339
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
139
Our kitchen mixer tap has started dripping. Like so much of the plumbing in our almost new build bungalow, it is lacking! The plumber didn't install any isolating cocks in the H&C feed to the tap so how can I identify which of the valves is passing? Shut the whole H&C water system down?
Replies
12
Views
340
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up to 1.3. I've had an engineer look inside the boiler and he can't see anything wrong. I've checked the pipes all over the house and cannot see any...