Hi,
Can anyone tell me if there is supposed to be any movement between a TRV and the radiator, as have replaced a radiator and tightened the connections as much as possible, but the TRV can still be moved backward and forward.
Many thanks,
Von 🤔 🤔 🤔
 
Can anyone tell me if there is supposed to be any movement between a TRV and the radiator,

The body of the valve should be rock steady with a rigid connection to the radiator. A small amount of play in the control knob is normal. I've just tried wobbling a sample of Draytons and the chromed dome moves slightly but it's by less than a millimeter.

Can you provide some details? E.g. a photo and rough indication of how much play you are getting.
[automerge]1580471424[/automerge]
photos of valve was olive brass if so you may not have tightened enough
Were there photos? I'm not seeing any. Actually, post #3 is missing for me. Very mysterious...
 
Hi,
Can anyone tell me if there is supposed to be any movement between a TRV and the radiator, as have replaced a radiator and tightened the connections as much as possible, but the TRV can still be moved backward and forward.
Many thanks,
Von 🤔 🤔 🤔
Just to be clear. The connection between the pipe and the radiator is called the valve body ..this has to be watertight and not move. The valve head is the plastic nob that grades from frost through blue to max..these can be a bit loose..did you set the valve head to maximum when you fitted if not it might well wobble ..once fitted turn down to desired setting. Some heads are threaded and others are push on ones but the same principle applies ..centralheatking
 

Reply to Movement between TRV and radiator. in the USA area at PlumbersForums.net

Similar plumbing topics

Recently had a Viessmann Vitodens combi boiler installed, quite often when the adjacent cold mixer tap is opened the boiler starts for a few seconds! Can anyone tell me what is causing this? And how to cure?
Replies
3
Views
217
Hi, My current hot water system needs to be replaced. Anyone got any suggestions or can recommend any plumbers around Derrimut area that won't rip me off? An office guy recommended me to apply for government rebates and get it installed through timetosave.com.au. How reliable is this...
Replies
6
Views
311
I have attached an image of the brass body within a tap. Having replaced a cartridge which has cured a leaking tap, I can see that there is a small leak from the brass body which can be unscrewed. Is there a seal behind the body? Thanks.
Replies
2
Views
318
I want to reconnect some outbuildings to an existing water supply. The supply pipe is old 22mm MDPE and buried for a fair distance so not going to dig it up and replace it 😬. Question is can I use normal 22mm plumbing push-fit connectors to make the connection as finding 22mm MDPE fittings...
Replies
1
Views
284
I was stupid enough not to check the position of the pipes under the tiles when installing a toilet and drilled right through the center of a 16 mm copper water pipe. I exposed the pipe by removing a ~30cm section of the plastic sleeve and a ~10 cm section of the pipe around the hole. Several...
Replies
0
Views
205
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock