& B.Gas who can't sort out simple problems.Of course it’s fixable and if it worked before then it should again. But concerned with the installer swapping pipes over
Discuss Hot water from Valliant Boiler in the Plumbing Jobs | The Job-board area at PlumbersForums.net
& B.Gas who can't sort out simple problems.Of course it’s fixable and if it worked before then it should again. But concerned with the installer swapping pipes over
British gas couldnt find the issue?& B.Gas who can't sort out simple problems.
No. The installer was obtained from Valiant website [Turn your guarantee up to 10].Margaret
Was the contract to instal the boiler and hive with British Gas?
Londonwhere are you based Margaret?
Margaret,
On the positive front, it is good that the original installer is actively engaged in the resolution. Irrespective of achieving success, at least he/ she has the commitment and is trying to resolve the issue.
Switching flow / return without sound logic (when the heating side is functioning ) is puzzling. I am assuming that he/she ( at the time of switching) has not relocated the magnetic filter ( which I recall is adjacent to the hot water cylinder) onto the “new” return, leaving the new boiler unprotected from debris flowing from the system back to the boiler? That is not the end of the world, but demonstrates poor thinking in the act of desperation
If you wish feel free to message me at [email protected]
If you are relatively close, I am happy to look at it for you - to give you a few pointers fir your installer to rectify the problem
Margaret,
I cannot see why the installer has reversed the flow on on your system. The issue you have described is that the only problem you have is that you cannot run Hot water without have the Central Heating on.
My view is that either :
The control wiring between the two two port valves and the Hive interface is incorrect.
Or, the micro switch in the two port valve controlling hot water is not functioning ( I think you said that the synchronous motor was changed. The installer may have damaged the micro switch or dislodged the connection in the process.
The only reason to change the pipework configuration that I can think of, is if the installer has fitted the Hot Water two port valve downstream of the Central Heating two port valve. I have seen this before on new installations.
To conclude, to operate a condensing boiler for Hot water only is as simple as it gets, a boiler, two pipes, a valve and an indirect cylinder. Better still you know that the hydraulic circuit works, because it functions when the central heating is on. I would have expected the installer to operate the boiler in this mode upon first use before testing the central heating circuit.
Presumably the installer cleaned the existing central heating system before installing the new boiler? So should have a good understanding of the system pipework layout.
With respect to the crossovers, they should be removed or if deemed to be correct the magnetic filter should be reinstalled on the return immediately before the boiler.
In my view, the actions taken by your installer earlier this week are putting your boiler warranty at risk.
My view has not changed since your problem was first posted. It is not a difficult fix for a competent heating engineer or a plumber with a good knowledge of heating systems - and this is most properly trained experienced plumbers.
On a final point, don’t let him/her take up any more flooring / floor boards - that is just not needed to fix this.
Feel free to share this note with your installer - it may help to focus their mind in the fault finding process.