Ment to come back to this one & forgot, sorry. If mains is going under the foundation & sometime also if going through the outside wall with other services there may be a requirement for a lintel to spread the load around the duct.
(sorry mutley just seen your post)
What type of floor construction have you got ? If it comes up through a ventilated floor void (suspended wooden or block & beam) then it must be insulated, check that the size of the MDPE & insulation will fit in the 110mm.
If it is a solid floor & the mains comes in further than 750mm from the outside wall then no insulation is required (must still be in a duct) if less than 750mm then insulated as pic.
Make sure new mains is run between 750 & 1350mm deep & do not back fill until water undertaker has carried out reg's inspection they will want to see it.
Seal - watched a youtube vid the other day, it was crap but they did have a purpose made seal for the end of the pipe which I had not seen before, will investigate but if anyone else knows of one let us have details.