It can be fitted no problem but the switching needs to be VOLT FREE
The only stats on boilers are to control the water temp. What you will have though is a built in timer.
Here is how most should be wired
Wires from inbuilt clock are to larger block to right. Remove 4 wires (brown L, blue N and 2 blacks and cut back.
Take 4 core from receiver to boiler.
Wire receiver to boiler as follows
L - brown on boiler block
N - blue
The next 2 wires are called different things on different receivers (could be A,B, 1,2 etc)
Com - 1st black on left pos 1
Demand- 2nd black.
What you have to make sure of is that the stat has volt free switching. What this means is no mains voltage (230v) is applied to any of the switch wires C,D 1,2 A,B etc.
If you apply 230v to the stat connections on this boiler it will cost you in the region of £250.