Discuss 24 RI CH comes on when water on. Possible programmer fault also in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Status
Not open for further replies.

armyash

Esteemed
Plumber
Gas Engineer
Subscribed
Messages
2,652
Hi everyone

Been a while, hope everyone is well.

Been to a job tonight, if hw on rads get hot also. Ch 2 port seized open. Lever on valve permanently slack.

24 RI

Another issue seems to be programmer might be working intermittently. Even with ch and hw turned off at programmer, boiler fired up. What else could it be if not programmer?

Thanks
 
The 2 port. Use your multimeter and chase the voltage to see where its coming from causing the boiler to fire. Sounds like a zone valve fault to me though.
 
Thanks the ch 2 port has definitely gone I know that much. Hot water coming through as soon as hw turned on.

Thanks for confirming for me. I was starting to over think things as usual and looking for another fault.
 
The 2 port that needs changing is a myson. 4 wires.

Is this an easy swap for a danfoss or any other.
Thanks
 
Yeah only difference would be a earth if you change to a metal head ie Honeywell
 
Only one I could get was a Drayton, is there any difference to the wiring? Thanks
 
It's 28mm, where does the white go?

Edit: from what I can see it goes in with the live? Is that correct?

Edit again: having another look it's in a terminal by itself as it becomes live when the valve close.
 
Last edited:
sorry just seen its a 28mm

its like the grey wire

so just make it safe dont need it
 
Last edited:
Glad that the lads could help. Sorry I was not around. Been away for a few days.
 
Status
Not open for further replies.

Reply to 24 RI CH comes on when water on. Possible programmer fault also in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi, would appreciate any thoughts on the below. I have an almost 10yr old Ferroli Modena 32S HE system boiler. (I am aware of their reputation...
Replies
3
Views
524
Good Afternoon all, I am hopeful someone may be able to offer some guidance on the following. In the home we have a gas boiler (serviced...
Replies
5
Views
533
Our Potterton EP2 was old and the sliders for HW/CH were loose. We couldn't get CH without the HW on! So I put a new digital EP2 on. It fit over...
Replies
2
Views
837
Customer complains of Intermittent heating on Y plan with Stat satisfied. New boiler fitted last year (no permanent live required or fitted...
Replies
25
Views
2K
Evening All, Been having on and off issues with a Greenstar CDI classic Combi were the hot water is not heating up but only intermittently. Some...
Replies
2
Views
517
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock