Hi I had water dripping out of the overflow, so fitted a new part 2 ball valve, all ok shutting off. 2days later its dripping again, Adjusted it, fine. Next evening come home running faster, Thought must be faulty so fitted a new one. 2 days later dripping again, must be a faulty batch so I thought. Got one from a different store and fitted, all fine 4 days later come home running faster than ever. This tank only feeds water to a shower and basin. no expansion. can someone help this one has me baffled ?
 
Could be mains cold water back feeding across & slowly filling the storage cistern up.
Got any mixer taps or shower valves with mains cold ?
 
Hi I had water dripping out of the overflow, so fitted a new part 2 ball valve, all ok shutting off. 2days later its dripping again, Adjusted it, fine. Next evening come home running faster, Thought must be faulty so fitted a new one. 2 days later dripping again, must be a faulty batch so I thought. Got one from a different store and fitted, all fine 4 days later come home running faster than ever. This tank only feeds water to a shower and basin. no expansion. can someone help this one has me baffled ?
Have you an indirect hot water cylinder? My money is on split coil, and water in two cisterns (expansion and CWS) seeking to find level
 
I'd be more inclined to go for a mixer tap problem. quickest way to prove it is by turning the mains off.
 
I'd be more inclined to go for a mixer tap problem. quickest way to prove it is by turning the mains off.
Thanks for replies, The cold water tank only feeds the cold basin tap and the power shower, there is a separate direct combination (fortic) tank that feeds the hot basin tap and power shower, not a mixer tap hope this clarifies the setup.
 
whats highest, the water level in the fortic or in the cold water tank ?
 
The water level in the fortic is higher.. The shower doesn't get used that often only when guest's stay, and has never been a problem until this time. Are you thinking the shower could be faulty? It has an integral pump in the shower if this helps.
 
try isolating the shower & see if the overflow stops dripping.
If it does there's your problem
 
did you change the whole valve or did you break it at the union inside the tank? some of the newer valves dont seem to seat properly on the lod unions and drip at the nut
 
I am going to try isolating the shower next. I have installed 3 brand new complete valves as I have also found that breaking them often means they do not seal so always now try to fit new complete units. I will try and isolate the shower tomorrow morning and see how it goes, will keep you posted! Many thanks for your help.
 
Status
Not open for further replies.

Reply to Part 2 ball valve in roof tank. in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi, We have a large Heatrea Sadia unvented hot water tank, not sure of the size in liters but its about 1600mm tall. The tank is around 3 years...
Replies
0
Views
424
Good evening, I'd like your opinion on something that is worrying me please: my landlady's plumber replaced the bottom/night element of my...
Replies
2
Views
492
Hi, I have 3 port value for HW & CH. Loft extension added many years ago so they added a T to go upstairs, only 2 rads up but 11 downstairs...
Replies
0
Views
272
First post as I can not figure this one out. I have a hot water boiler heating system, gas fired, with an HTP SuperStor indirect hot water tank...
Replies
2
Views
436
T
Hi, (Not a pro, just DIY) One of these worked OK for 18 years, but seemed to have gone faulty. Replaced it with same, twice in last 2years...
Replies
9
Views
816
Back
Top