Plumber is here now. He said 53 degrees flow is fine for the flow. He said 70 degrees would be too hot. That means the radiators must be oversized as the are delta 50 rads.
 
Ok works completed. 58 degrees on the flow and the return is 52 degrees. One thing we noticed, radiators can be bleed of air and the system has no air anymore. Silent central heating for the moment. Radiators are much more hot to feel. Still don't think they are running at full potential and to be honest he should have atleast balanced them as there are temperature variations between flow and return between all rads.

I will leave heating on for atleast an hour a day to see if air keeps returning in the system.

Does anyone think that the flow temps should be higher but don't forget that we have district heating system. Input Temp is around 80 degrees so not sure if heat exchanger can heat the cold water to 70 degrees. Engineer mentioned that the water in the radiators would be higher than what he is seeing on his thermal camera.
 
You have, (58+52)/2)-20, "35 deg" rads which will output 63% of 50 deg rads, the rads may have been over sized to take account of this, who knows?. If you gave dimensions of a room and the dimensions of its rads then someone on here would have a fair idea IMO as to under sizing or not.
I see you have 2 rads in a 30 M2 L shape so maybe you can just post the dimensions of those two rads.
 
Last edited:
My main concern now is my daughters room. I believe bthey have have undersized the radiator as it's only 600 X 600. It's stelrad compact K2 I believe. Output is 3100 BTU. Room size is 14.25 by 11.25 ft.

Room has two external walls and one of these has a French door leading to balcony which is around 2m by 2m in size.

Problem is I don't think they will ever change the size of the radiator.

Open Plan will be ok as we also cook there.
 
ask for the heatloss calcs
 
My main concern now is my daughters room. I believe bthey have have undersized the radiator as it's only 600 X 600. It's stelrad compact K2 I believe. Output is 3100 BTU. Room size is 14.25 by 11.25 ft.

Room has two external walls and one of these has a French door leading to balcony which is around 2m by 2m in size.

Problem is I don't think they will ever change the size of the radiator.

Open Plan will be ok as we also cook there.

From your info you have a 0.91 kw rad ("50deg") heating 14.9 m2, but because of lower running rad temps you only have a 0.57 kw rad ("35 deg") and I doubt very much if this was the design heat loss for this 14.9 m2 (38watts/m2).
You would need a ~ 60% bigger rad to compensate if a 50 deg rad was their standard.
As stated above it would be nice to get the heat loss calcs.
 
Last edited:
Hi, I never responded but thanks for everyone's input, help and advice. Eventually might change the radiator in my daughter's room but will leave it for now. Developer never ever responded with heat loss calculations. I think it is simple enough to upgrade the radiator and be done with it.
 
Yes it matters return should be at the bottom so when the water cools it flows into the return
Not necessary at all .
One of the biggest myths of small bore heating . TBOE doesn’t care what the configuration is and the so called “ traditional wisdom” of putting the return at the bottom or lower pipework is flawed.
Correctly as you state , as the hot flow gives up it’s heat it becomes less buoyant more dense and will sink , but there is no counter convective interaction and although the efficacy is improved with TBOE , it would improve further with Hot flow at bottom return at top . Why ? Because it created counter flow , which is far more efficient in mixing flows and therefore gives greater thermal efficiency and efficacy . Heat from the convective sense naturally wants to rise . It will of course give up heat becoming cooler and want to fall back down . If the hot feed is at bottom, it counter flows and blends far better . The remaining heat wants to rise anyway so it’s sensible to return from the top , not forgetting it’s still relatively hot and the useful heat exchange has taken place in the rad.
All large heat exchangers function with counter flow
 
How hot would the return be ?
 
Not necessary at all .
One of the biggest myths of small bore heating . TBOE doesn’t care what the configuration is and the so called “ traditional wisdom” of putting the return at the bottom or lower pipework is flawed.
Correctly as you state , as the hot flow gives up it’s heat it becomes less buoyant more dense and will sink , but there is no counter convective interaction and although the efficacy is improved with TBOE , it would improve further with Hot flow at bottom return at top . Why ? Because it created counter flow , which is far more efficient in mixing flows and therefore gives greater thermal efficiency and efficacy . Heat from the convective sense naturally wants to rise . It will of course give up heat becoming cooler and want to fall back down . If the hot feed is at bottom, it counter flows and blends far better . The remaining heat wants to rise anyway so it’s sensible to return from the top , not forgetting it’s still relatively hot and the useful heat exchange has taken place in the rad.
All large heat exchangers function with counter flow
Having the return from the Top certainly made a big difference in the few tests I carried out over 3 years ago
It seems pretty clear that convection just won't work properly in any system with the return on the top. In the BTOE there are 8 readings between 45C and 38C, the flow just seems to flow upwards to the top of the rad and then partially short circuits out the other end whereas in the other two it flows along the top of the rad and then drops down in parallel flow paths and out the return, (makes sense I suppose).View attachment 37636
1675794568639.png
 
I think that what Jonny_boy is saying that the conventional flow-top return-bottom arrangement results in a stratified temperature distribution but putting the flow in at the bottom and return out from the top would disrupt this pattern resulting in a higher average temperature of the radiator surface.

While this might be true for some designs of radiators, if you try it in practice with a typical domestic radiator the flow scoots up the inlet side, along the top and straight out of the return. This is the 'conventional wisdom' and @John.g's measurements seem to confirm it.

The flow speeds inside a radiator are really quite low and I have no difficulty believing that convection forces play a significant, maybe dominant, role even in a pumped system.
 
Last edited:

Reply to TBOE radiators in new build incorrectly piped in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Our kitchen mixer tap has started dripping. Like so much of the plumbing in our almost new build bungalow, it is lacking! The plumber didn't install any isolating cocks in the H&C feed to the tap so how can I identify which of the valves is passing? Shut the whole H&C water system down?
Replies
12
Views
336
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
137
Hello plumbers in my internet. So the Mrs want a spray mixer tap in the kitchen as we had two separate taps. I changed the tap for a temporary two hole mixer but the cold water pressure is high mains fed and the hot is low pressure immersion tank fed. I've been trying to find info on what I...
Replies
2
Views
130
Copper pipes, I think its fair to say, is not what it used to be, the copper is getting thin while the cost is going up. Meanwhile, plastic Pushfit seems to be getting better and better, cost and convenience was always better, but now the quality is to, have we reached a stage where plastic will...
Replies
2
Views
250
I was stupid enough not to check the position of the pipes under the tiles when installing a toilet and drilled right through the center of a 16 mm copper water pipe. I exposed the pipe by removing a ~30cm section of the plastic sleeve and a ~10 cm section of the pipe around the hole. Several...