W

will123

Hi,

We've moved into a new house that has a sealed central heating system with an Ideal boiler providing heat for the central heating and water cylinder.

I had a problem where I was getting air in the system and losing a little pressure, but I found a loose but on a radiator and tightened it which fixed the air problem.

I then topped the system up to 1 bar and this pressure held for just over a week before dropping to 0.8.

I thought the pressure should remain the same, so I called in a plumber. We are in a new build house so it is all under warranty. He checked for leaks and couldn't find anything. He recommended topping the system up to 1.5 bar, so we did. He then said that he expected the pressure could drop to between 1.3 and 1.4.

Well that was over three weeks ago and up until today the pressure has held at 1.5 bar. However, today it has dropped to 1.4.

Why is this? I mean I know the plumber said to expect this, but why now and why the drop?

All the pressured I mentioned above are from when the system is cold.

Thanks for listening, I'm just one of those homeowners who likes to understand what's going on!
 
It is not possible to teach you every aspect of a heating system. If it works, leave it alone. If it stops call an engineer. What the plumber has said is fine. Water contracts and expands with heat so the pressure will fluctuate. Fresh water has some bubbles in which will disperse, often via an auto air vent in the boiler, and some pressure will go. It is common to have to top up a system after it's first filling/usage for up to 3 weeks.
 
Thanks guys. I guess I am just overly paranoid with having both a new house and a new child!
 
Status
Not open for further replies.

Reply to Help me understand sealed system pressure please! in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
362
Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer warming up. The heat exchanger has been changed 6 months ago, so I do not believe it is that. Does anyone have any ideas on what it could be? Thanks
Replies
4
Views
252
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
5
Views
496
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m planning to pour a 100mm deep concrete patio on 100mm hardcore. In order to achieve the same final height to line up with the rest of the patio, I...
Replies
6
Views
261
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock