Margaret,

On the positive front, it is good that the original installer is actively engaged in the resolution. Irrespective of achieving success, at least he/ she has the commitment and is trying to resolve the issue.

Switching flow / return without sound logic (when the heating side is functioning ) is puzzling. I am assuming that he/she ( at the time of switching) has not relocated the magnetic filter ( which I recall is adjacent to the hot water cylinder) onto the “new” return, leaving the new boiler unprotected from debris flowing from the system back to the boiler? That is not the end of the world, but demonstrates poor thinking in the act of desperation

If you wish feel free to message me at [email protected]

If you are relatively close, I am happy to look at it for you - to give you a few pointers fir your installer to rectify the problem
 
Last edited:
Margaret,

On the positive front, it is good that the original installer is actively engaged in the resolution. Irrespective of achieving success, at least he/ she has the commitment and is trying to resolve the issue.

Switching flow / return without sound logic (when the heating side is functioning ) is puzzling. I am assuming that he/she ( at the time of switching) has not relocated the magnetic filter ( which I recall is adjacent to the hot water cylinder) onto the “new” return, leaving the new boiler unprotected from debris flowing from the system back to the boiler? That is not the end of the world, but demonstrates poor thinking in the act of desperation

If you wish feel free to message me at [email protected]

If you are relatively close, I am happy to look at it for you - to give you a few pointers fir your installer to rectify the problem


Hello Brambles, the installer was also puzzled when he returned to look at the boiler and the Drayton valves. Also tested and looked at the air vent. Has this happened to anyone before about the HW reverse flowing? Never did we have this with the HW before, it was only after the boiler was changed that we did not have hot water. From above, the criss-cross would this be an issue? I haven't seen such a thing before.

Thanks a lot.
 
Margaret,

I cannot see why the installer has reversed the flow on on your system. The issue you have described is that the only problem you have is that you cannot run Hot water without have the Central Heating on.

My view is that either :

The control wiring between the two two port valves and the Hive interface is incorrect.
Or, the micro switch in the two port valve controlling hot water is not functioning ( I think you said that the synchronous motor was changed. The installer may have damaged the micro switch or dislodged the connection in the process.

The only reason to change the pipework configuration that I can think of, is if the installer has fitted the Hot Water two port valve downstream of the Central Heating two port valve. I have seen this before on new installations.

To conclude, to operate a condensing boiler for Hot water only is as simple as it gets, a boiler, two pipes, a valve and an indirect cylinder. Better still you know that the hydraulic circuit works, because it functions when the central heating is on. I would have expected the installer to operate the boiler in this mode upon first use before testing the central heating circuit.

Presumably the installer cleaned the existing central heating system before installing the new boiler? So should have a good understanding of the system pipework layout.

With respect to the crossovers, they should be removed or if deemed to be correct the magnetic filter should be reinstalled on the return immediately before the boiler.

In my view, the actions taken by your installer earlier this week are putting your boiler warranty at risk.

My view has not changed since your problem was first posted. It is not a difficult fix for a competent heating engineer or a plumber with a good knowledge of heating systems - and this is most properly trained experienced plumbers.

On a final point, don’t let him/her take up any more flooring / floor boards - that is just not needed to fix this.

Feel free to share this note with your installer - it may help to focus their mind in the fault finding process.
 
Margaret,

I cannot see why the installer has reversed the flow on on your system. The issue you have described is that the only problem you have is that you cannot run Hot water without have the Central Heating on.

My view is that either :

The control wiring between the two two port valves and the Hive interface is incorrect.
Or, the micro switch in the two port valve controlling hot water is not functioning ( I think you said that the synchronous motor was changed. The installer may have damaged the micro switch or dislodged the connection in the process.

The only reason to change the pipework configuration that I can think of, is if the installer has fitted the Hot Water two port valve downstream of the Central Heating two port valve. I have seen this before on new installations.

To conclude, to operate a condensing boiler for Hot water only is as simple as it gets, a boiler, two pipes, a valve and an indirect cylinder. Better still you know that the hydraulic circuit works, because it functions when the central heating is on. I would have expected the installer to operate the boiler in this mode upon first use before testing the central heating circuit.

Presumably the installer cleaned the existing central heating system before installing the new boiler? So should have a good understanding of the system pipework layout.

With respect to the crossovers, they should be removed or if deemed to be correct the magnetic filter should be reinstalled on the return immediately before the boiler.

In my view, the actions taken by your installer earlier this week are putting your boiler warranty at risk.

My view has not changed since your problem was first posted. It is not a difficult fix for a competent heating engineer or a plumber with a good knowledge of heating systems - and this is most properly trained experienced plumbers.

On a final point, don’t let him/her take up any more flooring / floor boards - that is just not needed to fix this.

Feel free to share this note with your installer - it may help to focus their mind in the fault finding process.

Thanks Brambles for your responses. Much appreciated and all others on here for your reply. Just wanted to rectify whatever the underlying issue.

Yes, he said he replaced a syncron motor on the heating valve. This was done in February 2019. The house had old radiators and boiler. I had changed the whole house radiators (x7) all new, new Valliant boiler + hive controller. In regards to the syncron motor, found it rather odd for them to change in consideration these were newly installed. We didn't have these Drayton valves at all before and not sure why it would need replacing on the 5th month if these were new?

On another note, you mentioned there is no need to lift floorboards, he mentioned that he might have to disconnect the blue HW cylinder and lift the flooring in the air cupboard and see the pipework there? Is this needed? British gas also said the same thing?

At present, I am waiting for his return ...

Thanks.
 
Margaret,

I find this quite odd. Are you sure that the installer of the boiler was aGas Safe registered individual and that the installer of the system (if different) was a a credible plumber?

The issues you describe and the actions being taken just don’t seem credible to me.

On the basis that the boiler is performing properly, any reputable plumber should be able to diagnose (and probably fix) the problem with your hot water on site within 1 to 2 hours.

A good rule of thumb, is to diagnose the problem, think through the solution then get your tools out and implement it. Be very wary of people get their tools out before having thought through what the problem is
 
Margaret,

I find this quite odd. Are you sure that the installer of the boiler was aGas Safe registered individual and that the installer of the system (if different) was a a credible plumber?

The issues you describe and the actions being taken just don’t seem credible to me.

On the basis that the boiler is performing properly, any reputable plumber should be able to diagnose (and probably fix) the problem with your hot water on site within 1 to 2 hours.

A good rule of thumb, is to diagnose the problem, think through the solution then get your tools out and implement it. Be very wary of people get their tools out before having thought through what the problem is

Hello Brambles, he was obtained from Valiant website to have a valiant boiler installed, he is also on the gas safety register website.

Upon completion, initially, I did had to chase for the paperwork completion to obtain the 10-year guarantee and received this. (1) buildings regulation compliance gas safety certificate letter from vaillant; (2) buildings regulation certificate of compliance issued by vaillant; (3) Vaillant letter that my 10 years extended guaranteed.

I do recall when British Gas (BG) came on 24/04/2019 (was here for 2.5 hours), BG said might need to lift the flooring in the airing cupboard where the blue HW cylinder sits to see the pipe works but told me to contact the installer. I called for the installer and he came on 30/04/2019 checked the Drayton valves and the black airlock switch, having done the purge manually without using hive and lifting hallway floor boards to look for a T pipe or something, he then went to change the pipes in the kitchen from straight 2 straws to criss-cross. He then tried to test for HW and there was air sound splurging sound, he said the HW was still going in reverse flow. At the last resort, he said he still couldn't understand why the HW is reverse flowing that he then said may need to lift the flooring underneath the hot water cylinder tank in air cupboard.

At present, everything is left on running CH + HW, all radiators turned down and waiting for his return.

Hope this clarifies.
Thanks
 
Last edited:
Hi Margaret, I see in your response to @Brambles that the heating SYNCHRON motor was changed, yet the issue could be the hot water one.

Hello CMW1982, yes, I see on my very first OP on this forum that it was the heating synchron changed and the installer said that to me.

To note, he tried testing hot water by removing and not having the drayton cubes attached/connected to CH pipe and HW pipe. I recall that both B.Gas and himself held the HW drayton cube to their ears. Not sure what they listening to.

By the way, why would the CH Drayton synchron need changing if new and less than 6 months?
 
Last edited:
Hello CMW1982, yes, I see on my very first OP on this forum that it was the heating synchron changed and the installer said that to me.

To note, he tried testing hot water by removing and not having the drayton cubes attached/connected to CH pipe and HW pipe. I recall that both B.Gas and himself held the HW drayton cube to their ears. Not sure what they listening to.

By the way, why would the CH Drayton synchron need changing if new and less than 6 months?

I wouldn’t know on that as things fail for a reason be it poor quality or poor system conditions.

Regarding the listening, they may have been trying to hear the motor turning or even the microswitch.
 
Hi Margaret, are you still in the same scenario?

I’ve just been studying your photo of the cylinder cupboard, and I could be wrong (I am tired)but want to clarify something that’s bugging me. Are you able to photograph the yellowed markups on photo more closely? I want to see if the chrome valve is open, and also where that 15mm pipe tees in. I’m trying to figure out I feel your flow and return are piped up wrong. The Magnaclean states flow of water one way, but it could be another way?

58D5AE2C-6750-47E1-B4DF-02CA15A842BA.jpeg
 
Hi Margaret, are you still in the same scenario?

I’ve just been studying your photo of the cylinder cupboard, and I could be wrong (I am tired)but want to clarify something that’s bugging me. Are you able to photograph the yellowed markups on photo more closely? I want to see if the chrome valve is open, and also where that 15mm pipe tees in. I’m trying to figure out I feel your flow and return are piped up wrong. The Magnaclean states flow of water one way, but it could be another way?

View attachment 38466

Morning CBW1982, yes, I am still in the same scenario. Please see photograph markups more closely, (these were how they were situated (24/04/2019). The installer, he visited 30/04/2019 and said he will leave them off and they are not hanging on the pipework at present). Thanks a lot.

00.JPG


01.JPG


02.JPG


03.JPG
 
If I read those photos correctly, the flow is being directed into the DHW tank through both the flow and return connections.

Boiler Flow being directed to the two two port valves (HW and CH) and the magnaclean! HW return connection connected to the Magnaclean on the flow side. Ie. Flow to flow on the HW circuit when the two port valve is opened.

Margaret, I cannot see that this installation has been plumbed in by anyone with basic plumbing or heating engineering experience.

If I include the work undertaken to switch flow and return in one if your earlier posts and your comment that the valve actuators have mbeen left disconnected - it has all the signs of the work being undertaken by someone with a very low level of understanding as to how an S plan system works.

You need a normal plumber to come in and instal the pipework in a conventional manner for an S plan system. Thereafter, to check the connections and commission the Nest controller.
 
Last edited:
Morning Margaret, thanks for the photos. Sorry to be the bearer of bad news, but as @Brambles has said that looks like it’s been done unprofessionally, (but I think you knew that). It is fixable, but not sure how you go about trying to reclaim costs from your original installer, as if it were me I wouldn’t have him back. There is an isolation valve (chrome valve circled in my edited photo) turned off, and flow is either going backwards from magnetic filter (magnaclean) or the flow comes up to a closed off iso valve and through the return. Either way for this to function as it should then it needs sorting.
 
Last edited by a moderator:
If I read those photos correctly, the flow is being directed into the DHW tank through both the flow and return connections.

Boiler Flow being directed to the two two port valves (HW and CH) and the magnaclean! HW return connection connected to the Magnaclean on the flow side. Ie. Flow to flow on the HW circuit when the two port valve is opened.

Margaret, I cannot see that this installation has been plumbed in by anyone with basic plumbing or heating engineering experience.

If I include the work undertaken to switch flow and return in one if your earlier posts and your comment that the valve actuators have mbeen left disconnected - it has all the signs of the work being undertaken by someone with a very low level of understanding as to how an S plan system works.

You need a normal plumber to come in and instal the pipework in a conventional manner for an S plan system. Thereafter, to check the connections and commission the Nest controller.

Hello Brambles, thanks for the above. Just wanted to mention, in case I typed incorrect, I meant that the installer, he said he will leave the Drayton off and not attached to the pipework (it is dangling down and not 'clipped' onto the CH pipework). Hope this clarifies that part.
 
Hello Brambles, thanks for the above. Just wanted to mention, in case I typed incorrect, I meant that the installer, he said he will leave the Drayton off and not attached to the pipework (it is dangling down and not 'clipped' onto the CH pipework). Hope this clarifies that part.

This is what Brambles means, the Drayton (actuator - plumber/heating engineer terminology) has been disconnected, as in dangling down. You have flow into your cylinder twice, and possibly not going somewhere else as the isolation valve is off. Below is a ‘basic’ principle of how your system should work, however where it is blue, yours is red, and where it is red, yours is red. Hope this makes a bit more sense?

upload_2019-5-5_13-5-42.png
 
If I read those photos correctly, the flow is being directed into the DHW tank through both the flow and return connections.

Boiler Flow being directed to the two two port valves (HW and CH) and the magnaclean! HW return connection connected to the Magnaclean on the flow side. Ie. Flow to flow on the HW circuit when the two port valve is opened.

Margaret, I cannot see that this installation has been plumbed in by anyone with basic plumbing or heating engineering experience.

If I include the work undertaken to switch flow and return in one if your earlier posts and your comment that the valve actuators have mbeen left disconnected - it has all the signs of the work being undertaken by someone with a very low level of understanding as to how an S plan system works.

You need a normal plumber to come in and instal the pipework in a conventional manner for an S plan system. Thereafter, to check the connections and commission the Nest controller.

The magnaclean is new and was installed with the new Vaillant boiler. We didn't have this before. Likewise, the 2x Drayton and hive controller all new. Would the criss-cross be an issue and can these be put back to straight straws? Regarding the lifting of floorboards, he said he was looking for 'T pipe' or 'T valve' (I dont fully recall which) but he said was looking for 'T something' which was why the floorboards were lifted and he wanted to find the pipes from the airing cupboard to the where the boiler is situated in the kitchen. I recall the pipework running along the floor (where flooring lifted) the "middle" pipework was hot.
 
Last edited:
This is what Brambles means, the Drayton (actuator - plumber/heating engineer terminology) has been disconnected, as in dangling down. You have flow into your cylinder twice, and possibly not going somewhere else as the isolation valve is off. Below is a ‘basic’ principle of how your system should work, however where it is blue, yours is red, and where it is red, yours is red. Hope this makes a bit more sense?

View attachment 38483
The pic isn't clear but I believe the 15mm coming from the flow before the magna clean is just a bypass which is teed in to the top connection of the 22mm cylinder return.
 
The pic isn't clear but I believe the 15mm coming from the flow before the magna clean is just a bypass which is teed in to the top connection of the 22mm cylinder return.

If you mean the iso valve this appears to be closed. Also there’s another valve (looks like a lockshield) on the return pipe from cylinder. Whatever is wrong with the installation needs correcting.

Margaret, I don’t think re-doing the pipes (straws as you are referring) straight will make a difference.
 
Yeah the lockshied that's closed, to me looks like it should be a bypass, not 2 flow pipes. I'm not sure what that valve on the return is, looks like an old straight radiator valve.

But yes it does want correcting and I think Margaret should bite the bullet and call in another independent engineer.
 
The other angle I was looking at was the direction of flow on the Drayton valves. Should flow from A through to B, but looks incorrect on this set-up.

View attachment 38484

Hello there, I recall, when I pressed the hive to boost for HW (meaning 'on'), the Drayton on the HW pipe (was on A, and the black clip on the top was upwards popped out heading upwards). But when I clicked cancel HW Boost on the hive, the black on side slided downwards to B, and the top clip also slid downwards. Hope this makes sense as to what I saw.
 
This is what Brambles means, the Drayton (actuator - plumber/heating engineer terminology) has been disconnected, as in dangling down. You have flow into your cylinder twice, and possibly not going somewhere else as the isolation valve is off. Below is a ‘basic’ principle of how your system should work, however where it is blue, yours is red, and where it is red, yours is red. Hope this makes a bit more sense?

View attachment 38483
Thanks, CBW1982 for the diagram, would this possibly explain why my water is only lukewarm and not hot? [When immersion switched off and Hive left to run as per the set schedule timer]
 
The valve on the return from the cylinder is to throttle down the cylinder to slow the flow and help with heat transfer
 
Hello there, I recall, when I pressed the hive to boost for HW (meaning 'on'), the Drayton on the HW pipe (was on A, and the black clip on the top was upwards popped out heading upwards). But when I clicked cancel HW Boost on the hive, the black on side slided downwards to B, and the top clip also slid downwards. Hope this makes sense as to what I saw.

Hi Margaret,

It should when on go towards B, then return to A
 
Morning CBW1982, I recall when it was HW was activated for 'on' it was A, and when I clicked cancel on the Hive boost - the Drayton cube slid back down to 'B' and the clip on the top of the cube also went downwards.

Morning Margaret,

I would say that this is incorrect, and is probably as Craig has said why you needed a new synchron motor in the heating, wouldn’t surprise me if you needed one for the hot water also. It’s obviously been setup wrong, and as difficult as it sounds, I think you need to write off your other engineer and get another one in - maybe one for Citizens Advice? I would also complain to Vaillant as you obtained your engineer from their website - maybe something they could help with?
 
Morning Margaret,

I would say that this is incorrect, and is probably as Craig has said why you needed a new synchron motor in the heating, wouldn’t surprise me if you needed one for the hot water also. It’s obviously been setup wrong, and as difficult as it sounds, I think you need to write off your other engineer and get another one in - maybe one for Citizens Advice? I would also complain to Vaillant as you obtained your engineer from their website - maybe something they could help with?
Definitely complain to vaillant. The engineers on their website the same as Any other only means they have completed one of their training courses. It doesn't actually mean the installer knows what they are doing.
 
Definitely complain to vaillant. The engineers on their website the same as Any other only means they have completed one of their training courses. It doesn't actually mean the installer knows what they are doing.

Hello Craig, I remember I called out Vaillant and an engineer visited because of the reoccurring problem. He said it was nothing to do with the boiler and to contact the installer. The Vaillant engineer also said that they are not responsible for the installer even though I told him this person was obtained from their website, the Vaillant male said: "the installer is not employed by them". They are denying responsibility.

I also recall that I asked whether if there are there any other works required for the installation before any works started, and the installer said no and that all prices have been factored in.

Not sure where to go with this. Any suggestions? Thanks a lot, everyone on here.
 
Hello Craig, I remember I called out Vaillant and an engineer visited because of the reoccurring problem. He said it was nothing to do with the boiler and to contact the installer. The Vaillant engineer also said that they are not responsible for the installer even though I told him this person was obtained from their website, the Vaillant male said: "the installer is not employed by them". They are denying responsibility. Not sure where to go with this. Any suggestions? Thanks a lot, everyone on here.
Vaillant themselves aren't responsible for the installs of the independent installers on their website and to be honest, I'm not sure if a complaint will get you anything other than an apology but if it was me, I would still complain as an installer who they have effectively recommended has messed up and is costing you time and possibly money.
 
Last edited by a moderator:
Hello Craig, I remember I called out Vaillant and an engineer visited because of the reoccurring problem. He said it was nothing to do with the boiler and to contact the installer. The Vaillant engineer also said that they are not responsible for the installer even though I told him this person was obtained from their website, the Vaillant male said: "the installer is not employed by them". They are denying responsibility.

I also recall that I asked whether if there are there any other works required for the installation before any works started, and the installer said no and that all prices have been factored in.

Not sure where to go with this. Any suggestions? Thanks a lot, everyone on here.

Hello Margaret,

As myself and Craig have suggested, still complain to Vaillant because you have an installation that in effect you can’t use correctly. I have replied stating maybe CAB as you have a product that is not fit for purpose.

Thanks,
Chris.
 
Last edited by a moderator:
Forget Vaillant, the boilers fine and although you obtained the installers info off of their website they won't give a monkeys. They should do though, and remove the installer, but it will be of no concern to them.
Write a letter, recorded delivery, to the installer. Outline the issues and state if you do not receive within 7 days a definitive way forward to correct the install then you will have no option but to employ somebody to correct the installation at their expense.
No more phone calls only letters.
 
Forget Vaillant, the boilers fine and although you obtained the installers info off of their website they won't give a monkeys. They should do though, and remove the installer, but it will be of no concern to them.
Write a letter, recorded delivery, to the installer. Outline the issues and state if you do not receive within 7 days a definitive way forward to correct the install then you will have no option but to employ somebody to correct the installation at their expense.
No more phone calls only letters.


Hello SimonG, wanted to ask, I have an invoice from British Gas for their attendance to the house to look at the hot water issue (as the original installer was not available at the time when contacted). British gas came and he replaced the PCB board but I've been charged for this work, in consideration feel rather unfair with the additional charge when the boiler was newly installed?
 
I don't have many run ins when it comes to boilers under warranty but it is my understanding that if any individual other than the manufacturers attempt a repair, does it not void the warranty?
 
Hello SimonG, wanted to ask, I have an invoice from British Gas for their attendance to the house to look at the hot water issue (as the original installer was not available at the time when contacted). British gas came and he replaced the PCB board but I've been charged for this work, in consideration feel rather unfair with the additional charge when the boiler was newly installed?

Should have got Vaillant, it was under warranty. Would probably think it didn't even need a pcb board, but I would imagine that ship has sailed.

I always say to my customers with a new boiler, any issues phone me first, if I'm unavailable then phone the manufacturer as it's under warranty.
 
Hello, would like your opinion please. The original installer last visited on 30/04/2019 and he said would return after changing the two straw pipes to criss-cross. Before he left, the immersion was switched off, the CH left to run which gave us HW, the Drayton was not clipped onto the CH pipe but the HW did have Drayton attached. He also said to not use the hive. So my assumption is that everything was left 'on' running? Please correct me if I am wrong.

Over this time period, we had HW. However, CH was a bit weird. On 08/05/2019, we closed off the CH via using the hive in the evening. But in the morning the radiators were on and very hot. Having checked the hive, the status was off, but it stopped working late on.

Has anyone had this sort of problem?

Thanks a lot to those who previous replied to my post. I feel lost and not sure what to do.
 
I don't have many run ins when it comes to boilers under warranty but it is my understanding that if any individual other than the manufacturers attempt a repair, does it not void the warranty?

Hello Craig, thanks for your response. I did contact the installer on four previous occasions which he attended and the following was addressed:
  1. The first visit, air lock in the system and told us to if happen again to turn the black lever in the airing cupboard;
  2. The second visit replaced the syncron motor on the heating valve;
  3. The third visit advised to keep the immersion on constant;
  4. The fourth visit said found a small leak and replaced the red wheelie.

Thereafter, the fourth visit, the HW remained an issue.

The bank holiday approached, we tried to contact the original installer but he was not available and as am sure with anyone, having cover on the CH and HW, British G was booked in. I hope this clarifies as to the above?

Thanks.
 
It's quite clear you've got a control issue and an engineer who doesn't know what he's doing. You need to get a new professional in to sort out the situation.

To be honest I don't know why you'd get BG out when it's a new install and it's obvious it's something wrong with the new install and not the existing system. You should have pushed the original installer.

BG shouldn't have replaced the PCB when it wasn't at fault at all and really should refund you for this as the issue you called them out to is still occurring. However I doubt you'd get any money out of them when it becomes evident that the installation is wrong.

As for criss crossing the pipes (Which looks dreadful!), is the flow and return now the right way round? To check this look on your motorised valve on the cylinder (The white drayton box) which will have an A & B on the brass body. Turn the system on from cold and the hot water should flow from A to B on the motorised valve. If it doesn't then something is wrong. (So the top pipe going into the side of the cylinder should get hot before the bottom pipe).
 
Hi Margaret, I feel the best course of action for you to do now is contact another installer. Do a little research and find a competent one. Ask the installer to come round and investigate what's wrong with your system, and write a list of all that he feels is wrong and roughly how much it will cost to put right. Once you have this info, write a letter to your original installer stating that you have had another installer look at the installation and inform him what is wrong and how much you have been quoted to put it right. Tell him you will allow him upto 7 days to come back and correct his work, and that if he doesn't respond or again fails to get your system working properly, you will be getting the other installer back and you will then seek to claim back the cost of this additional work. As mentioned previously by Simon, Do this by recorded delivery, you will then know and have proof that your installer has received the letter.
 
Margaret,

If we trawl back through this problem, from my perspective it comes back to two issues:

From the photographs you have provided, it looks as if the pipework installation is sending a flow to both the flow and return terminals of the indirect hot water tank.

It also appears that the two port valves and possibly the Hive controller have been installed in correctly.

Both of the above give a clear indication that the installer of the system was inept and probably not competent.

To correct this situation you require a reputable plumber, to survey the system and to give you a priced proposal to modify the current installation into a fully working S Plan system.

At that point you can then decide how to proceed to get you system operating properly and (just as importantly) how to recover the additional money you have already spent and will need to spend to rectify the problem.

If the sum is large enough, you should consider giving the original installer one opportunity to correct the installation, thereafter engage a competent plumber and recover your costs through the small claims court.

Which ever route you take, to recover your costs, you need to establish a clear base line ( in the form if a short, but detailed report) now of what is wrong with the installation and how much it will cost to correct. It is equally important to establish a base line to preserve the warranty that you believe you have for the Vailient Boiler. By allowing people (BG) to tinker will a newly installed boiler, you are putting that warranty at risk

It may be that you household insurance policy will provide legal cover to assist in your claim.

I feel sorry for you with British Gas and I think that you should challenge them on the basis that they fitted a part that was not needed. However, if you call people in on an adhoc basis you need to recognise that they are going to charge for their time.

When I first read you post, I interpreted it as a control issue - they are generally a simple fix ( either correcting the wiring or replacing a faulty part). Once you provided photographs of the pipework around the hot water cylinder, it became apparent that the pipework has been installed incorrectly - this is a more expensive fix. It is also harder to interpret system behaviour, when the pipework is fundamentally wrong. I am surprised that you have ever managed to get hot water with the cylinder piped in that way

At the end of the day a system like yours is a very common straight forward installation - it is not complex and is fixable, once the scope of work required to do so is established.

Hopefully the above will help you to establish a clear and successful way forward.
 
Thanks all. Can the criss-cross pipes (originally two straws) be put back to normal? It was unexpected and an eyesore just as you walk into the kitchen! Why would this be changed to criss-cross anyway? Can this be put back to normal? Seems like decoration with two straight straws at the top, then twidles criss-cross towards the bottom then goes back to normal.

The installer was previously with BG and 13 years experience as displayed/advertised on Valiant website.
 
The installer was previously with BG and 13 years experience as displayed/advertised on Valiant website.
:eek::eek::eek::eek:

Can the criss-cross pipes (originally two straws) be put back to normal? - yes they can, but it needs to be done correctly and checked for correct operation. As we have said, it’s fixable, but needs doing by someone who should know what they’re doing.

I had an ex BG service my boiler (before I could) and I wasn’t impressed with what he’d left - a boiler that was condensing into the casing and a high PPM reading in the flue analyser.
 

Reply to Hot water from Valliant Boiler in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

  • Question
My disabled daughter’s hot water has stopped working. It’s a relatively modern Potterton boiler with an indirect sealed hot water system and a...
Replies
12
Views
932
The Water Board have just replaced the main water supply to our property. We have a ground floor combi boiler. The central heating system for the...
Replies
9
Views
566
M
Hello, We’ve recently moved into a fairly old, fairly big detached house (i.e. fairly draughty, but not too bad by any means) with a fairly new...
Replies
0
Views
288
MartinPod81
M
I live in an apartment with a cold water tank. The cold water tank feeds the cold water tap in the sink and the bath. Recently, I refurbished my...
Replies