hi Gents

We are having issues with constant hot water flow with the above boiler. The boiler was serviced over a year ago and had the same issues , at that time the plumber thought the issue was the thermistors and they were changed. This seemed to help the problem but did not cure it and it is now worse.

Here is the senario : when using the mixer shower, the water most of the time goes from hot to cold and will stay cold. if you open up the hot water tap in the bathroom or in the kitchen ,sometimes the boiler fires back up and hot water will come on again and sometimes It won’t. It doesn’t come up any faults on the lcd screen just goes back to winter mode : timer or stat off

I have noticed it mainly happens when only using the shower. Sometimes I notice a stutter in the water supply coming from the shower head then I know it will be getting cold soon. Sometimes I notice a slight drop in pressure also and know that it will soon go cold

Does any one know what could cause the issue.

In the summer I will be installing an extension and extra shower room so will be looking to get a system boiler and water tank installed. So I’m hoping I won’t need to replace the combi just now

Many thanks
 
If it doesn't happen with the kitchen hot then shower cartridge at fault maybe
 
Thanks for the input guys. Sometimes it happens on the kitchen tap but much less often. Could it be something to do with the flow rate though?
Mixer is a Vado PHA-148-C/2-C/P

I have also reset the boiler
Made sure it is at the 1.2bar and the condensate pipe water trap/pump thingy is clear
 
It will be your shower mixer letting the cold mix across to the hot.
It should have non return valves fitted to the inlets to stop the above from happening. They can also stick open, causing the same problem. .if your handy, remov the shower mixer to check. Or get a local plumber to sort it.
 
Sounds like a water flow sensing issue potentially with the boiler being that it can happen with the taps as well.
Not really a big issue to sort.
A GSR engineer will be able to sort it out easily as long as part is not seized in place which occasionally happens in which case you will end up with replacing the part housing as well.
I would guess the boiler is several years old & these things can cause the above issue,
Thanks.
Andy (Allgoode)
 
Hi guys.

So I had my boiler sorted. It was the flow turbine. The internal impeller had started to eat itself up. This would explain why it wasn’t working with the shower as the flow of hot water is less . I thought I would share the findings

Thanks
 
Cheers for the update.
Thought it was that as usual symptoms of turbine failure/sticking due to build up,etc.
Didn't want to post my part thoughts as i know to many people "have a go" even though the case front cover forms part of the combustion box seal.
Hope not to expensive for repair,
Cheers,
Andy
 
Thanks
Cheers for the update.
Thought it was that as usual symptoms of turbine failure/sticking due to build up,etc.
Didn't want to post my part thoughts as i know to many people "have a go" even though the case front cover forms part of the combustion box seal.
Hope not to expensive for repair,
Cheers,
Andy


Andy, no mate he was pretty reasonable . He was an older gent turns out he knew my dad , said at the start that he mostly installs boiler systems and shyed away from repairs as it mostly electronic and electrical.He took the details went away and did some research and came back with the right part. Better than the more expensive younger gun who serviced it last year , when at he time we told him it very occasianly stopped producing hot water said it was the thermistors! When I questioned him as to why he could not test them with a low reseistance ohmmeter ( me being a spark ) he said “na they just change them par for the course” and it made no difference . So I have now found the man to do my system boiler , water cylinder and plumbing work for my extension next summer.
 

Reply to Problem with hot water on logic combi 35 in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
157
Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer warming up. The heat exchanger has been changed 6 months ago, so I do not believe it is that. Does anyone have any ideas on what it could be? Thanks
Replies
4
Views
263
Hi, Later this year I am going away for a 2 week holiday and as the weather will be warm there is no need for the heating to be on and arguably no need for me to needlessly heat hot water. My intention was to turn the boiler off along with the mains water when going away. Now, I have heard...
Replies
1
Views
118
Hello plumbers in my internet. So the Mrs want a spray mixer tap in the kitchen as we had two separate taps. I changed the tap for a temporary two hole mixer but the cold water pressure is high mains fed and the hot is low pressure immersion tank fed. I've been trying to find info on what I...
Replies
2
Views
163
P
  • Question
Boiler is SIRIUS THREE FS 70 Potterton commercial. Situation: We are small building contractors and my labourers managed to damage the radiator pipes during the strip out. Not the end of the world as damages happens. I am responsible builder and paying my bills and to repair the damages if...