Guys , just curious, how do you work out your rad sizes when using WC , rather than a set DT of say 50
 
WC?
I work out the heat losses from room then look at Stelrad Charts to choose the rad. They do charts for 30T, 40T, 50T etc.
Does that help?

I think its the only way , as said I was just curious.
I have learnt from WC in my own house that sometimes my boiler flow temp can be lower than 45 C and it still heats the house and is no where near a DT of 40 / 50 .
I have started to leave off a “heat up”% of 1.5 because the heating is always on , would you agree ?
 
You just size as normal, the idea being that as the external temp rises from the designed low point, the required output from the heat emitter will be less to maintain the room temp. This is still met by progressively reducing the boiler flow temperature.
 
You just size as normal, the idea being that as the external temp rises from the designed low point, the required output from the heat emitter will be less to maintain the room temp. This is still met by progressively reducing the boiler flow temperature.

Cheers Chris , you have confirmed what I thought.
We bought a new house a couple of weeks ago and I am recalculating the rads . Would you agree and knock of the initial “ heat up “ calc from cold , just seems wrong putting it on .
 
Is there a superb app out therefor heat loss, free or fee .. I don’t mind

If you want a cheap quick one , Mr combis are ok .
However I have just worked our new bedroom heat loss / rad size etc etc , I did mine long hand and know it was right ( F1 F2 etc )and then compared it to the Mr Combi , quite a bit of difference.
 
If you want a cheap quick one , Mr combis are ok .
However I have just worked our new bedroom heat loss / rad size etc etc , I did mine long hand and know it was right ( F1 F2 etc )and then compared it to the Mr Combi , quite a bit of difference.

whose was higher ?
 

Reply to Rad delta T with wc. in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

B
    • Friendly
Hi, I've followed this excellent forum for several years but have never posted, so decided I'd better give some details. My status is the upper end of DIY and I've a couple of house renovations under my belt (my own homes) I am retired but do volunteer handyman jobs for the elderly. Not...
Replies
2
Views
171
I was stupid enough not to check the position of the pipes under the tiles when installing a toilet and drilled right through the center of a 16 mm copper water pipe. I exposed the pipe by removing a ~30cm section of the plastic sleeve and a ~10 cm section of the pipe around the hole. Several...
Replies
0
Views
214
Hi All, I am looking to take my bath out and fit a shower. Regards to tanking. Is it ok to just seal everything with plastic rather than just paint tanking slurry? Thanks in anticipation, best regards Staggers
Replies
3
Views
246
Hi guys....we have an old Astracast sink top....I think its a composite sink....has a big single bowl. My wife thinks it looks scruffy....looks ok to me.....sound but the bowl has seen a lot of work. So she wants a new one...Astracast it seems are no more. The problem is its size.....looked...
Replies
2
Views
171
Just started gound work on self build bungalow and wondering best way to do below ground soil pipes. For toilet I was going to go straight down through slab and out through deadwork into a manhole. I will work out falls from manhole and set the height of the waste water system as required. For...
Replies
2
Views
134
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock