Turning up the boiler stat/flow temp is no good as the manifold TMV will still hold its setpoint, you can turn up the manifold(s) TMV setpoint by 5C (as long as no damage to your flooring), if you get a return of 38/40C then IMO should be OK and I know of of a few condensing boilers that are running this way for years with no major problems.
If you really want control of the boiler return temp then a bypass of some sort between the flow and return is required (or maybe a low loss header). Don't know if its a regular method but I think a two port TMV (between the flow & return) with a capillary sensor on the return set to 45c or whatever should do the job with the minimum of trouble.
If you really want control of the boiler return temp then a bypass of some sort between the flow and return is required (or maybe a low loss header). Don't know if its a regular method but I think a two port TMV (between the flow & return) with a capillary sensor on the return set to 45c or whatever should do the job with the minimum of trouble.