Hi guys as above really, been to a couple of jobs where there has been a banging noise at the boiler on an OV system. everything is circulating ok and getting hot but occasionally there's a banging noise coming from the boiler.

What can cause this? muck in the system? Struggling pump?

Thanks
 
Without thinking of the obvious it could be no bypass on system so if both 2 ports shut down it can cause a clunking noise or sludged heat exchanger
 
Are they old cast iron heat exchangers? Gravity hot water?

It's mostly sludge on old stuff, can be pumps. If it's running ok then leave well alone you'll create problems.

If it ain't broke don't fix it!
 
Are they old cast iron heat exchangers? Gravity hot water?

It's mostly sludge on old stuff, can be pumps. If it's running ok then leave well alone you'll create problems.

If it ain't broke don't fix it!

The latest was a Worcester RI.

Leave it well alone I did, i advised that as it's currently working and i haven't heard the banging myself it's not worth messing with as i could cause an issue.

Just asking out of interest more than anything as it's annoying going to jobs where it's all working but the customer says there's something wrong. I tell them if it's all working, there is nothing for me to fix and the noise they hear could be a number of things but not worth messing with as could create a bigger problem than just noise.
 
New boilers?

somethings overheating but the cause could be numerous things, faulty stat, poor circulation etc
 
I've seen numerous Worcester Ri with crossed flow and return that do this. Partly because of the stupid arrows they put on the chassis that don't match up if you take the pipes up the back!

boiler seems to work fine but the thermistor is measuring the return temp so can boil if flow temp is excessive.
 
Someone forgot to wire the pump from the boiler to provide overrun had that a few times.

Blocked/restricted h plan

zone valve upside down

zone valve too close to the pump

no system bypass

lack of water in the system
 
cheers for the excellent replies, plenty for me to keep an eye out for.
 
Status
Not open for further replies.

Reply to OV system banging noise at boiler. Happened a few times, likely cause? in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Desperate for some help! Be a life saver of someone can help as suffer from a high intolerance to noise. Moved into new house 1940s (copper...
Replies
7
Views
845
This issue arose about a year ago. Does anyone have an idea why I occasionally hear (about once every hour or longer) a hammer related noise...
Replies
0
Views
415
Hi, Over the past few months, my wife and I have noticed a constant pulsing sound throughout the house which is particularly noisy at night (this...
Replies
4
Views
686
Hi All, Looking for a bit of advice on the best way to pipe this. - 24kW Worcester regular boiler in kitchen, approx. 9 years old - unvented...
Replies
16
Views
1K
Recently over the past 2 months, the boiler or area by the water tank has started making a loud groaning noise whenever hot water has been running...
Replies
0
Views
2K
Back
Top