I think that's what's happening, i just can't work out why the pump is running so fast to circulate water around the closest circuit to the boiler. I'm stumped :))

Below pics of pump operating different circuits, notice the ktichen manifold RPM compared to laundry and Radiators that have a longer circuit.

Also done an experiment with rads and kitchen (troubled manifold) both calling for heat, boiler flow never got over 43.6 degrees after 40 mins of running, i turned ufh manifold off and within 2.39 mins flow temp had risen 13.4 degrees to 57.

I am now thinking if the pump if pushing water that fast through flow to manifold is this indicating a blockage in the flow pipe?


IMG_9364.jpg



IMG_9393.jpg
IMG_9413.jpg
Its may cause erratic operation of the UFH manifold TMV because you have hot water at high pressure on one side of the TMV and much lower pressure on the other side coming from the cold manifold return.
 
Can you give me your observed/estimated readings for the two UFH manifolds, ie, boiler/manifold flow temp, manifold(s) flow (mixed) temps & return temps & the total manifold flow rates.
Also a rough idea of the total rated rads output and the actual/estimated dT.

Does that pump display only the RPM in that box?, ie some can display the calculated flowrate if selected.
 
Can you give me your observed/estimated readings for the two UFH manifolds, ie, boiler/manifold flow temp, manifold(s) flow (mixed) temps & return temps & the total manifold flow rates.
Also a rough idea of the total rated rads output and the actual/estimated dT.

Does that pump display only the RPM in that box?, ie some can display the calculated flowrate if selected.
(BOILER FLOW TEMP SET TO 65)

Kitchen ufh manifold (troubled)
Boiler/manifold flow temp 48 c
Manifold mixed flow temp 45
Manifold return temp 35
Total flow 28.5 LPM

Laundry manifold
Boiler/manifold flow temp 70 c
Manifold mixed flow temp 45
Manifold return temp 35
Total flow 16.5 LPM

Total Radiator output 19kw
DT across Rads 12 degrees
Flow 70
Return 58

I will check the pump re the calculates flow
 
OK here are my numbers.
Why is the boiler temp so low at 48C (SP 65C) assuming a heat demand of "only" 19.88kw for the kitchen manifold??.
You can see why the Blr pump speed is far greater on the kitchen manifold vis the Laundry manifold due to the different flowrates required, 21.92LPM vis 4.71LPM respectively.

The very low pump speed on rads only at 891LPM for a flowrate of 19.23LPM is indeed puzzling, would have expected it somewhere up to 1700/1800 RPM based on the blr circ pump speed of 1870 RPM required for the kitchen manifold with its blr circ pump flowrate of 21.92LPM.




(BOILER FLOW TEMP SET TO 65)

Kitchen ufh manifold (troubled)
Boiler/manifold flow temp 48 c
Manifold mixed flow temp 45
Manifold return temp 35
Total flow 28.5 LPM
Blr circ pump flowrate, 21.92LPM (Manifold output, 19.88kw) Pump RPM 1870.

Laundry manifold
Boiler/manifold flow temp 70 c
Manifold mixed flow temp 45
Manifold return temp 35
Total flow 16.5 LPM
Blr circ pump flowrate, 4.71LPM (Manifold output, 11.50kw,) Pump RPM 1080.


Total Radiator output 19kw
DT across Rads 12 degrees
Flow 70
Blr circ pump flowrate, 19.23LPM (Rads output, 16.10kw, based on mean rad temperatures)
Pump RPM 891





Return 58
 
OK here are my numbers.
Why is the boiler temp so low at 48C (SP 65C) assuming a heat demand of "only" 19.88kw for the kitchen manifold??.
You can see why the Blr pump speed is far greater on the kitchen manifold vis the Laundry manifold due to the different flowrates required, 21.92LPM vis 4.71LPM respectively.

The very low pump speed on rads only at 891LPM for a flowrate of 19.23LPM is indeed puzzling, would have expected it somewhere up to 1700/1800 RPM based on the blr circ pump speed of 1870 RPM required for the kitchen manifold with its blr circ pump flowrate of 21.92LPM.




(BOILER FLOW TEMP SET TO 65)

Kitchen ufh manifold (troubled)
Boiler/manifold flow temp 48 c
Manifold mixed flow temp 45
Manifold return temp 35
Total flow 28.5 LPM
Blr circ pump flowrate, 21.92LPM (Manifold output, 19.88kw) Pump RPM 1870.

Laundry manifold
Boiler/manifold flow temp 70 c
Manifold mixed flow temp 45
Manifold return temp 35
Total flow 16.5 LPM
Blr circ pump flowrate, 4.71LPM (Manifold output, 11.50kw,) Pump RPM 1080.


Total Radiator output 19kw
DT across Rads 12 degrees
Flow 70
Blr circ pump flowrate, 19.23LPM (Rads output, 16.10kw, based on mean rad temperatures)
Pump RPM 891





Return 58
The boiler will not get any higher than 48 degrees with heat only on kitchen manifold, I have again just now watched it SP is 65, flow no higher than 48 and boiler has been running for 48 mins continuously. I am totally stumped as to why the boiler does not perform when heating kitchen manifold.
 
The only logical explanation is that the demand is > than the boiler output?. I think you said somewhere that the boiler is actually derated to 23kw so not far away from the nearly 20kw kitchen demand, you might consider reduving the TMV setpoint to 38/40C, this should result in a reduction in the heat emitted by the loops and allow the boiler to get up to its SP temperature.

I will look up the boiler output nozzle rating and see what output it gives at 14.0bar.
 
The only logical explanation is that the demand is > than the boiler output?. I think you said somewhere that the boiler is actually derated to 23kw so not far away from the nearly 20kw kitchen demand, you might consider reduving the TMV setpoint to 38/40C, this should result in a reduction in the heat emitted by the loops and allow the boiler to get up to its SP temperature.

I will look up the boiler output nozzle rating and see what output it gives at 14.0bar.
It’s derated to 26kw.
The only logical explanation is that the demand is > than the boiler output?. I think you said somewhere that the boiler is actually derated to 23kw so not far away from the nearly 20kw kitchen demand, you might consider reduving the TMV setpoint to 38/40C, this should result in a reduction in the heat emitted by the loops and allow the boiler to get up to its SP temperature.

I will look up the boiler output nozzle rating and see what output it gives at 14.0bar.
It’s derated to 26kw, using a danfoss .55 80s, air setting 3.5.

I understand the different LPM kitchen vs Laundry but the kitchen flow is 5m from boiler and the laundry flow is 31m from the boiler, I thought the distance would also play a role in the laundry manifold flows.

Pump does not give me any flow rates.
 
Pipe (friction) losses are proportional to the square of the flow, so the losses at a flowrate of 4.71LPM are tiny with the piping sizes you have ~ only 5 to 6% of the losses at 20LPM. Your rads have no problem with a circulation demand of 19.23LPM.
 
Pipe (friction) losses are proportional to the square of the flow, so the losses at a flowrate of 4.71LPM are tiny with the piping sizes you have ~ only 5 to 6% of the losses at 20LPM. Your rads have no problem with a circulation demand of 19.23LPM.
I thought that was the case. Does the kitchen manifold need a bypass on it?

Just done laundry manifold, boiler temp SP 60c, flow out of boiler 71.6 degrees, return to boiler 43.1. Boiler stopped firing for 2 mins flow was still 62 degrees when boiler refires, return 44
 

Attachments

  • image.jpg
    image.jpg
    379.1 KB · Views: 9
Last edited:
Why does the kitchen manifold require a bypass??

What was the laundry manifold (mixed) temp? and was the manifold flowrate still 28.5LPM?.
If the boiler/manifold return was 43/44C then the manifold temperature had to be 6C to 8C higher so TMV not going much at a SP of 40C??

NOTE: Its the kitchen manifold SP temp that I suggested reducing to 38C/40C?? to see can the boiler increase to its cut out temp. Forget the laundry, it seems to be OK.
 
Last edited:
Why does the kitchen manifold require a bypass??

What was the laundry manifold (mixed) temp? and was the manifold flowrate still 28.5LPM?.
If the boiler/manifold return was 43/44C then the manifold temperature had to be 6C to 8C higher so TMV not going much at a SP of 40C??
I remember the plumber telling me if the pumpset was changed a bypass would need to be fitted, I'm not sure why :))

We have no bypass on our system at all.

Laundry manifold mix temp was flow 45 return 35, boiler return 44. I am picking a lot of water returning back to the boiler through the stupid pumpset on laundry manifold.

Another question I've been thinking about today, Our expansion vessel connects into the firebox (I think that's what its called) of the boiler, I am wonder when they removed the internal pump this vessel was removed from flow pipe. I'm not sure on this just asking out of curiosity. Where actually is an expansion vessel suppose to be connected to? Thanks john you are very helpful.

You can see in the 2nd image an updated model boiler than ours and the expansion vessel connects into the flow pipe.
IMG_9383.jpg
Screen Shot 2022-07-22 at 7.28.09 PM.png
 
Must go out for a hour or so, will revert later, can you run that test on the kitchen manifold.

The Laundry manifold TMV is performing perfectly as you can see by your findings, below, with mixed flowtemp of 45C (boiler at 70C) , there is not a lot of water returning to the boiler, only 4.,71LPM?.

Laundry manifold
Boiler/manifold flow temp 70 c
Manifold mixed flow temp 45
Manifold return temp 35
Total flow 16.5 LPM
Blr circ pump flowrate, 4.71LPM (Manifold output, 11.50kw,) Pump RPM 1080.
 
Must go out for a hour or so, will revert later, can you run that test on the kitchen manifold.

The Laundry manifold TMV is performing perfectly as you can see by your findings, below, with mixed flowtemp of 45C (boiler at 70C) , there is not a lot of water returning to the boiler, only 4.,71LPM?.

Laundry manifold
Boiler/manifold flow temp 70 c
Manifold mixed flow temp 45
Manifold return temp 35
Total flow 16.5 LPM
Blr circ pump flowrate, 4.71LPM (Manifold output, 11.50kw,) Pump RPM 1080.
if only our kitchen one would perform nicely, yes will run that test now.
 
if only our kitchen one would perform nicely, yes will run that test now.
Ok so here goes

Boiler setpoint = 65 c
Pump RPM 1350


Boiler flow and return - Boiler fired continuously for 61 mins,
F = 48.8 - R = 32 after 5 mins
F = 53.6 - R = 34.7 after 15 mins
F = 55.6 - R = 36.6 after 30 mins
F = 56.2 - R = 37.3 after 40 mins
F = 56.6 - R = 37.5 after 45 mins
F = 56.7 - R = 37.5 after 50 mins
F = 56.8 - R = 37.6 after 55 mins
F = 56.8 - R = 37.6 after 60 mins
FINAL FLOW = 56.8 C RETURN 37.6 C

Manifold TMV = 40 c
Flow and return
F = 45.0 - R = 34 after 6 mins
F = 47.2 - R = 35 after 16 mins
F = 48.6 - R = 37 after 31 mins
F = 48.6 - R = 37 after 46 mins
F = 48.6 - R = 37 after 51 mins
F = 48.6 - R = 37 after 56 mins
F = 48.6 - R = 37 after 61 mins
FINAL FLOW = 48.6 C RETURN 37

Boiler/Manifold Flow temp 56.8 - setpoint 65 c
Manifold Mixed temp 48.6
Manifold return temp 37
Total flow 27 LPM

Interesting that the radiators and Laundry manifold get 10 degrees above boiler set point but kitchen manifold never reaches boiler set point.
 
Last edited:
The above gives a manifold demand of 21.85kw so the boiler output must be there or there or there abouts the same since it can't reach its SP and cut out, I suppose the manifold temp of 48.6C isn't bad control since we don't know how accurate the TMV SP index is, you might reduce it to 30C sometime to see reduced manifold output and boiler cut out

For interest, you can see the bypass flow required to increase the boiler return temp from 37C to 45C.

The position of the EV connection is effectively into the pump suction in your boiler and it the new original seems to be into the pump discharge with the pump pumping into the return, probably OK in both cases.

Boiler return 37C (no bypass)
1658486047559.png



Boiler return 45C (with bypass)
1658485935181.png
 
The above gives a manifold demand of 21.85kw so the boiler output must be there or there or there abouts the same since it can't reach its SP and cut out, I suppose the manifold temp of 48.6C isn't bad control since we don't know how accurate the TMV SP index is, you might reduce it to 30C sometime to see reduced manifold output and boiler cut out

For interest, you can see the bypass flow required to increase the boiler return temp from 37C to 45C.

The position of the EV connection is effectively into the pump suction in your boiler and it the new original seems to be into the pump discharge with the pump pumping into the return, probably OK in both cases.

Boiler return 37C (no bypass)
View attachment 76763


Boiler return 45C (with bypass)
View attachment 76762
So should we put a bypass in somewhere? there was one on the side of the boiler teed into the flow and returning back into the bottom of the boiler ? The nozzles they have had in this boiler are 0.55 80 s 2.11kg/h and a .50 80s 1.87 kg/h. Thank you for your spreadsheets they are very informative.

Another question, sitting here reading the installation manual, with the nozzle currently in the burner, it refers to blast tube T3 to be installed, we currently have a T5 installed, would this cause an issue?
 

Attachments

  • IMG_9428.jpg
    IMG_9428.jpg
    262.1 KB · Views: 13
  • tempImagefdGIQH.png
    tempImagefdGIQH.png
    4.3 MB · Views: 4
  • tempImagezEDnFY.png
    tempImagezEDnFY.png
    3.5 MB · Views: 6
  • tempImagetft89x.png
    tempImagetft89x.png
    3.9 MB · Views: 6
Last edited:
I wouldn't have it as my top priority just now but can think about best way to achieve it, would be inclined to try a "Tapstat" with the sensor on the boiler return set to 45C (or whatever min return temp required).

How long is it taking the UFH to get the room (kitchen?) temp up their desired temp, at the moment the room/ambient dT isn't particularly bad, so roomstat should be cycling fairly often?, and the rooms with rads??.
Do you intend to increase the boiler output??.

The installed blast tube should be as recommended, I have a feeling that the reason for the small nozzle with the extremely high pump pressure is to get the emissions right, a, say, 0.65 nozzle with a more modest pump pressure of 10bar + the T3 should give the same boiler output and probably less flame impingment on the baffles.
 
Last edited:
I wouldn't have it as my top priority just now but can think about best way to achieve it, would be inclined to try a "Tapstat" with the sensor on the boiler return set to 45C (or whatever min return temp required).

How long is it taking the UFH to get the room (kitchen?) temp up their desired temp, at the moment the room/ambient dT isn't particularly bad, so roomstat should be cycling fairly often?, and the rooms with rads??.
Do you intend to increase the boiler output??.

The installed blast tube should be as recommended, I have a feeling that the reason for the small nozzle with the extremely high pump pressure is to get the emissions right, a, say, 0.65 nozzle with a more modest pump pressure of 10bar + the T3 should give the same boiler output and probably less flame impingment on the baffles.
Its taking 1 hour to get the floor temp up 3 degrees differential in the kitchen and it has a cycle time of approx 3 hours.

Yes I intend to increase the boiler output, but I'm unsure whether 35kw is enough output for UFH, & Rads. I will also get blast tube changed to instruction manual specs.
 
Its taking 1 hour to get the floor temp up 3 degrees differential in the kitchen and it has a cycle time of approx 3 hours.

Yes I intend to increase the boiler output, but I'm unsure whether 35kw is enough output for UFH, & Rads. I will also get blast tube changed to instruction manual specs.
If we have
21.85kw ufh kitchen
11.50kw ufh Laundry
16,50 Kw Radiators/Trench
3 Kw DHW
A total of 49Kw a 35 kw boiler is not going to perform very well is it if they all demanded heat at once.?
 
Yes, but there are lots of ways of skinning a cat, if the kitchen has a cycle time of 3hrs, 1 hr on time so kitchen average requirement is 21.85x0.33=8.3kw, ideally the UFH should give this output continuously and the manifold output can be reduced by various means, reducing the mixing temperature for example so assuming Laundry similar at 11.5x0.33=3.8kw, then continuous UFH demand is ~ 12.1kw, the rads might cycle in a similar fashion, so you may well find that 35kw output is quite sufficient.? You measured your oil consumption at ~ 23LPD or ~ 10kwh/hr so not a mile away from the above?.
 
Yes, but there are lots of ways of skinning a cat, if the kitchen has a cycle time of 3hrs, 1 hr on time so kitchen average requirement is 21.85x0.33=8.3kw, ideally the UFH should give this output continuously and the manifold output can be reduced by various means, reducing the mixing temperature for example so assuming Laundry similar at 11.5x0.33=3.8kw, then continuous UFH demand is ~ 12.1kw, the rads might cycle in a similar fashion, so you may well find that 35kw output is quite sufficient.? You measured your oil consumption at ~ 23LPD or ~ 10kwh/hr so not a mile away from the above?.
You are very knowledgeable. Thank you.
Ok so heres what I think I need to do from our conversations:

  • Reinstall original pump
  • Install another EV
  • Turn TMV down on kitchen manifold
  • Install new pump set on Laundry manifold
  • Upsize boiler back to 35kw
  • Replace blast tube to correct one, as per instruction manual
  • Install bypass?

And hopefully we will have a system the will operate efficiently.
 
I would suggest replacing the boiler PRV (safety valve) as well, it may be lifting before 3bar.

The laundry manifold seems to be performing spot on, it gives a mixing temp of 45C with a boiler temp of 70C, what is the TMV setting index?, you could reduce that by say 5c to test that the TMV is working OK.

Have you the spec on the original circ pump model etc.

Laundry manifold
Boiler/manifold flow temp 70 c
Manifold mixed flow temp 45
Manifold return temp 35
Total flow 16.5 LPM
Blr circ pump flowrate, 4.71LPM (Manifold output, 11.50kw,) Pump RPM 1080.
 
I would suggest replacing the boiler PRV (safety valve) as well, it may be lifting before 3bar.

The laundry manifold seems to be performing spot on, it gives a mixing temp of 45C with a boiler temp of 70C, what is the TMV setting index?, you could reduce that by say 5c to test that the TMV is working OK.

Have you the spec on the original circ pump model etc.

Laundry manifold
Boiler/manifold flow temp 70 c
Manifold mixed flow temp 45
Manifold return temp 35
Total flow 16.5 LPM
Blr circ pump flowrate, 4.71LPM (Manifold output, 11.50kw,) Pump RPM 1080.
Oh yes forgot about the PRV valve. So you think we should put a pump set on the laundry like the kitchen one? (Instead of the one attached)

This is the pump they moved from inside the boiler, also they have attached this pipe between flow and return. Do you think I should turn this on to get retune temp up?

So the only explanation we have as to why the boiler doesn’t reach serpoint when heating the kitchen manifold is because the manifold output is > or = to the boiler output?
 

Attachments

  • 43E23EF1-0B46-4D20-A6CB-4A0E2A8A1FA2.jpeg
    43E23EF1-0B46-4D20-A6CB-4A0E2A8A1FA2.jpeg
    369.7 KB · Views: 8
  • 51D2EA5E-5B9B-4973-9EB1-1DC528A57EE2.jpeg
    51D2EA5E-5B9B-4973-9EB1-1DC528A57EE2.jpeg
    377 KB · Views: 11
  • 00A6065F-8B85-438A-952A-A321B1E7F78F.jpeg
    00A6065F-8B85-438A-952A-A321B1E7F78F.jpeg
    477 KB · Views: 9
Oh yes forgot about the PRV valve. So you think we should put a pump set on the laundry like the kitchen one? (Instead of the one attached)
NO, what I said is that this TMV/pump set seems to be working perfectly well even though I would like to know how it "works" (see queries in attached that you can answer). Can you see what the TMV is set to just now?.
If it's working OK why change it?.
This is the pump they moved from inside the boiler, also they have attached this pipe between flow and return. Do you think I should turn this on to get retune temp up?
I don't think this will work because the circ pump is on the flow so the boiler return pressure is > than the flow (where it leaves the boiler) so the bypass flow will be the wrong way?.
So the only explanation we have as to why the boiler doesn’t reach serpoint when heating the kitchen manifold is because the manifold output is > or = to the boiler output?
Yes, IMO, so just reduce this (kitchen) TMV setting to say 30C or whatever is required to get the mixed flow temperature down to say 35C/38C.
 

Attachments

  • UFH Laundry Rev1.jpg
    UFH Laundry Rev1.jpg
    710.3 KB · Views: 9
NO, what I said is that this TMV/pump set seems to be working perfectly well even though I would like to know how it "works" (see queries in attached that you can answer). Can you see what the TMV is set to just now?.
If it's working OK why change it?.

I don't think this will work because the circ pump is on the flow so the boiler return pressure is > than the flow (where it leaves the boiler) so the bypass flow will be the wrong way?.

Yes, IMO, so just reduce this (kitchen) TMV setting to say 30C or whatever is required to get the mixed flow temperature down to say 35C/38C.
The laundry TMV is set to 45 c.

I have this morning turn the kitchen TMV down to 38 c and mixed water is still getting to 46 c. I am wondering if the pump pressure and speed of water is literally seeping through the valve.

Below is a better pic of the manual bypass, it actually tees of the flow before water even gets to 2 way valve and joins into the return pipe from DHW cylinder, which then tees into UFH return pipe.

Sorry for all the questions, hope your brain is not as confused as mine 😂😂
image.jpg
 
The laundry TMV is set to 45 c.
So the SP is 45C and the actual is 45C= perfect control, don't dream of changing it.
I have this morning turn the kitchen TMV down to 38 c and mixed water is still getting to 46 c. I am wondering if the pump pressure and speed of water is literally seeping through the valve.
Turn it down to 30C, see what effect it has, if any.
I would think something wrong with the TMV as the laundry is under similar working conditions and working perfectly, why was a decision made to replace them with this kitchen type? which ironically is not working.

Below is a better pic of the manual bypass, it actually tees of the flow before water even gets to 2 way valve and joins into the return pipe from DHW cylinder, which then tees into UFH return pipe.

Sorry for all the questions, hope your brain is not as confused as mine 😂😂
Yes, that might work, but don't really know its purpose, would prefer to eventually see a temperature controlled one installed in the correct position.
 
So the SP is 45C and the actual is 45C= perfect control, don't dream of changing it.

Turn it down to 30C, see what effect it has, if any.
I would think something wrong with the TMV as the laundry is under similar working conditions and working perfectly, why was a decision made to replace them with this kitchen type? which ironically is not working.


Yes, that might work, but don't really know its purpose, would prefer to eventually see a temperature controlled one installed in the correct position.
The kitchen pump had started leaking and they recommended this, as the same as the laundry is obsolete now.

I will turn Kitchen TMV down and if this doesn’t work I will get it replaced.

The purpose of that pipe was the plumbers quick fix to get return water up in temp, as he didn’t want to investigate any of the other issues and thought he would just keep adding pieces to the system in the hope it would fix everything. 😂

Thank you
 
Just crack it open gradually until it raises the return temperature to 45C or so.

You might also have a look at this and comment.
 

Attachments

  • UFH Laundry Rev1.jpg
    UFH Laundry Rev1.jpg
    710.3 KB · Views: 9
Just crack it open gradually until it raises the return temperature to 45C or so.

You might also have a look at this and comment.
Just crack it open gradually until it raises the return temperature to 45C or so.

You might also have a look at this and comment.
Yes correct, hot flow pipe from boiler.

The other pipe is the return to boiler/cold return.

the little pipe on the end of the manifold, is an unused pipe (yes cowboys instaledl our system)

Attached is diagram on how isotherm is suppose to work
 

Attachments

  • isothermtech.pdf
    306.8 KB · Views: 9
Last edited:
Yes correct, hot flow pipe from boiler.

The other pipe is the return to boiler/cold return.

the little pipe on the end of the manifold, is an unused pipe (yes cowboys instaledl our system)

Attached is diagram on how isotherm is suppose to work
I cracked open that manual pass valve and you wouldn’t believe it the boiler got up to temperature (well boiler step point was 60c but boiler flow reached 72c) and the expansion vessel off the hot water cylinder was dripping. So I believe the expansion vessel in the boiler is either not working or to small when running the kitchen UFH manifold.
 
Do you mean the expansion valve on the HW cylinder is dripping, if so, this, or a failing HW cylinder EV has got nothing to do with the boiler EV or PRV, what is/was the boiler pressure gauge reading when this dripping occurs?.
 
Do you mean the expansion valve on the HW cylinder is dripping, if so, this, or a failing HW cylinder EV has got nothing to do with the boiler EV or PRV, what is/was the boiler pressure gauge reading when this dripping occurs?.
Yes expansion valve on HW cylinder was dripping, with that bypass valve open hot water was feeding down the pipe to where the EV is on cylinder. Nothing else was calling for heat other than Kitchen UFH with manual bypass open. Boiler pressure was 1.5 bar, pump was 1.35 bar, flow temp was 72 degrees. (Hope that makes sense)

Another question, our original nozzle was a .65 80 s 2.47kg/h, if I'm reading these specs correct on the side of the burner does it indicate the nozzle size must be 2.8 - 4.5 kg/h and is the output of this burner 33-54 kw, should it couldn't be downsized to a 26kw?
 

Attachments

  • IMG_5286.jpg
    IMG_5286.jpg
    1.4 MB · Views: 6
Last edited:
If that bypass valve is feeding HOT water into the HW cylinder then it will have to be from the HW cylinder hw outlet which will be at higher pressure when the cylinder is heating or is hot with no HW draw off, if tied into the boiler system primary system flow pipe it cannot feed hw as the primary/boiler system pressure is only 1.5bar. If it was connected from the cold mains then that will lift the cylinder expansion valve but the pipe would be cold.?

Nozzle Sizing: From below. a 0.65 nozzle will give a burner output of 31kw @ 12.5bar which will be 31*(14/12.5)^2, 32.81kw @ 14bar, a boiler output of 28.87kw @ 88% boiler efficiency.

Your present 0.55?? nozzle will give a burner output of 26kw @ 12.0bar which will be 26*(14/12.0)^2, 28.10kw @ 14bar, a boiler output of 24.73kw @ 88% boiler efficiency.
 

Attachments

  • Danfoss Diesel Nozzle.png
    Danfoss Diesel Nozzle.png
    4.2 MB · Views: 9
If that bypass valve is feeding HOT water into the HW cylinder then it will have to be from the HW cylinder hw outlet which will be at higher pressure when the cylinder is heating or is hot with no HW draw off, if tied into the boiler system primary system flow pipe it cannot feed hw as the primary/boiler system pressure is only 1.5bar. If it was connected from the cold mains then that will lift the cylinder expansion valve but the pipe would be cold.?

Nozzle Sizing: From below. a 0.65 nozzle will give a burner output of 31kw @ 12.5bar which will be 31*(14/12.5)^2, 32.81kw @ 14bar, a boiler output of 28.87kw @ 88% boiler efficiency.

Your present 0.55?? nozzle will give a burner output of 26kw @ 12.0bar which will be 26*(14/12.0)^2, 28.10kw @ 14bar, a boiler output of 24.73kw @ 88% boiler efficiency.
Ok so you get a burner output and a boiler output from one nozzle calculations?

In below photo, pipes in red were hot, pipe going into EV was cold
FEA00670-4410-4E88-A0E1-03E480202AE3.jpeg
 
Yes, the table gives (presumably) burner output, the only assumption that will marginally affect the boiler output is its efficiency so 85% to 92% should cover it, the calculation for pressure is universally used, ie flow is prop to the sq.root of pressure, I should have shown that as ^0.5 and not ^2, but I did use ^0.5 in the calculation.

Can't really comment on that by pass except to suggest finding out exactly where the connections are teed in.
 

Reply to What size boiler needed in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

Hi. I need a new toilet supply line but don’t know the size type of the fitting at the shut off valve. It is not 3/8 compression. It is a plastic nut about the same size as the one going into the cistern but has a different thread. Attached is a photo. Can you advise. Thanks.
Replies
2
Views
225
Hi all. Hope you have all been keeping well. A while back I decided I only wanted to fit one brand of boiler and decided on Viessmann due to space for servicing and changing parts if ever needing to. I am finding my decision rather hard due to the different clearances on flue runs and cupboards...
Replies
9
Views
261
We are from Alberta, and I own an electrical company. I have been asked by a BC Mechanical P. Eng. to install an emergency STOP button at the man-door to the boiler room. It's intent is to 'halt' the operation of the boilers in the room should there be an emergency. He is demanding that I do...
Replies
5
Views
306
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
397
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...