Hi, we have an oil boiler which feeds HW, rads, and two UFH heating circuits using 4 zone valves and 2 pumps. Would anyone have a look at the photo and tell me if its right that the green pump has to be on to feed the UFH mix pump? Could the UFH pump have been teed in parallel with the green pump? I was having a look at the pipework and was surprised that the green pump was on when the Radiators and HW were off. The system works but seem to struggle when both the radiators and UFH need to heat up at the same time (mornings)
pipework.jpg


Thanks
 
Its hard to make everything out due to the close up photo. The green pump is the system pump which will circulate from the boiler and around the circuits and will be energised whenever a zone is falling for heat. Each UFH manifold should have its own circulating pump.
Has the system always struggled when both are on in the morning, or only recently?
What output is the boiler? And what is the load of each circuit?
 
Aye, picture further out needed. What's the motorised valve for at the bottom of pic? There doesn't seem to be a motorised valve for the under floor.
 
Its only recently I've noticed it struggling but it has been cold this past week and the radiators have been on constantly because we have a new-born in the house. The boiler is a warmflow and says 70/90. There are 4 single radiators upstairs and 1 double. The UFH areas are about 20sqm and 12 sqm though the smaller one doesn't get used.
pipework2.jpg
 
In the colder weather the radiators need more power to achieve the same room temperature. Its entirely possible your system has been designed at the wrong outside temperature and lacking the boiler output to meet the demands in this cold weather, or the boiler output is not enough. You could also have a system pump flow rate problem, where by the UFH is drawing its design flow rate leaving less than required for the radiators, which would obviously leave the emitters (radiators) struggling to stay warm. Increasing the pump setting will increase the pump head and flow rates and could suffice, however this could throw the boiler delta t out and may result in hydronic separation or a buffer being the answer.
Is it a condensing boiler? Do you have any idea of the circuit loads?
 
As a quick workaround you should have some sort of programmable thermostat on underfloor area just time it on say 90min earlier than rest of heating . Also what backset temperature is that thermostat set at?
 

Reply to pipework query, pump feeding pump? in the Ireland area at PlumbersForums.net

Similar plumbing topics

Hi they used to say as a last resort you could discharge the D2 pipework at high level and turn it back to the wall. Similar to a combi boiler. I have just looked back through the regs this seems to have changed and it isn't mentioned now. It now mentions if at high level it should be discharged...
Replies
11
Views
267
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up to 1.3. I've had an engineer look inside the boiler and he can't see anything wrong. I've checked the pipes all over the house and cannot see any...
Replies
2
Views
202
P
Hello plumbers in my internet. So the Mrs want a spray mixer tap in the kitchen as we had two separate taps. I changed the tap for a temporary two hole mixer but the cold water pressure is high mains fed and the hot is low pressure immersion tank fed. I've been trying to find info on what I...
Replies
2
Views
137
S
Hi, I seemed to have a blockage in kitchen sink. A plumber came and cleared all the pipework that is visible inside my home (there was debris and pebbles!) We saw that the pipe that takes water down the gutter was visibly full to the top. He said he will return with a coil to push through...
Replies
1
Views
65
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
339
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock