I've been told that after cleaning out baffles you can't analyse the gass accurately for some reason. Is there any truth in this?
Seems to me that if cleaned as thoroughly as possible the readings shouldould be more accurate than what they were when all sorted up inside. 🤔

Any pointers or advice on the matter hugely appreciated.

Thanks
 
You wouldn't stick your flue gas analyser into a sooted up boiler or flue. Whoever told you that is wrong. Once the boiler has been cleaned you would obviously then use your smoke pump before taking flue gas readings with your analyser to set the burner up properly.
If the person who told you that is also the person maintaining your boiler I would look at getting someone else.
 
🐂 --it cleaning baffles is part of a full strip down and service on a oil boiler, a new oil filter and nozzle is the norm and once completed the boiler is tested with a smoke pump with a temporary oil pressure gauge fitted , before finally using a flue gas analyser to achieve a satisfactory reading by either adjusting the air into the burner and or oil pressure . Kop
 
Thank you guys very much for the responses.
That's cleared that up nicely.

Of all the services the boiler has had over the years never have I seen anyone use a smoke pump. 🤔
I think I understand the idea of smoke test but can't quite see why it's an important step if a gas analyser is used afterwards.
Is it a visual aid to show customer or is it healthier for analyser to be closer to the correct setting or?

Im really interested to learn so very grateful for any further comments on this.
Thank you very much. 👍
 
Thank you guys very much for the responses.
That's cleared that up nicely.

Of all the services the boiler has had over the years never have I seen anyone use a smoke pump. 🤔
I think I understand the idea of smoke test but can't quite see why it's an important step if a gas analyser is used afterwards.
Is it a visual aid to show customer or is it healthier for analyser to be closer to the correct setting or?

Im really interested to learn so very grateful for any further comments on this.
Thank you very much. 👍
Healthier for the analyser as you say you really don't want to put it into a boiler with poor combustion it knacker the cells . Kop
 

Reply to Boiler adjustment after baffles cleaned in the USA area at PlumbersForums.net

Similar plumbing topics

Desperate for some help! Be a life saver of someone can help as suffer from a high intolerance to noise. Moved into new house 1940s (copper...
Replies
7
Views
845
About 12 days ago attended a boiler lock out. Apparently another plumber was there a week before to and adjusted the photo cell. .. It is a grant...
Replies
25
Views
3K
Baxi heat only boiler (7 yrs old) - switches off after a few minutes with some banging noises followed by a red flashing light on boiler Reset the...
Replies
7
Views
3K
Hi all. I have an open vented system with magnaclean filter installed at the return pipe close to boiler. I understand how the magnacleanse...
Replies
1
Views
2K
Hello, I have a had a gravity boiler replaced from a Potterton 80e to a more recent Valliant ecoplus boiler. The cold water tank is in the loft...
Replies
6
Views
2K
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock